    3 way bypass

    Chilled water a/h replacement, 2" feed, 1 1/4 at a/h, I'm putting in a strainer, a 3 way valve and a circuit setter, I was going to install a
    1 1/4 3 way valve, boss ordered 3/4, I say circuit setter will take care of flow through a/h and would be better at 1 1/4, there is a major issue in build with bypass, right or wrong?
    Rather be golfing!

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Depending on the CV rating of the valve. 1 1/4" would by my choice with that information. Correct in letting the circuit setter do its job!





    With that said always refer to rule #1!

  3. Likes CHILLERSVCMAN liked this post.
  4. #3
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    Even with the circuit setter properly sized, if the valve CV is too large there could be an issue with hunting if the valve is modulating. Especially if the controlled reference is discharge air. But like pecsmg stated info supplied doesn't give much to go on.

  5. Likes CHILLERSVCMAN liked this post.
  6. #4
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    464
    Post Likes
    Do you have the old 3 way valve, if you do what manufacture and what numbers are on the valve? Do you know the specs on the new coil GPM ,etc ? Hopefully WAYNE or one of the other TAB guys see this, they could help you out better.

    Sent from my ASUS_P00J using Tapatalk

  7. #5
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    You need to know the flow and some information on the chilled water system. hvac69 is on the money because if the control valve is oversized hunting will occur. The control valve has to sized to supply design flow to the coil. Oversized circuit setters can also be closed enough to cause premature failure of the circuit setter and result in inaccurate flow readings.
    Without more information we can't tell you more than to make sure the valve is properly sized. How did the old valve function?
    No man can be both ignorant and free.
    Thomas Jefferson

  8. #6
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    If its a new ahu, you should have all the design data needed to properly size the valve and circuit setter.

    How was the replacement AHU selected?

  9. Likes pecmsg liked this post.
  10. #7
    Join Date
    Sep 2020
    Location
    Canada
    Posts
    16
    Post Likes
    I read an article once that discussed how circuit setters are only needed when the valve is two position. If a 3 way valve is modulating the circuit setter doesn't need to be there. It seems to make sense to me. Thoughts?

  11. #8
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    You need a circuit setter on both ports. One reason is to balance the pressure drop to assure flow control to the load and return.
    No man can be both ignorant and free.
    Thomas Jefferson

  12. #9
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,265
    Post Likes
    And . . . you need to consider the sum of all the three-ways in the loop. The total flow of all should be above the chiller's minimum flow requirements.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •