  1. #41
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by Sapote View Post
    Do you guys isolated the micron gauge before releasing the refrigerant to avoid contaminating?
    No. I try to keep the number of connections and valves as low as possible. I do try to keep the stem of the guage pointed up to keep oil from running into it.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  2. #42
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,816
    Post Likes
    Quote Originally Posted by Sapote View Post
    Do you guys isolated the micron gauge before releasing the refrigerant to avoid contaminating?
    No

  3. #43
    Join Date
    Aug 2020
    Location
    So California
    Posts
    310
    Post Likes
    For those who don't isolate the micro gauge, how do you know if its displayed valve is correct? last time it was calibrated?

  4. #44
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by Sapote View Post
    For those who don't isolate the micro gauge, how do you know if its displayed valve is correct? last time it was calibrated?
    You can calibrate the bluevac in the field. Also it has to be cleaned regularly.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  5. #45
    Join Date
    Aug 2020
    Location
    So California
    Posts
    310
    Post Likes
    Quote Originally Posted by R600a View Post
    You can calibrate the bluevac in the field. Also it has to be cleaned regularly.

    Sent from the Okie state usin Tapatalk
    How do one know the ambient pressure in the field any where?

  6. #46
    Join Date
    Aug 2020
    Location
    So California
    Posts
    310
    Post Likes
    Quote Originally Posted by R600a View Post
    You can calibrate the bluevac in the field. Also it has to be cleaned regularly.
    IF you trust the CRT's ball valve, then why not isolating the micron gauge with one and forget about recalibrating and cleaning?

  7. #47
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by Sapote View Post
    How do one know the ambient pressure in the field any where?
    Calibrating a micron gauge has nothing to do with pressure they are not a pressure sensing device.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  8. #48
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,816
    Post Likes
    Quote Originally Posted by Sapote View Post
    For those who don't isolate the micro gauge, how do you know if its displayed valve is correct? last time it was calibrated?
    When the bluvac is out of calibration there is a indicator plus another indicator for oil fouling.

  9. Likes R600a liked this post.
  10. #49
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by itsiceman View Post
    When the bluvac is out of calibration there is a indicator plus another indicator for oil fouling.
    And of course go bluevac or go home.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  11. #50
    Join Date
    Aug 2020
    Location
    So California
    Posts
    310
    Post Likes
    Quote Originally Posted by R600a View Post
    Calibrating a micron gauge has nothing to do with pressure they are not a pressure sensing device.
    Very funny you, because I designed such a thing. Micron gauge using the principle of thermal conduction in the gas medium to determine the density of the gas, or the pressure of it given its temperature is known. There is a heater element and a thermocouples inside, and the computer chip doing all the calculation running a programming codes. Ask how do I know.

    Of course we calibrated the gauges in the factory using a know pressure for a particular gas.

    It's similar to the Mass Air sensor for metering the air intake in your modern fuel injected engines.

  12. #51
    Join Date
    May 2018
    Posts
    573
    Post Likes
    I use a Bluvac, so isolating it is not mandatory, it can handle 500psi according to the specs. Having said that, I usually release the charge, or add charge, whichever the case may be, til the pressure is above atmosphere, say 15-50psi, stop, remove vacuum gauge, install cores, and finish charging.

  13. Likes joemach, Matt Woodbridge liked this post.
  14. #52
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,816
    Post Likes
    Quote Originally Posted by channellxbob View Post
    I use a Bluvac, so isolating it is not mandatory, it can handle 500psi according to the specs. Having said that, I usually release the charge, or add charge, whichever the case may be, til the pressure is above atmosphere, say 15-50psi, stop, remove vacuum gauge, install cores, and finish charging.
    500 psi is a old spec. New spec is 1000 psi.

  15. #53
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by Sapote View Post
    Very funny you, because I designed such a thing. Micron gauge using the principle of thermal conduction in the gas medium to determine the density of the gas, or the pressure of it given its temperature is known. There is a heater element and a thermocouples inside, and the computer chip doing all the calculation running a programming codes. Ask how do I know.

    Of course we calibrated the gauges in the factory using a know pressure for a particular gas.

    It's similar to the Mass Air sensor for metering the air intake in your modern fuel injected engines.
    Now I'm curious. Since you're an engineer could you please look up bluvac calibration instructions? I would be really interested to hear your opinion on their method.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  16. #54
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    206
    Post Likes
    Quote Originally Posted by Sapote View Post
    Do you guys isolated the micron gauge before releasing the refrigerant to avoid contaminating?
    Of course, not due to contamination, but because positive pressure isn't good for micron gauges

    Sent from my SM-A516U using Tapatalk

  17. #55
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by Matt Woodbridge View Post
    Of course, not due to contamination, but because positive pressure isn't good for micron gauges

    Sent from my SM-A516U using Tapatalk
    Especially if you use a Just Better at leaking micron gauge.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  18. Likes Matt Woodbridge, Zamoramax liked this post.
  19. #56
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,816
    Post Likes
    Quote Originally Posted by Matt Woodbridge View Post
    Of course, not due to contamination, but because positive pressure isn't good for micron gauges

    Sent from my SM-A516U using Tapatalk
    1000 psi...
    Not really worried about overpressure.

  20. Likes Matt Woodbridge liked this post.
  21. #57
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    206
    Post Likes
    Quote Originally Posted by R600a View Post
    Especially if you use a Just Better at leaking micron gauge.

    Sent from the Okie state usin Tapatalk
    Lol, after my response, I read all your guys comments, on there actually good for i think someone mentioned 1000 psi. I wouldn't try it with my gauge, but just in case, I dont have to worry so much

    Sent from my SM-A516U using Tapatalk

  22. Likes R600a liked this post.
  23. #58
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    206
    Post Likes
    Quote Originally Posted by itsiceman View Post
    1000 psi...
    Not really worried about overpressure.
    Yeah I just seen that, I've just never tried any positive pressure, ive always taken off my gauge.

    Sent from my SM-A516U using Tapatalk

  24. #59
    Join Date
    Aug 2020
    Location
    So California
    Posts
    310
    Post Likes
    Quote Originally Posted by channellxbob View Post
    I use a Bluvac, so isolating it is not mandatory, it can handle 500psi according to the specs. Having said that, I usually release the charge, or add charge, whichever the case may be, til the pressure is above atmosphere, say 15-50psi, stop, remove vacuum gauge, install cores, and finish charging.
    That's not too difficult, isn't it? This is the whole point I try to say in the other post about releasing refrigerant just enough higher than ambient pressure before installing the core valve, but people here think I'm nut.

  25. #60
    Join Date
    Aug 2020
    Location
    So California
    Posts
    310
    Post Likes
    Quote Originally Posted by Matt Woodbridge View Post
    Of course, not due to contamination, but because positive pressure isn't good for micron gauges
    Just had a quick look at the micro BluVac user guide. It says:
    "
    If oil or other contamination is inadvertently drawn into the sensor, the display will show:
    To clean the sensor:
    1. Turn the μBluVac+ power on.
    2. Shake out any excess oil.
    3. Using an eye dropper or syringe, fill the sensor port hole with isopropyl alcohol. Do not insert any object into the port.
    4. Shake out the alcohol.
    5. Repeat steps (3) and (4) three times.
    6. Thoroughly dry the sensor by pulling a vacuum for about 1 minute, or allow at least 1 hour to air dry.
    7. If OIL still shows on the display, perform a freezer calibration.
    "
    Wow, with all the steps involved in cleaning, why not add an isolation valve?

  26. Likes Matt Woodbridge liked this post.
+ Reply to Thread
Page 3 of 16 FirstFirst 1234567891013 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •