    R12 Subzero 532 issues

    I have a subzero 532 from 1991 with R12. The condenser fan failed in 1998 and the fridge compressor failed. The compressor was replaced, but I've had poor performance with the fridge ever since. I have low and high side ports on this system and am thinking the best case is the charge was never sufficient and I can just hook up a manifold and check it and up the charge if needed.

    Here's the nameplate if this works:
    photos.app.goo.gl/JJr7v9tY9oW3ohs38

    Well I guess I'm not allowed to post images or links, but only one design pressure is given for both the freezer and refrigerator section. 235 hi 140 lo.

    Subzero tech support says my charge pressures should be 16/120 fridge and 4/120 freezer, and they claimed they never printed those numbers on their nameplate (they did). I assume those are to be with the unit acclimated to room temperature and compressor on only briefly.

    I plan to order some R12 and be prepared to charge it up when I connect the manifold to check pressures.

    Any comments on this unit and how I should do this?

    Is there any way this can be properly converted to R12a? My local (Subzero listed) repair guy says he just changes them to 134a, but Subzero says no never do that. R12a seems really good, but I would probably need someone to come evacuate the R12 before doing that.

    Thanks.

  2. #2
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes

    R12 Subzero 532 issues

    If you don’t understand the difference in design pressure and refrigerant charge, shouldn’t you call someone to take care of it for you?

    And why wait almost 22 years to check it?


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  3. Likes stumpdigger liked this post.
  4. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Those pressures listed on the name plate are "test pressures", which basically means the maximum pressure those parts of the system can hold without exploding.

    No other refrigerant will work as good as R12 did. I don't know what the proper procedure would be to change it to R12a, and even if I did, we aren't supposed to be giving this type of advice to people on this forum, except for in the locked areas that are reserved for licensed professionals. Sorry.
    If at First You Don't Succeed, Skydiving Is Not for You.

  5. Likes stumpdigger liked this post.
  6. #4
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    I'd be willing to bet that someone did a leak check and repair then put in a different refrigerant due to the cost of R-12 (you can thank your government for that). It is also possible that your unit has more than one type of refrigerant in it now (not good).

    Your unit can be converted to a current refrigerant, but to do it properly, you would probably be surprised at how much it would cost. Typically, a 30 year old unit is only converted if the new one cannot fit into the same space.

    If you are trying to save some money, my recommendation would be to look up some second hand shops that are selling used equipment. Where I live, that used to be a thriving industry, and the sellers would typically give you a 90 day warranty. Not bad considering the great reduction in price from new equipment.




    Quote Originally Posted by dbur View Post
    I have a subzero 532 from 1991 with R12. The condenser fan failed in 1998 and the fridge compressor failed. The compressor was replaced, but I've had poor performance with the fridge ever since. I have low and high side ports on this system and am thinking the best case is the charge was never sufficient and I can just hook up a manifold and check it and up the charge if needed.

    Here's the nameplate if this works:
    photos.app.goo.gl/JJr7v9tY9oW3ohs38

    Well I guess I'm not allowed to post images or links, but only one design pressure is given for both the freezer and refrigerator section. 235 hi 140 lo.

    Subzero tech support says my charge pressures should be 16/120 fridge and 4/120 freezer, and they claimed they never printed those numbers on their nameplate (they did). I assume those are to be with the unit acclimated to room temperature and compressor on only briefly.

    I plan to order some R12 and be prepared to charge it up when I connect the manifold to check pressures.

    Any comments on this unit and how I should do this?

    Is there any way this can be properly converted to R12a? My local (Subzero listed) repair guy says he just changes them to 134a, but Subzero says no never do that. R12a seems really good, but I would probably need someone to come evacuate the R12 before doing that.

    Thanks.
    I do a triple evac with nitro to remove non condensables.

  7. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Good Luck and God Bless

    Call someone that knows what there doing!

  8. Likes stumpdigger liked this post.
  9. #6
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Beat you to it by five seconds, LOL


    Quote Originally Posted by pecmsg View Post
    Good Luck and God Bless

    Call someone that knows what there doing!
    I do a triple evac with nitro to remove non condensables.

  10. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    The million dollar question is If it was repaired 22 years ago and has performed poorly for 22 years, why all of a sudden do you want it fixed now?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  11. Likes stumpdigger liked this post.
  12. #8
    Join Date
    Jul 2020
    Posts
    22
    Post Likes
    Thread Starter
    It is a built in and I can't remodel my kitchen for another unit. Also even a used unit is asking almost as much as I paid for this new. $ are tight this year so I can't be blowing 1000's of $ on this when maybe just a top off of R12 will make it serviceable again. Not sure I'd want another Sub Zero again anyway after the myriad problems I have had with this one. Even my 40 year old $200 Sears unit is still working fine. So my only real option is to get this one operating effectively again. I've contacted a few pro's and one didn't want to touch an R12 system, another said he would just charge it with 134a (he was a subzero listed service provider). Sub Zero tech support says in no way do that. So my options are find some R12 and and top off and hopefully get lucky, get someone to do a full evac for me and move to an alternate coolant (Sub Zero says 414a or b). R12a seems a better option but not many service people in US are familiar with it. (R12a is much more efficient than 134a and more compatible with R12 systems). I could give a link to an engineering journal comparison but I'm not allowed to post links here.

  13. #9
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Probably due to the [unqualified] techs that you have been calling. Trying to go cheap.

    Haven't looked at your profile, but where you are doesn't display on your posts. Tell us where you are, and maybe there is someone local here to your area.

    Gonna have to pay though.


    Quote Originally Posted by dbur View Post
    It is a built in and I can't remodel my kitchen for another unit. Also even a used unit is asking almost as much as I paid for this new. $ are tight this year so I can't be blowing 1000's of $ on this when maybe just a top off of R12 will make it serviceable again. Not sure I'd want another Sub Zero again anyway after the myriad problems I have had with this one. Even my 40 year old $200 Sears unit is still working fine. So my only real option is to get this one operating effectively again. I've contacted a few pro's and one didn't want to touch an R12 system, another said he would just charge it with 134a (he was a subzero listed service provider). Sub Zero tech support says in no way do that. So my options are find some R12 and and top off and hopefully get lucky, get someone to do a full evac for me and move to an alternate coolant (Sub Zero says 414a or b). R12a seems a better option but not many service people in US are familiar with it. (R12a is much more efficient than 134a and more compatible with R12 systems). I could give a link to an engineering journal comparison but I'm not allowed to post links here.
    I do a triple evac with nitro to remove non condensables.

  14. #10
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    R12 currently sells wholesale for $2300 for a 30 pound jug. There are other R12 replacements but all are pricey. I find it difficult to believe that a compressor that has run on a low charge for 22 years has suffered zero internal damage.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  15. Likes BALloyd liked this post.
  16. #11
    Join Date
    Jul 2020
    Posts
    22
    Post Likes
    Thread Starter
    Location is Oregon. And I haven't been talking to cheap providers. The one guy who wanted to do 134a is actually a Subzero approved service tech.

  17. #12
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    I have a number of ideas; do not have it changed to R-134a, don't attempt to do anything yourself, not necessarily in that order. No one built your house around the refrigerator, it will pull right out. Hire a professional, there are links on this site.
    " The more I learn the more I realize how much I don't know"

  18. #13
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by dbur View Post
    Location is Oregon. And I haven't been talking to cheap providers. The one guy who wanted to do 134a is actually a Subzero approved service tech.
    To convert to 134A requires a new condensing unit, evaporator(s) and metering device. If there going thru all that might as well go R404A

  19. Likes stumpdigger liked this post.
  20. #14
    Join Date
    Oct 2014
    Location
    Maplewood, Minnesota
    Posts
    1,154
    Post Likes
    Quote Originally Posted by pecmsg View Post
    To convert to 134A requires a new condensing unit, evaporator(s) and metering device. If there going thru all that might as well go R404A
    My vote is 290 and an open flame.

  21. Likes WT70 liked this post.
  22. #15
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    290 and a flame won't do anything.

    If you really want some action, you need to add some oxygen.

    Okay now, where's my beer . . . Need to sit back and wait for the Fireworks . . .


    Quote Originally Posted by Pnasty View Post
    My vote is 290 and an open flame.
    I do a triple evac with nitro to remove non condensables.

  23. Likes 2sac, stumpdigger, Pnasty liked this post.
  24. #16
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by BBeerme View Post
    290 and a flame won't do anything.

    If you really want some action, you need to add some oxygen.

    Okay now, where's my beer . . . Need to sit back and wait for the Fireworks . . .
    Maybe go real old school with a SO2 unit...
    " The more I learn the more I realize how much I don't know"

  25. #17
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Consider calling the local union and getting a commercial refrigeration guy to come out.
    " The more I learn the more I realize how much I don't know"

  26. #18
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by stumpdigger View Post
    Consider calling the local union and getting a commercial refrigeration guy to come out.
    We charge too much

  27. #19
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by pecmsg View Post
    We charge too much
    as in "overcharging" In the long run we would be way cheaper.

  28. Likes BBeerme liked this post.
  29. #20
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by stumpdigger View Post
    as in "overcharging" In the long run we would be way cheaper.
    Exactly

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •