    What are the best FlowHoods on the market? Testo vs. Evergreen vs. ???

    Hello,

    My company is looking to add another Flowhood to our inventory. I took our vintage Shortridge out of service. I did some side-by-side comparisons of different equipment, and the Shortridge was not even in the ballpark of accuracy, while our Evergreen was spot-on, in most cases.

    I work with a technician who uses an Evergreen 3-pounder. It's an amazing piece of equipment. A breeze to use, accurate, and the flow-plates allow accurate readings down to 30CFM. I personally don't like it because the skirt is paper-thin, and everything feels delicate. We've had problems with the Wrist Reporter in the past, and I doubt Evergreen is improving their products.

    Does anyone use the Testo 420? How do you like it? Are there any other models you would recommend? The ability to use a stand and take remote measurements are a big selling point.

  2. #2
    Join Date
    Dec 2014
    Posts
    3,175
    Post Likes
    I think Shortridge is the cream of the crop, but that perception is from years ago.
    We have 2 Alnors that are OK.
    Hopefully one of the pro balancers chimes in.


    Sent from my SM-G950U using Tapatalk

  3. #3
    Join Date
    Apr 2020
    Location
    South USA
    Posts
    20
    Post Likes
    Thread Starter
    There might be something wrong with our Shortridge hood. I've been getting extremely high airflow measurements, especially on smaller grilles. The flow baffles and grid are not quite in alignment, but I don't know how it would affect it that much. The meter works fine, with current calibration.

    I'm not very motivated to try to fix it. It's so bulky and hard to use compared to the new hood.

  4. #4
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    4,439
    Post Likes
    I assume you are partial to the digital hood. Most are now days but make sure whatever you buy has time weighted averaging. The first digital hoods were susceptible to pressure changes and were not very accurate.
    I liked the Shortridge analog the best because I could rely on it to read slightly below a pitot traverse. I never knew where the digital was going to come in. Alnor actually made the original Shortridge meter.
    The electronic meters in my experience were very reliable for pitot traverse.
    No man can be both ignorant and free.
    Thomas Jefferson

  5. #5
    Join Date
    Apr 2020
    Location
    South USA
    Posts
    20
    Post Likes
    Thread Starter
    I think I read that Alnor uses a hot-wire system? These new products on the market have really impressive specifications. But I understand that they're only accurate with a correctly-sized skirt, and when airflow is linear through the device.

    This afternoon we read about 200 outlets, some were 700 CFM on a 20 foot ceiling, others were 75 CFM in small compartments. This was a piece-of-cake with the 3lb flowhood with extension pole and all the accessories. With the Shortridge, ... I don't even want to think about it. I'd be hating my life by about now.

    The boss wants to buy either Shortridge or Evergreen because that's what the other techs in the area are using, and he's afraid of unknown brands. I'm trying to tell him that TSI, Testo, Dwyer, and a lot of other brands are a lot bigger and a lot older than either of these.

    My understanding is that after Ernie Shortridge passed away, the company has been going downhill. They charge $595 to give you a calibration sticker, while the local shop can do the same thing for about $100 or so. This price doesn't include any repairs. The bad thing is that nobody else knows how to work on the contraption. I sent an email to the company with a technical question, and never got a response. The Shortridge website looks like it wasn't updated since W was president. It sounds to me like these guys are just milking their customers for whatever they can get.

  6. #6
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    4,439
    Post Likes
    I never found a shop anywhere that would calibrate a flow hood for $100.
    I used a light weight flow hood on a try out basis. Contact the vendor and ask about doing that.
    The weight of a flow hood was not the most important thing to me. How it stacked up to a pitot traverse was.
    No man can be both ignorant and free.
    Thomas Jefferson

  7. #7
    Join Date
    Apr 2020
    Location
    South USA
    Posts
    20
    Post Likes
    Thread Starter
    Maybe $100 was for the air meter only. One of the other techs uses a calibration lab in Oklahoma. I forgot how much they charged, but it was still a lot less than the factory.

    When we get some free time, I'm going to take a few flow hoods to a site, read a branch, and compare it to a traverse. I think the results will be enlightening.

  8. #8
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    4,439
    Post Likes
    I used the Oklahoma lab all the time and was well satisfied with them.

    You should compare the hoods with a pitot. You can check both accuracy and repeatability of the hood. I checked mine with the inclined manometer because it is more accurate than the high dollar electronic meters. Give it time to adjust to the room temperature because that and being level is the only thing you have to worry about.
    No man can be both ignorant and free.
    Thomas Jefferson

  9. #9
    Join Date
    Mar 2020
    Posts
    2
    Post Likes
    Quote Originally Posted by RobertStephens View Post
    There might be something wrong with our Shortridge hood. I've been getting extremely high airflow measurements, especially on smaller grilles. The flow baffles and grid are not quite in alignment, but I don't know how it would affect it that much. The meter works fine, with current calibration.

    I'm not very motivated to try to fix it. It's so bulky and hard to use compared to the new hood.
    The grid has some small wire spring things that secure it to the hood body, if the grid is not in the proper position, it will greatly affect your readings. Shortridge sells replacement spring thingy fairly cheap, I have had to replace them many times because of people trying to carry the hood by the velgrid attachment.

  10. #10
    Join Date
    Mar 2020
    Posts
    2
    Post Likes
    As Wayne mentioned, measurements that can reasonably match up with a pitot tube traverse are what makes a flowhood reliable. I have used the dwyer and evergreen hood, both were nice and made things easier but were not as reliable in my opinion as the shortridge. Alnor has also been reliable the few times I used it.

  11. #11
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    9,681
    Post Likes
    I'm not sure about using a calibration shop other than factory for flow hoods ( digital). Reason the last time I checked the factory also upgraded the firm ware. Maybe other companies can too but it seems not likely they would have the ability to know the upgrade.
    Other measuring devices would be easier.
    Give me a relay with big enough contacts, and I'll run the world!

    You can be anything you want......As long as you don't suck at it.

    If a person wants to create a machine that will be more likely to fail...Make it complicated.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  12. #12
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,559
    Post Likes
    I measured my return grille last weekend with a TEC flow grid on a DG-1000, and cpm[ared to a Testo flow hood. They both measured exactly 759 CFM. I had expected some difference but was impressed that they both read the same.

    BTW, cleaning the blower wheel as it was a little dusty, certainly not loaded, increase air flow to 1049 CFM.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  13. #13
    Join Date
    Nov 2004
    Location
    Northern Calif
    Posts
    48
    Post Likes
    Quote Originally Posted by kdean1 View Post
    BTW, cleaning the blower wheel as it was a little dusty, certainly not loaded, increase air flow to 1049 CFM.
    Man, I would have loved to see the before and after pics of the wheel, that is a significant gain.

  14. #14
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    4,439
    Post Likes
    In reference to your post #5 Robert Ernie Shortridge did pass away. I really liked and respected him. He would tell you to the smallest detail about anything you ask. I talked to him several times and never got the run around. I don't know how they are doing now.
    Too high airflow measured with a flow hood is usually leaking sensor hoses or on the grid somewhere.
    No man can be both ignorant and free.
    Thomas Jefferson

  15. #15
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,559
    Post Likes
    Quote Originally Posted by dieseldude View Post
    Man, I would have loved to see the before and after pics of the wheel, that is a significant gain.
    Here you go.

    I didn't bother with an after pic.

    I hope the picture loads from my photo album. I didn't see it included when I made the post.




    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •