    Trane 2007 heat pump RTU piping understanding wanted

    I'm trying to understand the refrigeration flow of a 2007, Trane heat pump RTU, model WSC060A3R..
    It has a one direction drier, so the drier is only operative in heat. The check valve branches off the distributor and looks like it goes back into the condenser. What is the logic of this? I would like to find a diagram of the flow.
    I recently had a unit with a failed compressor and check valve. I have heard it is good to replace the check valve with the compressor, I think I will do that from now on, so I don't have to recover twice. Alas.

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,251
    Post Likes
    Quote Originally Posted by mccann View Post
    I'm trying to understand the refrigeration flow of a 2007, Trane heat pump RTU, model WSC060A3R..
    It has a one direction drier, so the drier is only operative in heat. The check valve branches off the distributor and looks like it goes back into the condenser. What is the logic of this? I would like to find a diagram of the flow.
    I recently had a unit with a failed compressor and check valve. I have heard it is good to replace the check valve with the compressor, I think I will do that from now on, so I don't have to recover twice. Alas.
    Check your email.
    Instead of learning the tricks of the trade, learn the trade.

  3. Likes mccann liked this post.
  4. #3
    Join Date
    Apr 2008
    Location
    Tucson, AZ
    Posts
    331
    Post Likes
    Thread Starter
    Interesting. That the check valve takes the liquid into the condenser for one more loop. Do they do that to subcool it, or just to confuse me? So it looks like in cooling, the check valve screen is the filter. The drier is just for in heating. hmmm.
    Last edited by mccann; 06-28-2020 at 01:16 PM.

  5. #4
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Not sure about your particular unit but lots of different condensers have sub cooling loops on them.

    Sent from my SM-G965W using Tapatalk

  6. Likes mccann liked this post.
  7. #5
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,251
    Post Likes
    Quote Originally Posted by mccann View Post
    Do they do that to subcool it, or just to confuse me?
    The answer to that question is above my pay grade - sorry.
    Instead of learning the tricks of the trade, learn the trade.

  8. Likes BALloyd liked this post.
  9. #6
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Quote Originally Posted by mccann View Post
    Do they do that to subcool it, or just to confuse me?
    Quote Originally Posted by rundawg View Post
    The answer to that question is above my pay grade - sorry.
    Little bit of this, little bit of that maybe?

    Sent from my SM-G965W using Tapatalk

  10. #7
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Quote Originally Posted by mccann View Post
    Interesting. That the check valve takes the liquid into the condenser for one more loop. Do they do that to subcool it, or just to confuse me? So it looks like in cooling, the check valve screen is the filter. The drier is just for in heating. hmmm.
    Its been a while since I worked on one of these, but as I recall...the extra loop used for subcooling also gives the extra refrigerant that's not needed in heating mode somewhere to go, like a charge compensator. Its subcooled in cooling mode, and isolated from the circuit in heating mode. I think that's what I remember, anyway.

    I used to work on these fairly often when I did national accounts, and I was thrown by the layout for a few times at first. One stumped me for a long time trying to find the cause of low suction pressure. Of course the drier dutifully had been changed. I knew there was a check valve there, but I didn't know it had a strainer in there, too. Couple of days of frustration until I figured that one out, screen was almost completely blocked. Later I realized you could reach up in there behind the electrical panel and feel that check valve, and if there was a problem, it'd be cold right there.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  11. Likes mccann liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •