    2 evaporators with single LLSV

    When we have 2 evaporators in a WI cooler where each evaporator has it's own TXV, why is it a bad idea to put a single liquid line solenoid valve?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Who says it’s bad.

    You will have to control the frost downstream but that’s easy.

  3. Likes BobFrost liked this post.
  4. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    I've never heard that it was bad either. I've put them on top of the box before, and then bull-head teed to both evaps while trying to keep the pipe distances as close to equal as possible. I thought this was the way they were supposed to be done.

    I've also installed 2 evaps on one system where both of the evaps came with the solenoids already pre-installed, and also 2 thermostats. I think in that case I left the 2 solenoids in there and rigged up the thermostats so that only one of them worked (one stat controlled both solenoids).

    By the way, what's this frost thing you speak of pecmsg? Are you saying the liquid line on the outlet of the solenoid will get cold during pump-down? That's not something I've ever considered before. If that's what you're saying, would you insulate those sections?
    If at First You Don't Succeed, Skydiving Is Not for You.

  5. Likes BobFrost liked this post.
  6. #4
    Join Date
    Feb 2006
    Location
    Austin, Texas
    Posts
    543
    Post Likes
    It is best to have one pump down solenoid and one cold control. I have freeze up problems otherwise

  7. Likes BobFrost liked this post.
  8. #5
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    I have lots of that set up. I used to do a Beverage Barn kinda place that had 5 evaps on 1 LLSV.

  9. #6
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,683
    Post Likes
    No issues at all doing one LLSV, as long as the one valve is rated to flow enough refrigerant for both coils.
    But otherwise it’s very common.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  10. Likes stumpdigger liked this post.
  11. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by ammoniadog View Post
    I've never heard that it was bad either. I've put them on top of the box before, and then bull-head teed to both evaps while trying to keep the pipe distances as close to equal as possible. I thought this was the way they were supposed to be done.

    I've also installed 2 evaps on one system where both of the evaps came with the solenoids already pre-installed, and also 2 thermostats. I think in that case I left the 2 solenoids in there and rigged up the thermostats so that only one of them worked (one stat controlled both solenoids).

    By the way, what's this frost thing you speak of pecmsg? Are you saying the liquid line on the outlet of the solenoid will get cold during pump-down? That's not something I've ever considered before. If that's what you're saying, would you insulate those sections?
    On rear occasions I’ve seen it happen. Armorflex takes care of it!

  12. #8
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    I was taught the length of the liquid line should be equal from the solenoid to either metering device.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  13. #9
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    As mentioned should not be a problem as long as the solenoid is sized right for the flow of both TEVs and the liquid line after the solenoid are equal in length , as well as the suction lines.
    Try to run the liquid line into the tee on the bullhead , if on the run one valve may not get the same amount of gas. After the TEV that’s on the run starts to pinch off then the valve on the bullhead can get enough gas the pinch back as well. That’s when they start to screw with each other especially if low on charge. Also need to have enough room in the CDU for pump down. Long suction lines and long line after the solenoid may cause high trip during pump down.


    Sent from my iPhone using Tapatalk

  14. #10
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    depends how far apart really, for medium temp I dont see an issure , for low temp you would need to stage the defrosts I think
    Keep it simple to keep it cool!

  15. #11
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    Last heatcraft class I attended, the equal pipe length thing was scoffed at.
    As long as there is not a huge amount of piping friction difference, it really doesnt matter.


    Sent from my SM-G950U using Tapatalk

  16. Likes BobFrost, icemeister liked this post.
  17. #12
    Join Date
    Jan 2019
    Location
    EU
    Posts
    76
    Post Likes
    Thread Starter
    Hi guys, thanks for a lot of useful replies.

    Quote Originally Posted by pecmsg View Post
    Who says it’s bad.
    Quote Originally Posted by ammoniadog View Post
    I've never heard that it was bad either.
    I've been told this on couple of occasions without explanation why it would be bad.
    Luckily, there is hvac-talk to clear thing out.


    By reading these posts here, I come to conclusion that it's easier to put 2 solenoids (for 2 evaporators) instead of watching out for equal pipe lengths.

  18. #13
    Join Date
    Jan 2019
    Location
    EU
    Posts
    76
    Post Likes
    Thread Starter
    Quote Originally Posted by rickl View Post
    It is best to have one pump down solenoid and one cold control. I have freeze up problems otherwise
    Can you explain it a bit? What causes this freeze up?

  19. #14
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    1,345
    Post Likes
    When each coil has its own LLSV and stat, the first stat could call for cooling and keep the temp low enough to prevent the second stat from closing. With only one coil cooling it will have a very long run time in order to satisfy that stat and will freeze up.

    I have units that are setup both ways. One specific unit, a 2 system/
    4 evap coil at a C-store isn’t stocked very well and the air doesn’t turn over very well on one end. The coil on the far would freeze up simply because it was so much colder on that side. In that situation I added a second stat so essentially each CU had its own control.

    Depending on the type of system and how it’s used both ways can work. More commonly the single stat and LLSV is the way to go.

  20. #15
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Two or more solenoids with single condensing unit can cause oil management issues if suction piping is not self draining/returning from both evaps. Typically I prefer seeing a single llsv.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •