Try setting your IP network number to 0.
I've got an Automated Logic site with 11 LGRs, each with an ARCnet segment under it.
I'm trying to discover the ALC controllers in a soft JACE.
If I manually add an LGR to the router table, I can then manually add a controller from that network, and it will let me discover points. But I haven't discovered a single controller.
My usual tricks are to register the JACE as a foreign device, or set it up as a BBMD, but neither has made a difference.
I'm using BACnet IP on the JACE, with a unique Device ID, and the IP network number set to 2400 (I also tried 1 and 2).
What am I missing?
LGRs:
Example Controllers:
The soft JACE's IP info:
IPv4 Address. . . . . . . . . . . : 192.168.8.46
Subnet Mask . . . . . . . . . . . : 255.255.248.0
Default Gateway . . . . . . . . . : 192.168.15.254
Try setting your IP network number to 0.
"It's not that I'm smart, it's that I stay with the problem longer
Albert Einstein
Tried net 0, the JACE rejects it and goes into fault.
Can WebCTRL discover the Jace?
Controls, the cause of... and solution to... all your HVAC problems.
One phone call is worth a thousand emails.
Review network subnets and BBMD tables, everyone gets the same table. Match whatever the WebCTRL network number is at IP level.