    I am working on a walk in cooler condenser and the contactor coil keeps failing. It was short cycling so I put a TDOB relay wired between low pressure switch and contactor coil. But now the coil on the contactor keeps failing on contactor not sure what is causing this I removed the TDOB for now . I guess I need to replace the solenoid valve so it will pump down and stay there it must be leaking .

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Why was it short cycling?

  3. #3
    Join Date
    Oct 2002
    Location
    Southeast Ohio
    Posts
    517
    Post Likes
    Thread Starter
    solenoid valve is leaking during shut down

  4. #4
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Does it have an adjustable low pressure switch? If so, can you widen the differential? Since Ohio is a relatively warm state, you should be able to get by with a higher cut-in than what I would be able to get away with here in Minnesota.

    Try adjusting it so it cuts out at about 5psi, and cuts in around a saturated suction pressure/temperature of about whatever the lowest outdoor temperature is that the thing will see. If this happens to be an indoor condensing unit then you can set the differential even wider to cut in at a saturated pressure/temperature of about 40°F.

    As pecmsg said, what's making it short cycle? I kind of doubt it's you solenoid, although it is a possibility. Another possibility would be weak suction valves if it has a reciprocating compressor, or a leaking internal compressor check valve if it's a scroll. If it's a scroll, it's also somewhat common for the thing to "burp" after it pumps down, which can cause a viscous cycle of short cycling too, which can sometimes be helped by widening the low pressure switch differential, or adding the time delay relay.
    If at First You Don't Succeed, Skydiving Is Not for You.

  5. #5
    Join Date
    Oct 2002
    Location
    Southeast Ohio
    Posts
    517
    Post Likes
    Thread Starter
    It is possible the valves in compressor is leaking I haven't tried closing the valve on liquid line to see for sure which is leaking. The pressure switch is fixed. I'm going to order one with a wider range. But I still don't understand why TDOB relay is doing what it is.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •