    Not blowing cold air

    Lennox system.
    Put gauges on and not getting a reading on the low side. High side is 50psi.
    Sub cooling at 2.
    Is it possible for the unit to be low on Freon without freezing up?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    What does zero low and 50 high tell you?

  3. #3
    Join Date
    Jun 2020
    Posts
    6
    Post Likes
    Thread Starter
    No refrigerant

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Dezzzy View Post
    Lennox system.
    Put gauges on and not getting a reading on the low side. High side is 50psi.
    Sub cooling at 2.
    Is it possible for the unit to be low on Freon without freezing up?
    How did you get 2° SC at 50#'s operating pressure?

  5. #5
    Join Date
    Jun 2020
    Posts
    6
    Post Likes
    Thread Starter
    I’m sorry I meant to put 0 for the sub cooling.

  6. #6
    Join Date
    Jun 2020
    Posts
    6
    Post Likes
    Thread Starter
    I’m sorry I meant to put 0 for the sub cooling.

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes

  8. #8
    Join Date
    Jun 2020
    Posts
    6
    Post Likes
    Thread Starter
    Lennox heat pump(410a) not blowing cool air.
    Compressor, fan and blower operating at normal amps. Return air is 78 supply air is 74. Pressures are reading 0/50 psi. No sub cooling. No ice on the coils. Leak detector is going off at the Evaporator coil.
    My question is the unit contains low pressure switches so if the pressures are low then why it’s not cutting the compressor off.
    Second question, the control board have the red and green light that lets you know how the unit is operating. According to the legend the unit is operating normal.

  9. #9
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    5,120
    Post Likes
    Time to get a tech out there to look at it!

    Sent from my SM-G960U using Tapatalk
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Dezzzy View Post
    Lennox heat pump(410a) not blowing cool air.
    Compressor, fan and blower operating at normal amps. Return air is 78 supply air is 74. Pressures are reading 0/50 psi. No sub cooling. No ice on the coils. Leak detector is going off at the Evaporator coil.
    My question is the unit contains low pressure switches so if the pressures are low then why it’s not cutting the compressor off.
    Second question, the control board have the red and green light that lets you know how the unit is operating. According to the legend the unit is operating normal.
    Your profile states "Contractor"

    Nothing you've said tells me your remotely qualified to be working on this equipment!

    If you are in the field then Pleas be careful. No jumping out of safety's. No pushing in contractors.

  11. Likes JayMan7 liked this post.
  12. #11
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Your profile states "Contractor"

    Nothing you've said tells me your remotely qualified to be working on this equipment!

    If you are in the field then Pleas be careful. No jumping out of safety's. No pushing in contractors.
    Was that on purpose ? Funny in any case.
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  13. Likes pecmsg liked this post.
  14. #12
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    5,120
    Post Likes
    Quote Originally Posted by Cagey57 View Post
    Was that on purpose ? Funny in any case.
    Hahaha good catch

    Sent from my SM-G960U using Tapatalk
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  15. #13
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Cagey57 View Post
    Was that on purpose ? Funny in any case.

  16. #14
    Join Date
    Jun 2020
    Posts
    6
    Post Likes
    Thread Starter
    Thank you for the response. Gentlemen have a nice night.

  17. Likes JayMan7 liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •