    5 ton 120k BTU furnace. 2 year old house
    HO has pretty low airflow through the registers, everything seems to be sized properly on the main branches for supply and return, but there's around 24 supplies in this home all with 6" round and 4x12 registers, and the return is all properly sized up above, but when it transitions into the return 90 at the unit, it tapers way down (I'm guessing because there is a clean out in the way). It, also has a 12 inch round return for the basement on the other side of the furnace not in the picture. I'm wondering if this place has too many registers or if this trainsition on the return could be the culprit, any thoughts?
    The airflow at the registers seems okay but it definently feels less than normal. It's pretty loud when it runs too. Thanks!
    Jan 2012
    Broomall, PA
    Any measurements made, TESP, airflow, etc.?
    If I do a job in 30 minutes it's because I spent 30 years learning how to do that in 30 minutes. You owe me for the years, not the minutes.
    Jun 2002
    nw ohio
    Let me guess.
    This system has always had low airflow because it was designed to have low airflow.
    Return air should enter a 5-ton upflow blower from both sides of the blower compartment
    or through the bottom of the blower compartment.
    Unless there's another return on the right side of the furnace that I can't see...
    I've already been wrong six or seven times today!
    "Compressors never die; they're always murdered!" - Glenn Hannegan Jr
  4. Likes Metalman0880, DOGBOY, kdean1 liked this post.
  5. #4
    Jul 2019
    Montana
    Quote Originally Posted by Spide View Post
    Let me guess.
    Yep 12 inch round on the other side basically 90s straight into the return grill downstairs with a 16x20x1
    The pictures filter is 16x25x1
  6. #5
    Jun 2002
    nw ohio
    Is the only problem low airflow from the supply diffusers?
    The owner wants to feel the air coming out of the vents?
    What did the owner say the problem is??
  7. #6
    Jul 2019
    Montana
    They're ac leaks refrigerant so it was a no cooling call, but theyre side complaint was airflow, theyre up and running now with the leak fixed
  8. #7
    Jun 2002
    nw ohio
    What was wrong with the airflow according to the owner?
    What criteria was the owner using to determine he has low air flow?
  9. #8
    Nov 2011
    CO
    what spiderman said!! not enough return, should be both sides or the bottom. should be wording for that in the manual.
  10. #9
    Feb 2016
    Louisburg Kansas
    With 24 diffusers airflow per diffuser will probably be less than 100 CFM even with no duct problems. If the house cools properly there is no reason to worry about the airflow per grille. With that many diffusers the loud noise is most likely in one area. That appears to be at the furnace return. That doesn't necessarily mean mods have to be made to the duct to get enough airflow. The noise is whatever the owner can tolerate as long as flow isn't overly restricted.
    Thomas Jefferson
  11. #10
    Oct 2011
    Culver, Oregon (Central OR)
    Quote Originally Posted by 71CHOPS View Post
    It does have return on the other side.
  12. #11
    Jul 2018
    NW Louisiana
    OK, my question is, the return duct gets narrower and then goes into the 90* then into the unit, Is this normal in some areas? All of the systems here that I work on, the return doesn't reduce down like that, even the commercial systems, unless they split off, and I am pretty sure, when you restrict the airflow, the system gets louder also.
  13. #12
    Jun 2013
    Toronto, Ontario
    Quote Originally Posted by 406Tinner View Post
    If all it’s going on for return air besides that single undersize boot is a 12” round sucking air from one room then I would say that is probably no beuno, needs a bottom return box and a much bigger boot to meet spec
  14. #13
    Athens, Ohio
    One inch pleated air filter?
    Check static pressure and velocity.
    AOP Rules: Rules For Equipment Owners.
    Free online load calculator: http://www.loadcalc.net/
    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."
  15. #14
    Mar 2011
    London Ky.
    Have you explained it don't have to peel the paint off the walls to work right ???
  16. #15
    Atlanta GA area
    Definitely NOT enough return...
    24 x 6: supplies... is somewhere in the 1750-1800 CFM's area... a little light for 5 tons... however enough to have good aiflow... IF there was enough air to flow...
    As noted earlier... 5 tons of airflow needs either both sides or one side + bottom inlet!
    You will need to talk them into one of those return plenums that raises the furnace about 10-12" off the floor... and feeds air into both the bottom and the side.
    AND... the smallest filter you can use... is 20x25x1...
    A 20x25x4 or 5 media would be better!
    GA-HVAC-Tech
    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!