    Question

    5 ton 120k BTU furnace. 2 year old house
    HO has pretty low airflow through the registers, everything seems to be sized properly on the main branches for supply and return, but there's around 24 supplies in this home all with 6" round and 4x12 registers, and the return is all properly sized up above, but when it transitions into the return 90 at the unit, it tapers way down (I'm guessing because there is a clean out in the way). It, also has a 12 inch round return for the basement on the other side of the furnace not in the picture. I'm wondering if this place has too many registers or if this trainsition on the return could be the culprit, any thoughts?
    The airflow at the registers seems okay but it definently feels less than normal. It's pretty loud when it runs too. Thanks!
    Attached Images Attached Images  

  2. #2
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    4,743
    Post Likes
    Any measurements made, TESP, airflow, etc.?
    If I do a job in 30 minutes it's because I spent 30 years learning how to do that in 30 minutes. You owe me for the years, not the minutes.

    Helpful Calcs, tips, tricks on my YouTube channel: https://www.youtube.com/channel/UCgm...TUTAdKmqRiTDEg

  3. #3
    Join Date
    Jun 2002
    Location
    nw ohio
    Posts
    257
    Post Likes
    Let me guess.
    This system has always had low airflow because it was designed to have low airflow.

    Return air should enter a 5-ton upflow blower from both sides of the blower compartment
    or through the bottom of the blower compartment.

    Unless there's another return on the right side of the furnace that I can't see...
    I've already been wrong six or seven times today!
    "Compressors never die; they're always murdered!" - Glenn Hannegan Jr

  4. Likes Metalman0880, DOGBOY, kdean1 liked this post.
  5. #4
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    260
    Post Likes
    Thread Starter
    Quote Originally Posted by Spide View Post
    Let me guess.
    This system has always had low airflow because it was designed to have low airflow.

    Return air should enter a 5-ton upflow blower from both sides of the blower compartment
    or through the bottom of the blower compartment.

    Unless there's another return on the right side of the furnace that I can't see...
    I've already been wrong six or seven times today!
    Yep 12 inch round on the other side basically 90s straight into the return grill downstairs with a 16x20x1
    The pictures filter is 16x25x1

  6. #5
    Join Date
    Jun 2002
    Location
    nw ohio
    Posts
    257
    Post Likes
    Is the only problem low airflow from the supply diffusers?
    The owner wants to feel the air coming out of the vents?
    What did the owner say the problem is??
    "Compressors never die; they're always murdered!" - Glenn Hannegan Jr

  7. #6
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    260
    Post Likes
    Thread Starter
    Quote Originally Posted by Spide View Post
    Is the only problem low airflow from the supply diffusers?
    The owner wants to feel the air coming out of the vents?
    What did the owner say the problem is??
    They're ac leaks refrigerant so it was a no cooling call, but theyre side complaint was airflow, theyre up and running now with the leak fixed

  8. #7
    Join Date
    Jun 2002
    Location
    nw ohio
    Posts
    257
    Post Likes
    What was wrong with the airflow according to the owner?
    What criteria was the owner using to determine he has low air flow?
    "Compressors never die; they're always murdered!" - Glenn Hannegan Jr

  9. #8
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,434
    Post Likes
    what spiderman said!! not enough return, should be both sides or the bottom. should be wording for that in the manual.

  10. #9
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    With 24 diffusers airflow per diffuser will probably be less than 100 CFM even with no duct problems. If the house cools properly there is no reason to worry about the airflow per grille. With that many diffusers the loud noise is most likely in one area. That appears to be at the furnace return. That doesn't necessarily mean mods have to be made to the duct to get enough airflow. The noise is whatever the owner can tolerate as long as flow isn't overly restricted.
    No man can be both ignorant and free.
    Thomas Jefferson

  11. #10
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    Quote Originally Posted by 71CHOPS View Post
    what spiderman said!! not enough return, should be both sides or the bottom. should be wording for that in the manual.
    It does have return on the other side.

  12. #11
    Join Date
    Jul 2018
    Location
    NW Louisiana
    Posts
    468
    Post Likes
    OK, my question is, the return duct gets narrower and then goes into the 90* then into the unit, Is this normal in some areas? All of the systems here that I work on, the return doesn't reduce down like that, even the commercial systems, unless they split off, and I am pretty sure, when you restrict the airflow, the system gets louder also.

  13. #12
    Join Date
    Jun 2013
    Location
    Toronto, Ontario
    Posts
    131
    Post Likes
    Quote Originally Posted by 406Tinner View Post
    Yep 12 inch round on the other side basically 90s straight into the return grill downstairs with a 16x20x1
    The pictures filter is 16x25x1
    If all it’s going on for return air besides that single undersize boot is a 12” round sucking air from one room then I would say that is probably no beuno, needs a bottom return box and a much bigger boot to meet spec

  14. #13
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    One inch pleated air filter?
    Check static pressure and velocity.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  15. #14
    Join Date
    Mar 2011
    Location
    London Ky.
    Posts
    27
    Post Likes
    Have you explained it don't have to peel the paint off the walls to work right ???

  16. #15
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    Definitely NOT enough return...

    24 x 6: supplies... is somewhere in the 1750-1800 CFM's area... a little light for 5 tons... however enough to have good aiflow... IF there was enough air to flow...

    As noted earlier... 5 tons of airflow needs either both sides or one side + bottom inlet!

    You will need to talk them into one of those return plenums that raises the furnace about 10-12" off the floor... and feeds air into both the bottom and the side.

    AND... the smallest filter you can use... is 20x25x1...
    A 20x25x4 or 5 media would be better!
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •