    I installed it not long ago ( less than 6 months ) after changing the compressor here at the shop. It started the error about month after, though less frequently. Now it's every time they go to get ice from it. It's level and clean. But I am going to go ahead and clean / descale it to eliminate that as a problem.

  2. #22
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    3,404
    Post Likes
    Possibly a sticking hot gas valve.

    Usually excessive harvest time is due to dirty evap or one that is losing the nickle plating. But that would be a continuing problem. Does this model have a air pump assist? If so, take a look at that as well.
    “A dying culture invariably exhibits personal rudeness. Bad manners. Lack of consideration for others in minor matters. A loss of politeness, of gentle manners, is more significant than is a riot.”
    ― Robert A. Heinlein

  3. #23
    Join Date
    May 2020
    Location
    New Orleans
    Posts
    53
    Post Likes
    Thread Starter
    Quote Originally Posted by Juan Madera View Post
    Possibly a sticking hot gas valve.

    Usually excessive harvest time is due to dirty evap or one that is losing the nickle plating. But that would be a continuing problem. Does this model have a air pump assist? If so, take a look at that as well.
    I've dealt with the nickle plating issue multiple times in the past. This evaps plating is in excellent condition and it's apparently very clean. I'm not familiar with air assist. I assume it's to help the fall ice off the evap. I didn't see anything like that on the unit nor in the manual. I'll look though.

  4. #24
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,748
    Post Likes
    Quote Originally Posted by Accurate AC View Post
    Got ya. Thanks
    That's a basic machine and the manual covers almost all situations! LED flickering means there getting a signal to Open/Close

  5. #25
    Join Date
    Mar 2018
    Posts
    34
    Post Likes
    Quote Originally Posted by Accurate AC View Post
    Every time when I arrive I find the machine shut down on a harvest error. Every time I retrieved the code and I reset the power it operates perfectly. Production time is less than 20 min per drop. Harvest time is correct. Bridge thickness is perfect. Pressures are good in production and harvest ( so far as my experience and research tells me ). The water system is super clean. The evaporator nickle plating is in great shape. The water supply / filter is new with good pressure on the filter gauge. The ice drops evenly with no hang ups. I'm hoping someone here has experience they can share with me to help me get this issue solved. I appreciate you help.
    Quote Originally Posted by Accurate AC View Post
    I installed it not long ago ( less than 6 months ) after changing the compressor here at the shop. It started the error about month after, though less frequently. Now it's every time they go to get ice from it. It's level and clean. But I am going to go ahead and clean / descale it to eliminate that as a problem.
    Sounds like a refurb if you changed the compressor and resold it. You guys likely didn't find the issue that took out the original compressor, and have an intermittent issue. I play a daily game with the old SY300 in the shop I run, typically I find the pump running but not actually pumping water, calcium build up usually preventing the actuator from spinning and moving water. If I'm not mistaken, the safety indication for long harvest and long freeze time are the same safety code on those units. So you could have one or the other, or both issues.

    You need to spend a couple hours watching it to see when the issue happens. Get a stopwatch or any timing device, record the pre-chill, water-fill, freeze time, and harvest time for at least 5 consecutive batches. Take note of any irregularities in ice formation on the plate, differences in thickness, harvest times, etc...

    While you are watching, run some simple electrical tests to ensure proper voltage to all components

    If you get 5 straight batches of ice with zero issues and consistent timing on the batches, just inform them the issue is intermittent and replacing the ice machine is probably the best option.

    A small undercounter unit like the one you are working on is only about $1500-2000 to replace brand new, and other than the water line and drain all you have to do is plug it in.

  6. #26
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by VectorTech View Post
    Sounds like a refurb if you changed the compressor and resold it. You guys likely didn't find the issue that took out the original compressor, and have an intermittent issue. I play a daily game with the old SY300 in the shop I run, typically I find the pump running but not actually pumping water, calcium build up usually preventing the actuator from spinning and moving water. If I'm not mistaken, the safety indication for long harvest and long freeze time are the same safety code on those units. So you could have one or the other, or both issues.

    You need to spend a couple hours watching it to see when the issue happens. Get a stopwatch or any timing device, record the pre-chill, water-fill, freeze time, and harvest time for at least 5 consecutive batches. Take note of any irregularities in ice formation on the plate, differences in thickness, harvest times, etc...

    While you are watching, run some simple electrical tests to ensure proper voltage to all components

    If you get 5 straight batches of ice with zero issues and consistent timing on the batches, just inform them the issue is intermittent and replacing the ice machine is probably the best option.

    A small undercounter unit like the one you are working on is only about $1500-2000 to replace brand new, and other than the water line and drain all you have to do is plug it in.
    A typical S problem is a dirty water level probe intermittently causing no water hence no pumping. Pull the trough out and pull the water level probe straight down and disconnect. Clean the metal and the plastic inside and out around the sensor. If you thing the pump is stalling on trash you can pull the pump out the same way and soak the pump part in cleaner.

  7. Likes Accurate AC liked this post.
  8. #27
    Join Date
    May 2020
    Location
    New Orleans
    Posts
    53
    Post Likes
    Thread Starter
    Quote Originally Posted by VectorTech View Post
    Sounds like a refurb if you changed the compressor and resold it. You guys likely didn't find the issue that took out the original compressor, and have an intermittent issue. I play a daily game with the old SY300 in the shop I run, typically I find the pump running but not actually pumping water, calcium build up usually preventing the actuator from spinning and moving water. If I'm not mistaken, the safety indication for long harvest and long freeze time are the same safety code on those units. So you could have one or the other, or both issues.

    You need to spend a couple hours watching it to see when the issue happens. Get a stopwatch or any timing device, record the pre-chill, water-fill, freeze time, and harvest time for at least 5 consecutive batches. Take note of any irregularities in ice formation on the plate, differences in thickness, harvest times, etc...

    While you are watching, run some simple electrical tests to ensure proper voltage to all components

    If you get 5 straight batches of ice with zero issues and consistent timing on the batches, just inform them the issue is intermittent and replacing the ice machine is probably the best option.

    A small undercounter unit like the one you are working on is only about $1500-2000 to replace brand new, and other than the water line and drain all you have to do is plug it in.
    According to the service manual the safety indication for long harvest ( Harvest time exceeds 3.5 minutes for 3 consecutive harvest cycles ) is two blinks of the red LED. Long freeze time ( Freeze time exceeds 60 minutes for 3 consecutive freeze cycles ) in one blink.

    That being said I never checked the water level sensor nor watched it on site for as long as you suggest. It is something I plan on doing after I gather all the info / advice I can. I did run it here at the shop for 48 hours ( and timed freeze and harvest for about 8 hours ) with no faults.

    Unfortunately it was repaired for sale to a friend at slightly above cost so that means "lifetime warranty". This is why one should never sell anything to a friend - LOL. I will be sitting with it for several hours, logging data and, if I don't find the fault, post the data here.

  9. #28
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    If it shut down on a error the code is stored in memory for a period of time.
    From off watch for the code before the machine restarts after you turn the power switch on.

  10. #29
    Join Date
    May 2020
    Location
    New Orleans
    Posts
    53
    Post Likes
    Thread Starter
    Quote Originally Posted by itsiceman View Post
    If it shut down on a error the code is stored in memory for a period of time.
    From off watch for the code before the machine restarts after you turn the power switch on.
    I did. Result = 2 red LED blinks.

  11. #30
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by Accurate AC View Post
    I did. Result = 2 red LED blinks.
    Yes, That's what you wrote in the first post...

    Should I repeat the three things that I wrote that are most likely causing your issue?

  12. #31
    Join Date
    Mar 2018
    Posts
    34
    Post Likes
    Quote Originally Posted by itsiceman View Post
    A typical S problem is a dirty water level probe intermittently causing no water hence no pumping. Pull the trough out and pull the water level probe straight down and disconnect. Clean the metal and the plastic inside and out around the sensor. If you thing the pump is stalling on trash you can pull the pump out the same way and soak the pump part in cleaner.
    You would love to see the unit in this store iceman, I've put a lot of band-aids on it haha. Compressor is still kicking so its not time to replace yet (cost issue, sigh). Water probe housing broke, so a good few wraps of electrical tape and shoving it in place is doing the trick. Left side of curtain mount broke off, so a eyelet screwed into the plastic replaced it. Pump housing also lost a plastic tab, so after cleaning a fresh piece of saran wrap holds that in place. Finally replaced water trough recently, both tabs were gone and self-tappers were the new tabs holding it up.

    15 years old and still running with original compressor ^_^

  13. #32
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    The harvest cycle on the Manatowoc is the point in which the machine is under greatest load. What I find is a combination of a less than perfect evaporator and a worn compressor unable to produce the heat required to warm the backside of the evaporator to allow the sheet of ice to drop. I've tuned them up some when they get to this point which requires adding the slightest amount of refrigerant and carefully watching that head pressure while in the harvest cycle using a stubby gauge. The book calls for 165-180, so pushing it to the max may buy a few months but that's it. It's basically dead. I've never had a compressor flat out die in any of my Manatowocs, only wear out. But make sure the unit is level before going through all of the work. I maintain 22 water cooled units in a large faciilty.

  14. #33
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by Capz View Post
    The harvest cycle on the Manatowoc is the point in which the machine is under greatest load. What I find is a combination of a less than perfect evaporator and a worn compressor unable to produce the heat required to warm the backside of the evaporator to allow the sheet of ice to drop. I've tuned them up some when they get to this point which requires adding the slightest amount of refrigerant and carefully watching that head pressure while in the harvest cycle using a stubby gauge. The book calls for 165-180, so pushing it to the max may buy a few months but that's it. It's basically dead. I've never had a compressor flat out die in any of my Manatowocs, only wear out. But make sure the unit is level before going through all of the work. I maintain 22 water cooled units in a large faciilty.
    I've never add over the factory charge but seen low on charge kill a harvest. I have tilted the machine forward and just raised the head via the water regulating valve to drop ice before for old pump or evap that's in bad shape.

  15. #34
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    Quote Originally Posted by itsiceman View Post
    I've never add over the factory charge but seen low on charge kill a harvest. I have tilted the machine forward and just raised the head via the water regulating valve to drop ice before for old pump or evap that's in bad shape.
    I agree with that.

    I'm referring to the oldest of units, Q models. Typically by the time a compressor is too weak to harvest, it's not producing very good ice either. Adding a slight amount gently decreases the SH assisting the freeze cycle.....but who knows, maybe all i am doing is adding make up gas that may have seeped from schreader valves over the 15 yrs or so.. I get 15 years out of the water cooled units at my facility. No point replacing a compressor, the evap plating is worn off too. Also no point in trying to remove the gas and weighing it. I don't trust the scales for small amounts. I go with the pressure/temp readings, water temp, cycle times and the book. I've brought a few back from the dead which gives us time to order a new one.

  16. #35
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    We still have B water-cooled machines we take care of.
    Those water-cooled last a long time.

  17. #36
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by itsiceman View Post
    We still have B water-cooled machines we take care of.
    Those water-cooled last a long time.
    Still have 12 in them?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  18. #37
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by 2sac View Post
    Still have 12 in them?
    Do we have 12 of them? Maybe
    Do we have 12 in them? No
    Still have 402B in them though

  19. #38
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    I want that itty bitty tank of my truck real bad lol

  20. #39
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    It was olive green if I recall
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  21. #40
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by 2sac View Post
    It was olive green if I recall
    Olive as in I'llive never find it in my truck if I ever need it again but as soon as I take it off I'll need it again.

  22. Likes 2sac liked this post.
+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •