    Thank you WAYNE3298 for starting this thread.
    A lot of interesting discussion has resulted and as this is an extremely common argument in our company I am following the discussion closely.

    I'd like to add my 0.02
    While I disagree with the op It may have some merit in real world systems in my market because 99% of duct systems that I deal with are unsealed often finger jointed attic duct systems so when the system is running it is depressurizing the house and causing more humid air infiltration.

    Sent from my "smart" phone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  2. #42
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    With the same logic which dictates separate AC systems for the first and second floors (which is that the applications are substantially different) - I'd like to mention that the two jobs that need doing are really better off as independent operations.

    For cooling I keep my house at 75º F. and a dehumidifier set to 55%. So long as the cooling units keep the RH below 55% - the dehumidifier doesn't run. If the RH ever tries to increase - the dehumidifier brings it down. Some bear whispered that idea to me - and it really works great. <g>

    I'm not sure - but I think it may cost less to operate as well.

    PHM
    -----------


    Quote Originally Posted by RobertStephens View Post
    I keep my home thermostat at 74 F, which is comfortable, as long as humidity is low.

    But on days like today, with humidity at 80 something %, then 74 F feels too hot. So if I set my upper limit of 70% RH, my system will temporarily decrease the temp setpoint. I assume this is so that a longer run-time would remove more total moisture, so that when the temperature creeps back to 74 F, WB temp and humidity would be lower. I don't know if that makes sense.

    If thermostats are trying to maintain occupant comfort, they should take WB temperature into account, no? Maybe I'm overthinking this
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  3. #43
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Poodle when design is mentioned it is 75 F @ 50% RH. If the space is conditioned UNIFORMLY to that or any other design condition time doesn't matter. That doesn't mean that time is never a factor because to reach design the heat load not only matters it is the controlling factor.

    RobertStevens you are not overthinking this because WB is what it's all about. In commercial applications around here cooling coils are designed for 55 F DB and 55 F WB which is 100% RH. RH of the space can be determined using DB Vs WB.
    No man can be both ignorant and free.
    Thomas Jefferson

  4. #44
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    R600A you make a good point. Designs don't take into account the excess duct leakage you mentioned. That certainly makes the problems worse and if the leakage is as serious as you mentioned everything else becomes a guess.
    No man can be both ignorant and free.
    Thomas Jefferson

  5. #45
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    OK guys I'll confess. The title of this thread even though true was formulated to generate interest in RH and it's control not to reveal anything earth shattering. In my years experience the thing I have seen most misunderstood is relative humidity even with engineers. You guys haven't let me down because this thread has really become interesting.
    I hope you all will keep it going.
    No man can be both ignorant and free.
    Thomas Jefferson

  6. #46
    Join Date
    Apr 2020
    Location
    South USA
    Posts
    28
    Post Likes
    I appreciate everyone illuminating this topic.

    I was reading through a commercial building RTU sequence of operations. If the RH% goes over the setpoint, it will increase cooling and turn on reheat. I guess that's basically the same as a dehumidifier does. I'm not sure about the efficiency.

  7. #47
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    When that happens Robert the concern for comfort overrides efficiency. That is a standard way to dehumidify and works.
    No man can be both ignorant and free.
    Thomas Jefferson

  8. #48
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    3,521
    Post Likes
    Quote Originally Posted by RobertStephens View Post
    I appreciate everyone illuminating this topic.

    I was reading through a commercial building RTU sequence of operations. If the RH% goes over the setpoint, it will increase cooling and turn on reheat. I guess that's basically the same as a dehumidifier does. I'm not sure about the efficiency.
    At the government site there are places that efficiencies don't count. When %RH is over "X" the BAS throws the chilled water valve wide open. Then it tempers the supply air with the downstream HW coil. This will suck down %RH pretty quick. I have even seen this done with electric reheat...
    SOP
    Life is too short, Behappy!
    TFMM

  9. #49
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Okay, I'm still a bit confused. I have a LOT of experience with controlling humidity, but not for comfort cooling. Those were environmental chambers. So as such, the amount of refrigeration for the 'conditioned space' would far exceed the amount of refrigeration for comfort cooling, at least on a cubic foot of air.

    Some of these chambers would cycle between hot and cold. Or, between humid and dry. Sometimes at the same temp, other times at varying temps. Depending on what the chamber was designed for, and programming available, sometimes the temp or humidity would ramp from one to another. Other times it was as fast as possible.

    There was no slowing of the air, because then there wouldn't be a uniform temp throughout. And on that note, compared to comfort cooling, based on the cubic feet being treated, the airflow in an environmental chamber would far exceed that for comfort cooling.

    Some chambers would use a bare tube coil for the dehum, others would use the same finned coil, but with a regulator to keep the finned coil at 32*C. And as mentioned by others, mechanical cooling runs constant, buffered by some sort of heat to keep the temp at set point.

    Had to say all of the above, to get to the part that I am still a bit confused about.

    With an over driven system like an environmental chamber, temp can be achieved quickly. But the humidity lags and can take awhile. I don't think you could put time as a factor in a calculation for, as stated in the original post, "in the RH equation that relates to time".

    I mean, once the coil is at 32*F, and the "room" temp is met, it can only pull out moisture so fast. I've seen it first hand. Maybe it's because of the [relative] higher air flows compared to comfort cooling. But you can definitely pull down a hot humid box to temp faster than it takes for the humidity to catch up.


    Quote Originally Posted by BBeerme View Post
    Okay, I'm thinking the answer lies here.

    It takes longer to remove the moisture in air than it takes to change the temp of the air.

    If I'm wrong, please tell me why.

    Remember, I live in an area that has none of those concerns. Me just thinks it's interesting to learn these things.
    I do a triple evac with nitro to remove non condensables.

  10. #50
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Cycling between heating and cooling has been used in commercial buildings for HVAC humidity control. For HVAC it's a poor excuse for humidity control but works to an extent. It is usually done when the original design didn't include humidity control and the owner needs it. I only saw a few systems like that and that was done because the cooling coil discharge temperature couldn't get below 55 F.
    No man can be both ignorant and free.
    Thomas Jefferson

  11. #51
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    I've never seen that, but like I said earlier, where I live doesn't really have a humidity problem. Maybe a week a year. Maybe two at the very most; on an outlier.

    I'm still confused on the time factor. How can [or could] it possibly be entered into an equation?

    I mean, you can run the evap saturation a bit below freezing, but beyond that, bigger compressor won't make any difference. Removing humidity takes time. How to calculate is well beyond what I know. I just fix the stuff.


    Quote Originally Posted by WAYNE3298 View Post
    Cycling between heating and cooling has been used in commercial buildings for HVAC humidity control. For HVAC it's a poor excuse for humidity control but works to an extent. It is usually done when the original design didn't include humidity control and the owner needs it. I only saw a few systems like that and that was done because the cooling coil discharge temperature couldn't get below 55 F.
    I do a triple evac with nitro to remove non condensables.

  12. #52
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Time can be used to determine the approximate length of time conditioning the air will take if you know the load and capacity of the equipment. The point I was making is in an HVAC system if the entire conditioned space reaches design (75 F @ 50% RH) the time it takes to do it doesn't matter. The statement although true was made to help generate interest in this thread.
    No man can be both ignorant and free.
    Thomas Jefferson

  13. #53
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    We commonly maintain ambient dew points below 32^F by passing the air through drying wheels that absorb moisture from the air and then are heated to the point were the moisture leaves the air in a regeneration cycle and that heats the wheel to the point were the wheel is dry enough to return to the 32^F dew point air.
    The Munters Dry Cool is an example. This is commonly used in commercial drying of materials in the restoration industry.
    Good thread. Thanks.

    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  14. #54
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    The last Munters unit I balanced was on the roof of a college. I always thought they were good units they were a pain to balance.
    I don't know how reliable they are but they appeared sturdy to me. What say you Teddy Bear?
    No man can be both ignorant and free.
    Thomas Jefferson

  15. #55
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    What stops the coil from removing moisture below a certain temperature? In this case 75º. If the cooling system was removing moisture until the space temperature was 75º - why wouldn't it continue to remove moisture as it continued to cool to below 75º? If the RH reduced on the way down to 75º - why would the moisture content of the air remain the same as it cooled below 75º?

    PHM
    --------------


    Quote Originally Posted by WAYNE3298 View Post
    Post #32 has some excellent points. What happens also is that if a system designed to condition to 75 F @ 50% RH is allowed to cool to below 75 F the RH will increase. If the occupants know this at least some of them think the humidity is uncomfortable. They don't realize the water content of the air hasn't changed. They don't know RH is all about the DB temperature and water content of the air.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  16. #56
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    I think it is due to the RELATIVE part of RH.

    Moisture in the air can remain the same, but the RH changes as the temp changes.


    Quote Originally Posted by Poodle Head Mikey View Post
    What stops the coil from removing moisture below a certain temperature? In this case 75º. If the cooling system was removing moisture until the space temperature was 75º - why wouldn't it continue to remove moisture as it continued to cool to below 75º? If the RH reduced on the way down to 75º - why would the moisture content of the air remain the same as it cooled below 75º?

    PHM
    --------------
    I do a triple evac with nitro to remove non condensables.

  17. #57
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Agreed - but my question is: Why would it stay the same if the cooling system is continuing to remove moisture from the air?

    If the system was removing moisture as it cooled down TO 75º - wouldn't it continue to remove moisture as it cooled to Below 75º?

    How could the moisture content remain the same? Which was what was stated in the post I originally questioned.

    PHM
    -------


    Quote Originally Posted by BBeerme View Post
    I think it is due to the RELATIVE part of RH.

    Moisture in the air can remain the same, but the RH changes as the temp changes.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  18. #58
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Bingo BBeerme. The amount of moisture in the air is indicated by and depends on the temperature of the air discharging the cooling coil. If the cooling coil only discharges air at 55 F at 100% RH the amount of water in that air is fixed even though the room temperature can fall below set point because set point is DB temperature. As BBeerme said that's where the relative part comes in.
    No man can be both ignorant and free.
    Thomas Jefferson

  19. #59
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    Bingo BBeerme. The amount of moisture in the air is indicated by and depends on the temperature of the air discharging the cooling coil. If the cooling coil only discharges air at 55 F at 100% RH the amount of water in that air is fixed even though the room temperature can fall below set point because set point is DB temperature. As BBeerme said that's where the relative part comes in.
    The problem with that is that the discharge temp of the coil will change as return temp and humidity change.

    Sent from my "smart" phone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  20. #60
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    You seem to keep including additional facts as you go along. <g>

    Quote Originally Posted by WAYNE3298 View Post
    Bingo BBeerme. The amount of moisture in the air is indicated by and depends on the temperature of the air discharging the cooling coil.

    (Isn't this a pretty large IF?)

    "If" the cooling coil only discharges air at 55 F at 100% RH the amount of water in that air is fixed even though the room temperature can fall below set point because set point is DB temperature.

    As BBeerme said that's where the relative part comes in.
    What factor of system operation would dictate that the cooling coil would perpetually continue to discharge air at 55º?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  21. Likes R600a liked this post.
+ Reply to Thread
Page 3 of 6 FirstFirst 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •