    Winding resistances jumping

    Hey itís ya favorite HVAC noob here.

    So I got a single phase scroll compressor from the job today. (Itís scrap, we replaced with a new one)

    Instead of throwing it away I brought it home because Iím curious. So when I set the multimeter to ohms and touch any two combinations from common, start, or run the numbers jump. I thought I wasnít getting a good connection so I attached alligator clips from my leads to the terminals and the same thing. Any insight?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,229
    Post Likes
    Yes they do Jump under certain conditions. Scrape the pine or clean with emery cloth. Alligator clips wiggled give a better reading with a standard OHM meter.

    Get a Mega Ohm and play with that on old units.

  3. Likes Sabr7 liked this post.
  4. #3
    Join Date
    Apr 2020
    Location
    Georgia
    Posts
    12
    Post Likes
    Question, is the ohms only jumping at first and then go to OL? Constantly jump? How about from terminals to casing of compressor?

  5. #4
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by Bruce Melton View Post
    Question, is the ohms only jumping at first and then go to OL? Constantly jump? How about from terminals to casing of compressor?
    It jumps normally from some high number to a lower number. I understand thatís because of the inrush of voltage the meter sends out. So after it settles from that it goes to another number and continues to drop and then back up to a different number.

    It never goes to OL. It constantly jumps, yes. From terminals to casing is OL. (I scratched away through the paint to make sure Iím on the metal of the casing)


    Sent from my iPhone using Tapatalk

  6. #5
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Yes they do Jump under certain conditions. Scrape the pine or clean with emery cloth. Alligator clips wiggled give a better reading with a standard OHM meter.

    Get a Mega Ohm and play with that on old units.
    Any recommendations on a megger?


    Sent from my iPhone using Tapatalk

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,229
    Post Likes
    Quote Originally Posted by Sabr7 View Post
    Any recommendations on a megger?


    Sent from my iPhone using Tapatalk
    How much Money do you have?

  8. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,229
    Post Likes
    Quote Originally Posted by Bruce Melton View Post
    Question, is the ohms only jumping at first and then go to OL? Constantly jump? How about from terminals to casing of compressor?
    Too ground should be ZERO always!

  9. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,229
    Post Likes
    A little read on Motors:
    Attached Images Attached Images

  10. Likes Sabr7 liked this post.
  11. #9
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    How much Money do you have?
    $300-500. Sounds like youíre gonna say a fluke..


    Sent from my iPhone using Tapatalk

  12. #10
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Too ground should be ZERO always!

    Well let me try this again..


    Sent from my iPhone using Tapatalk

  13. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,229
    Post Likes
    Quote Originally Posted by Sabr7 View Post

    Well let me try this again..


    Sent from my iPhone using Tapatalk
    Don't worry about megging until you begin to get to compressors or motors that cost 3-5k or more. Not worth it. Basic ohm is all you need.

  14. #12
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,229
    Post Likes
    I'll test with my Fluke...………….If they want more I'll call an independent and take a % of there bill to confirm!

  15. #13
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,858
    Post Likes
    Quote Originally Posted by Sabr7 View Post
    Hey it’s ya favorite HVAC noob here.

    So I got a single phase scroll compressor from the job today. (It’s scrap, we replaced with a new one)

    Instead of throwing it away I brought it home because I’m curious. So when I set the multimeter to ohms and touch any two combinations from common, start, or run the numbers jump. I thought I wasn’t getting a good connection so I attached alligator clips from my leads to the terminals and the same thing. Any insight?


    Sent from my iPhone using Tapatalk
    when you cranked up the new compressor was there any issues ? or did the replacing go smooth