  1. #14
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    786
    Post Likes
    Thread Starter
    Quote Originally Posted by mtsaz100 View Post
    get a tekmate for r22- and the srl8 for 410a. Yes its a pain. I got an h10 instead of the srl8 because I have a cps leak "wanna be" seeker---it finds NOTHING, tekmate- perfect for r22, dtek- perfect for r22, 134A, and ok for 410a, bacharach (ultrasonic)--good for coil leaks and flare leaks, and the h10 pro which is what I use 90% of the time- the other 10% is divided among the others (not the cps). that is the most worthless piece of garbage I have ever used.
    Thanks. Iíve heard some good things about the tekmate


    Sent from my iPhone using Tapatalk

  2. #15
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    786
    Post Likes
    Thread Starter
    Just another random gripe: donít look for a leak after youíve washed the outdoor coil with renewz. Found out the hard way awhile back on a maintenance.

    I usually wash the coil first thing so it has a chance to dry and I can check the charge with a known clean coil. I found the system low and got approval for leak search. Started indoors and sure enough, fin pack leak.

    Checked lineset and when I pulled the top to check the coil and tubing, I couldnít even get the detector inside the cabinet before it started screaming. With some experimenting, some head scratching and some wasted time i figured out it was the cleaner residue on the bottom of the pan. Had to wash it a few more times with the hose and remove all debris before I could check it.


    Sent from my iPhone using Tapatalk

  3. #16
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    823
    Post Likes
    D-Tec Select. Best detector Iíve ever used. If it doesnít beep, there is no leak.

    The only other detector Iíd consider is the H-10.
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  4. #17
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,044
    Post Likes
    The inficon i tried recently did good with the h10 reference bottle. Not near as good as the h10 though in practice.


    Sent from my iPhone using Tapatalk

  5. #18
    Join Date
    Jun 2011
    Location
    michigan
    Posts
    373
    Post Likes
    Quote Originally Posted by GenesisRefrig View Post
    D-Tec Select. Best detector Iíve ever used. If it doesnít beep, there is no leak.

    The only other detector Iíd consider is the H-10.
    Select is horrible. H10pro is great for 22 and ok for 410a.
    Slr8 is great for 410a and horrible on 22.
    The select barely picks up anything compared to those 2

  6. #19
    Join Date
    Aug 2010
    Location
    Living rent free
    Posts
    6,391
    Post Likes
    JB prowler 5000, for the win..

    Sent from my moto g(7) power using Tapatalk
    "If you canít describe what you are doing as a process, you donít know what you are doing." ~ W. Edwards Deming

    All those who wander..are not lost.

    Do NOT..mistake my kindness for weakness.

    The early bird may get the worm..but the second mouse gets the cheese.

  7. #20
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    44,289
    Post Likes
    I have an older H10 (not PRO) I use for R22... seems to be more sensitive to 22 than the newer PRO...

    For 410... use the H10 PRO... seems to wok better on 410.

    Yeah, the H10's are expensive... however they just work!

    Anyone have one of the old H10 plug in models... it is really sensitive to 22... however has to be plugged in and is kinda finicky to work with... got mine years ago from another contractor...
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *Cheap is not good, good is not cheap; however expensive is not a guarantee of quality!
    Choose your contractor wisely!

  8. #21
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    823
    Post Likes
    Quote Originally Posted by kra2y View Post
    Select is horrible. H10pro is great for 22 and ok for 410a.
    Slr8 is great for 410a and horrible on 22.
    The select barely picks up anything compared to those 2
    I must have gotten a rare one, because in 5 years, my D-Tek Select has never missed a leak. I’ve had others, and never trusted them. Too many false alarms. With the Select, if it goes off, there is refrigerant. Every time.
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  9. Likes N2fords liked this post.
  10. #22
    Join Date
    May 2006
    Location
    Deep Southeast
    Posts
    9,579
    Post Likes
    Quote Originally Posted by Achso017 View Post
    Just another random gripe: donít look for a leak after youíve washed the outdoor coil with renewz. Found out the hard way awhile back on a maintenance.

    I usually wash the coil first thing so it has a chance to dry and I can check the charge with a known clean coil. I found the system low and got approval for leak search. Started indoors and sure enough, fin pack leak.

    Checked lineset and when I pulled the top to check the coil and tubing, I couldnít even get the detector inside the cabinet before it started screaming. With some experimenting, some head scratching and some wasted time i figured out it was the cleaner residue on the bottom of the pan. Had to wash it a few more times with the hose and remove all debris before I could check it.


    Sent from my iPhone using Tapatalk
    a lot of leak detectors are set off by Big Blue and other leak detection products. The SLR8 is set off if you breathe in front of the sensor.

    As others have said, the SLR8 works better on 410a. I use the SLR8 for 410 and a TIFZX for R-22.

    Graph from Nathan's report:

    Name:  NATHAN HVAC 2014 Leak detector Graph Only_Marked.png
Views: 134
Size:  197.1 KB
    Dem=Washington Democrat
    dem = the average citizen democrat
    Liberalism refers to a systemically corrupt ideology


    How to apply for Professional Membership

  11. Likes Juan Madera liked this post.
  12. #23
    Join Date
    May 2006
    Location
    Deep Southeast
    Posts
    9,579
    Post Likes
    Dem=Washington Democrat
    dem = the average citizen democrat
    Liberalism refers to a systemically corrupt ideology


    How to apply for Professional Membership

  13. #24
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    786
    Post Likes
    Thread Starter
    Quote Originally Posted by vin lashon View Post
    Wow, great video


    Sent from my iPhone using Tapatalk

  14. #25
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    786
    Post Likes
    Thread Starter
    Thank god for big blue. I had an R22 system with a 3 lb leak today. SLR8 couldnít find anything. Sprayed all the indoor coil copper joints and found a bunch of small leaks with one or two larger ones.

    If I wasnít so broke Iíd go and buy a tekmate. But, Iím broke


    Sent from my iPhone using Tapatalk

  15. #26
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,044
    Post Likes
    H10 nough said


    Sent from my iPhone using Tapatalk

  16. Likes ga-hvac-tech liked this post.