    9k + 9k + 24k = 36k??

    Im not the best at math but I know 9 + 9 + 24 = 42.

    Im tagging along for an install of a multi zone mini split. Two bedrooms having 9k BTU head each and an open space having 24k (and Im fairly new to the trade) but I just want to understand this... why is the condenser at a rating of 36k BTU...?

    Also, after doing the BTU calculations it says we will need 21,600 BTU for the open space. Thats how we got at the 24k number.. is it generally better to scale up or down in choosing the tonnage?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Is a 3.5 ton available in your model ?

  3. #3
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    No, it goes from 3 ton to 4 ton.. weird


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,233
    Post Likes
    Quote Originally Posted by Sabr7 View Post
    I’m not the best at math but I know 9 + 9 + 24 = 42.

    I’m tagging along for an install of a multi zone mini split. Two bedrooms having 9k BTU head each and an open space having 24k (and I’m fairly new to the trade) but I just want to understand this... why is the condenser at a rating of 36k BTU...?

    Also, after doing the BTU calculations it says we will need 21,600 BTU for the open space. That’s how we got at the 24k number.. is it generally better to scale up or down in choosing the tonnage?


    Sent from my iPhone using Tapatalk
    Why does your profile say Contractor?

  5. #5
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    So if it's oversized it will most likely do less dehumidification.

  6. Likes Sabr7 liked this post.
  7. #6
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Why does your profile say Contractor?
    I need to edit that.


    Sent from my iPhone using Tapatalk

  8. #7
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Looks like a chiller tech to me.

  9. #8
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Looks like a chiller tech to me.
    Well I work for a contractor who does plenty of chiller work.. but I think I like working on residential more , whats your preference?


    Sent from my iPhone using Tapatalk

  10. #9
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    So if it's oversized it will most likely do less dehumidification.
    So can I get away with 1.5 instead of 2 ton


    Sent from my iPhone using Tapatalk

  11. #10
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Quote Originally Posted by Sabr7 View Post
    Well I work for a contractor who does plenty of chiller work.. but I think I like working on residential more , whats your preference?


    Sent from my iPhone using Tapatalk
    I'm 80% refrigeration and commercial HVAC. 10% residential & 10% miscellaneous.

  12. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,233
    Post Likes
    My Fujitsu book shows a 9, 9 and 24 to a 42

    Each manufacture is different and specific what with what.


    What brand are you dealing with?

  13. #12
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Quote Originally Posted by Sabr7 View Post
    So can I get away with 1.5 instead of 2 ton


    Sent from my iPhone using Tapatalk
    Who did the load calculations ?

  14. #13
    Join Date
    Aug 2019
    Location
    Maryland
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    My Fujitsu book shows a 9, 9 and 24 to a 42

    Each manufacture is different and specific what with what.


    What brand are you dealing with?
    Daikin, surprisingly
    I guess they have a 3.5.. just not for their mini splits


    Sent from my iPhone using Tapatalk