  1. #27
    Join Date
    May 2019
    Posts
    45
    Post Likes
    Does the compressor ID tag match the cond unit ID tag as far as 1 or 3 phase?

    If somehow a 3 phase compressor ended up in a 1 phase cond unit, and then the replacement was based on the compressor ID tag the problem would repeat itself.

  2. #28
    Join Date
    May 2003
    Location
    USA
    Posts
    216
    Post Likes
    Thread Starter
    Comp model
    ZPD54K5E-PVF130
    208/230 1 Ph
    Actual voltage 239
    Run cap 100mfd, checked at 99.7
    Amps and voltage were checked at contactor.
    Amp Draw is 11
    It does have an unloader but not digital, it's off the scroll head, unit does have HGRH, valve was checked, check valves at reheat coil are in correct direction, all valves were checked and open
    Last edited by rimide; 03-28-2020 at 11:53 AM. Reason: Wrong number

  3. #29
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,661
    Post Likes
    Quote Originally Posted by rimide View Post
    Comp model
    ZPD54K5E-PVF130
    208/230 1 Ph
    Actual voltage 239
    Run cap 100mfd, checked at 99.7
    Amps and voltage were checked at contactor.
    Amp Draw is 11
    It does have an unloader but not digital, it's off the scroll head, unit does have HGRH, valve was checked, check valves at reheat coil are in correct direction, all valves were checked and open
    PVF in that MN#???? Even if it is PFV, that ain't right

  4. #30
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,246
    Post Likes
    Run Cap 100 / 370
    230 1 phase
    60 Hz
    LRA 134
    RLA25.6

  5. #31
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,246
    Post Likes
    Copeland Mobil app calls for 100 / 370
    OPI calls for 80 / 370
    Attached Images Attached Images

  6. #32
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    .
    Attached Images Attached Images  

  7. #33
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,246
    Post Likes
    That still doesn't explain whats going on.

  8. #34
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Agree where's the other numbers asked for ?

  9. #35
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,661
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    PVF in that MN#???? Even if it is PFV, that ain't right
    My mistake(again) I was looking at the 50hz info

  10. #36
    Join Date
    May 2003
    Location
    USA
    Posts
    216
    Post Likes
    Thread Starter
    What other numbers do you need

  11. #37
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Two bad compressors has to be one in a thousand.

  12. #38
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    Quote Originally Posted by rimide View Post
    What other numbers do you need
    Condensing unit if split or package number if RTU.

  13. #39
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,661
    Post Likes
    Just one more thing that IDK about. Why is an unloader used on a digital Scroll when the digital part controls/matches the comp load from 100% down to 10%???