    Angry YLAA Expansion Valve

    Does anyone know why York discontinued the TXV on the YLAA and now changed them to EEV?

    I priced a job in December and they quoted me the TXV at that time, now the customer wants to do the job, the TXV has been discontinued and I've to put in a EEV, on both systems.
    Price has increased about 5 fold

  2. #2
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    7,486
    Post Likes
    Prolly because of the earlier warranty failures.

    Requote the job. When the factory changes the scope of work, all you can do is comply.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,920
    Post Likes
    I didn’t know they discontinued the TXV. Of course, the Danfoss TXVs were junk on their best day.

  4. #4
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    252
    Post Likes
    Thread Starter
    Yep Ill have to re-quote, but its a bit annoying to be honest. I might try local supplier to see if they can get the TXV, but it is likely an OEM part.
    Have any of ye installed the EEV on these chiller as a retrofit?

    Anyway's thanks for the advise guys. Happy St. Patricks day...

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,920
    Post Likes
    Quote Originally Posted by Chillmac View Post
    ...Have any of ye installed the EEV on these chiller as a retrofit?...
    I have . It comes as a kit and is pretty easy except for some miscellaneous copper fittings and insulation you may need. The Sporlan EEVs work very well. The Danfoss EEVs suck and are only slightly better than the Danfoss TXVs.

  6. #6
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    7,486
    Post Likes
    Yeah, careful replacing an OEM TXV with an off the shelf....the manufacturer specific may have a different turn down ratio.

    jay, is york still using danfoss after the warranty failures?

  7. #7
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,920
    Post Likes
    Quote Originally Posted by 71CHOPS View Post
    Yeah, careful replacing an OEM TXV with an off the shelf....the manufacturer specific may have a different turn down ratio.

    jay, is york still using danfoss after the warranty failures?
    I do not know. I wouldn’t put the Danfoss back in anyway.

  8. #8
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    252
    Post Likes
    Thread Starter
    I'll just go with the recommended upgrade.
    Thanks guys.

  9. #9
    Join Date
    May 2016
    Location
    Toronto, CAN
    Posts
    146
    Post Likes
    That funny, I had a ylaa last year that was almost looking like low charge or faulty exv. Talked to factory and they said exv was out and replacement was txv. Went through all the wires and 1 pin wasn't making contact in Molex so easy fix really. That chiller has had a few pins come loose inside Molex', friday unit I guess. Running on r22.

    A new site has 3 ylaa with txv and there has been retrofits of removing OEM txv and installing 2 smaller txv In parallel. Running on 410a at -3c, strange choice but hey I'm no engineer.

  10. #10
    Join Date
    Mar 2005
    Posts
    1,380
    Post Likes
    CAREL exv and drivers very competitive priced and super user friendly to test and tune
    Keep it simple to keep it cool!

  11. #11
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    252
    Post Likes
    Thread Starter
    OEM parts only for this customer.
    Which is fine by me..

  12. #12
    Join Date
    Mar 2005
    Posts
    1,380
    Post Likes
    $£$£
    Keep it simple to keep it cool!

  13. #13
    Join Date
    Jan 2013
    Location
    United Kingdom
    Posts
    293
    Post Likes
    This may help a little

    si0333-1Sporlan Danfoss Retro-fit.pdf

    Regards

  14. Likes stanbyyourword liked this post.
Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR