    Limit Switch Open Error ICP Furance

    Have a customer with a ICP high efficiency furnace, throwing a 4 flashing light code, limit switch open. Here is what I have done so far (most as part of general service):
    Changed 2 x limit switch
    Changed Pressure switch
    Changed ignitor
    Changed flame sensor
    Changed board

    Anyone any ideas with these furnaces as to why it would still throw this code after this?

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Have you made sure polarity is correct , you know , the switch on blower door is hot ( not neutral) and the ground is nice and snug

  3. #3
    Join Date
    Oct 2014
    Location
    Maplewood, Minnesota
    Posts
    1,154
    Post Likes
    Is the limit actually open?
    Did you replace all those things in response to this one error code?
    Are you a technician? If you are you need to contact a more senior tech to show you how to trouble shoot properly. You have replaced everything but motors and heat exchanger, customer would have been better off with a sales tech in this case.

  4. #4
    Join Date
    Mar 2020
    Posts
    2
    Post Likes
    Thread Starter
    The main fan comes
    On when the switch is activated but that is as far as the cycle goes

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Do you know how to test across a safety switch to see if its open or closed ?

    You know its got a couple different high limits ... right

    Some have 3 - 4 of them

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Call A professional

  7. #7
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Limit switch or pressure switch?

    If limit switch why replace a pressure switch?
    Or vise versa?

    Like others said, is the limit actually open? Ohm meter the limits and see if they are open and close.

    After the furnace is off for an hour does the furnace run at all or go right to error code?

    Which limit, roll out or HX high limit?


    Sent from my iPhone using Tapatalk

  8. Likes jmac00 liked this post.
  9. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by The Gaffer View Post
    Have a customer with a ICP high efficiency furnace, throwing a 4 flashing light code, limit switch open.
    Model number please.
    Instead of learning the tricks of the trade, learn the trade.

  10. #9
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    some furnaces have a limit switch on the blower housing, which MANY techs miss.

    someone needs to figure out how to test a safety circuit, instead of loading up the parts cannon
    Why am I the only naked person at this gender reveal party

  11. #10
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    Quote Originally Posted by jmac00 View Post
    some furnaces have a limit switch on the blower housing, which MANY techs miss.

    someone needs to figure out how to test a safety circuit, instead of loading up the parts cannon
    Bingo!! These get missed all the time. Betcha that's what it is.

  12. #11
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Quote Originally Posted by jmac00 View Post
    some furnaces have a limit switch on the blower housing, which MANY techs miss.

    someone needs to figure out how to test a safety circuit, instead of loading up the parts cannon
    Do icp have those? I know that’s a big trane thing.


    Sent from my iPhone using Tapatalk

  13. #12
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    1,301
    Post Likes
    He forgot to change the inducer motor and heat exchanger. I hate when people only replace MOST of the parts. Do the job right, and replace them all. Darn Millennials!
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  14. Likes doc havoc liked this post.
  15. #13
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Quote Originally Posted by The Gaffer View Post
    Have a customer with a ICP high efficiency furnace, throwing a 4 flashing light code, limit switch open. Here is what I have done so far (most as part of general service):
    Changed 2 x limit switch
    Changed Pressure switch
    Changed ignitor
    Changed flame sensor
    Changed board

    Anyone any ideas with these furnaces as to why it would still throw this code after this?
    Wow! That’s getting expensive. Evidently none of those parts were bad. Tell us what you measured instead of what you guessed at.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  16. #14
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    Do icp have those? I know that’s a big trane thing.


    Sent from my iPhone using Tapatalk
    not sure about ICP, ya Trane and Rheem both have them on the blower housing, but it this ICP is a multi-position unit, it should have a limit on the blower housing
    Why am I the only naked person at this gender reveal party

  17. #15
    Join Date
    May 2018
    Location
    Elizabethtown, PA
    Posts
    181
    Post Likes
    Have you actually confirmed that the temp isn't getting too high? Checked the filter/airflow/TESP?

  18. #16
    Join Date
    Mar 2003
    Location
    Scottsburg, Indiana
    Posts
    382
    Post Likes
    Can tell your not experienced, cause for a limit code, there are 100 things I would have done before changing the ignitor or flame sensor. When it gives a code, it usually does not mean new part. Think of why the main limit would be kicking out. Heres a hint: something is probably needing cleaned

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •