    Frosted compressor w/ suction accumulator

    Hi guys,

    This is a theoretical question. It's not my installation.

    I took a photo of a compressor unit with suction accumulator installed.
    Name:  20200129_052113.jpg
Views: 264
Size:  129.6 KB

    Why is the compressor frosted although there is a suction accumulator present in a system?

  2. #2
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,275
    Post Likes
    The theoretical answer is by having a surface temperature below 32f.

    Maby the accumulator is full because of an overcharge and or evap fan failure.
    Quote Originally Posted by BobFrost View Post
    Hi guys,

    This is a theoretical question. It's not my installation.

    I took a photo of a compressor unit with suction accumulator installed.
    Name:  20200129_052113.jpg
Views: 264
Size:  129.6 KB

    Why is the compressor frosted although there is a suction accumulator present in a system?
    Sent from mars using Tapatalk

  3. #3
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,656
    Post Likes
    Just suppose that this is a freezer. Just suppose that the box temp is -12*F and also suppose that the TXV is set for a 6*SH. So I suppose that the "vapor only" refrigerant leaving the evap is also "liquid free",and at a temp of -6*F, meaning that the accumulator is not being used as a temporary liquid holding tank because there is no liquid to be held in the accumulator,at this time. Now suppose that the -6*F freon inside the suction line has some moisture in the air on the outside of the suction pipe. I now supposed that the moisture in the air would now FREEZE out of the air causing a frosted suction line and possible/probably/more than likely a frosted comp, I think. So it is very possible that the frost is normal.

    But on the other hand, if this a med temp box, then they have some major problems.

  4. #4
    Join Date
    Jan 2019
    Location
    EU
    Posts
    39
    Post Likes
    Thread Starter
    I believe it's a LT application because there is a head fan installed.

  5. #5
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    3,353
    Post Likes
    Let's suppose that TechmanTerry is correct and that he gave a very good explanation.
    If at First You Don't Succeed, Skydiving Is Not for You.

  6. #6
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,366
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    Just suppose that this is a freezer. Just suppose that the box temp is -12*F and also suppose that the TXV is set for a 6*SH. So I suppose that the "vapor only" refrigerant leaving the evap is also "liquid free",and at a temp of -6*F, meaning that the accumulator is not being used as a temporary liquid holding tank because there is no liquid to be held in the accumulator,at this time. Now suppose that the -6*F freon inside the suction line has some moisture in the air on the outside of the suction pipe. I now supposed that the moisture in the air would now FREEZE out of the air causing a frosted suction line and possible/probably/more than likely a frosted comp, I think. So it is very possible that the frost is normal.

    But on the other hand, if this a med temp box, then they have some major problems.
    Good explanation, but you forgot to include the evaporator TD.

    So assuming a -12F box temp and a 10F TD, the SST would be -22F.

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,366
    Post Likes
    Quote Originally Posted by BobFrost View Post
    Hi guys,

    This is a theoretical question. It's not my installation.

    I took a photo of a compressor unit with suction accumulator installed.


    Why is the compressor frosted although there is a suction accumulator present in a system?
    As explained earlier, frost doesn't always mean floodback. Here's a pic of a supermarket rack with a measured 28F of suction superheat...ie, textbook normal conditions for the application:

    Name:  FrostedRackwith28degSHbySmilies.JPG
Views: 221
Size:  22.3 KB

  8. Likes Andrew Schaefer, COOLJIM liked this post.
  9. #8
    Join Date
    Feb 2010
    Location
    In a motor room somewhere in Wisconsin or surrounding states
    Posts
    8,175
    Post Likes
    As long as the oil sump is warm! If that is cold you have floodback