Results 1 to 8 of 8
    Jan 2019
    EU
    Frosted compressor w/ suction accumulator
    Hi guys,
    This is a theoretical question. It's not my installation.
    I took a photo of a compressor unit with suction accumulator installed.
    Why is the compressor frosted although there is a suction accumulator present in a system?
    Jul 2019
    Oklahoma home its in the name
    The theoretical answer is by having a surface temperature below 32f.
    Maby the accumulator is full because of an overcharge and or evap fan failure.
    Quote Originally Posted by BobFrost View Post
    Hi guys,
    Sent from mars using Tapatalk
    Mar 2015
    Medford, N.Y.
    Just suppose that this is a freezer. Just suppose that the box temp is -12*F and also suppose that the TXV is set for a 6*SH. So I suppose that the "vapor only" refrigerant leaving the evap is also "liquid free",and at a temp of -6*F, meaning that the accumulator is not being used as a temporary liquid holding tank because there is no liquid to be held in the accumulator,at this time. Now suppose that the -6*F freon inside the suction line has some moisture in the air on the outside of the suction pipe. I now supposed that the moisture in the air would now FREEZE out of the air causing a frosted suction line and possible/probably/more than likely a frosted comp, I think. So it is very possible that the frost is normal.
    But on the other hand, if this a med temp box, then they have some major problems.
    Jan 2019
    EU
    I believe it's a LT application because there is a head fan installed.
    Apr 2003
    Maple Grove, MN
    Let's suppose that TechmanTerry is correct and that he gave a very good explanation.
    If at First You Don't Succeed, Skydiving Is Not for You.
    Jul 2000
    Guayaquil, EC
    Quote Originally Posted by TechmanTerry View Post
    Good explanation, but you forgot to include the evaporator TD.
    So assuming a -12F box temp and a 10F TD, the SST would be -22F.
    Jul 2000
    Guayaquil, EC
    Hi guys,
    As explained earlier, frost doesn't always mean floodback. Here's a pic of a supermarket rack with a measured 28F of suction superheat...ie, textbook normal conditions for the application:
  8. Likes Andrew Schaefer, COOLJIM liked this post.
  9. #8
    In a motor room somewhere in Wisconsin or surrounding states
    As long as the oil sump is warm! If that is cold you have floodback
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR