    American Standard air handler blower

    American Standard model TWE048C140C0.
    When power is turned on blower motor powers for 1-2 seconds then will coast to a stop. Is this normal for this American Standard?
    Changed blower relay because blower would only run part time. Blower did same thing with old blower board

  2. #2
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    So why the board change then ?

  3. #3
    Join Date
    Jan 2020
    Posts
    3
    Post Likes
    Thread Starter
    The blower would quite intermittently. And at that time there would not be any power coming from board relay to the motor.

  4. #4
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    So you changed the board and the same problem exist ?

  5. #5
    Join Date
    Jan 2020
    Posts
    3
    Post Likes
    Thread Starter
    No the blower only operating intermitteny has been solved. The board was bad!

  6. #6
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    4,772
    Post Likes
    I've seen tranes do that,(blower cycle on powerup, even w psc motors.) same difference.
    Col 3:23


    questions asked, answers received, ignorance abated

  7. #7
    Join Date
    Mar 2020
    Posts
    7
    Post Likes
    Seen this with Trane and American standard but only on the x 13 motors

  8. #8
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    1,696
    Post Likes
    On many units at "power-up" the blower runs as a purge before the system goes into normal service

  9. #9
    Join Date
    Jan 2010
    Posts
    19,279
    Post Likes
    On some Carrier units if there's a call for heat and you power it up the blower will run first.