    Coil Pressure Drop

    When setting flow rate through a coil using the manufactures pressure drop vs. flow, do they take in account the difference in height between the entering and leaving pressure ports or does it not matter?

    My pea brain seems to think that if there was a difference of 4 feet between the entering and leaving pressure ports that you would have to compensate for it. Never have, just always have wondered this.

  2. #2
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    The manufacturers are giving you the resistance to flow only and that's what you are trying to measure. My gages will read differential pressure but I still locate the meter at the coil height mid point. Water has weight that has to be accounted for.
    No man can be both ignorant and free.
    Thomas Jefferson

  3. #3
    Join Date
    Jan 2020
    Posts
    8
    Post Likes
    Thread Starter
    [QUOTE=WAYNE3298;25839114]The manufacturers are giving you the resistance to flow only and that's what you are trying to measure. My gages will read differential pressure but I still locate the meter at the coil height mid point. Water has weight that has to be accounted for.[/QUOTE

    Thanks for your response. It seems to me that setting your gauge at mid-point of the coil would minimize the influence of the pressure tap height locations.

  4. #4
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    The mid point does compensate. You do the same thing for pumps. One place it usually makes a big difference is on dry cooling towers.
    No man can be both ignorant and free.
    Thomas Jefferson

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •