Before you plug the unit in - what do the molex pins and sockets look like? Clean and all pins the same length ?
PHM
-------
-
Originally Posted by
Ineedanap
First this unit has been taken out of service. The initial problem was the blower motor would cut out. After some checks determined the control board was cutting the power to the motor. I replaced control board and now the unit wont power up.
I have checked at the plug and at the control board. I have 240 volts but the transformer is loosing a leg. I unplugged the transformer and checked at the board. This is a GE Zoneline heat pump PTAC model #AZ65H15DABW1. I have checked the inline fuse and I do have continuity across it. The connections seem tight and I see no broken wires.
I have even brought in someone more knowledgeable than me and they weren't able to figure it out. Thinking the new board was defective, I put the old board back in, it still wouldn't power up. I called GE and was told they have no dedicated tech support. I haven't been able to find a wiring schematic for this unit what I have only shows plug connections on the board.
At this point I figure the problem is somewhere in the wiring, but I have been unable to locate. My theory right now is that somewhere was a wire that was frail and the pulling of the unit to replace the board finished it off but Ill be dogged if I can locate. At this point I just need another direction to look.At this point its personal. I figure if it happens once it will happen again that is why I want to resolve this. Any help would be greatly appreciated.