Thread: Chilled water leak

  1. #1
    Join Date
    Nov 2018
    Location
    Saudi Arabia
    Posts
    59
    Post Likes

    Chilled water leak

    Dears

    I have leak in chilled water leak in network. Observed consumption of make up water 60 l/hr.

    Didn't found leak by visual inspection of pump rooms.

    Is there any way to find leak area?

    Sent from my INE-LX1r using Tapatalk

  2. #2
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Air bleeders piped to drains?
    UA Local 32 retired as of Jan 2020

  3. #3
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,782
    Post Likes
    Cracked U bend in a coil? Are the condensate drains plumbed right over a floor drain?

    Sent from my SM-G935U using Tapatalk
    -----Stop, step back, relax and have another go at it.-----

  4. #4
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    If you have them I would start with checking the automatic air bleeders. You can walk the pipe at the same time. Then go to the coils.
    No man can be both ignorant and free.
    Thomas Jefferson

  5. #5
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Failed plate heat exchanger that has secondary pressure lower than chilled water loop pressure .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  6. #6
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    Failed plate heat exchanger that has secondary pressure lower than chilled water loop pressure .
    I will put my money on this option.....let it ride.

    Sent from my SM-G965W using Tapatalk

  7. #7
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    Quote Originally Posted by BALloyd View Post
    I will put my money on this option.....let it ride.

    Sent from my SM-G965W using Tapatalk

    Except that the OP says he confirmed there are no leaks by visually inspecting the pump rooms.

    With commercial work, Many times, the problem doesn’t exist in the room with the problem.

    I can walk into a building with 100 VAV boxes, and look in the mechanical room, and determine there’s no leak in that room.....doesn’t mean there aren’t any leaks out in the other 10,000 feet of piping.

  8. #8
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Pretty sure Healy was implying an internal leak to the lower pressure side. This would not be visually apparent.
    Quote Originally Posted by 71CHOPS View Post
    Except that the OP says he confirmed there are no leaks by visually inspecting the pump rooms.

    With commercial work, Many times, the problem doesn’t exist in the room with the problem.

    I can walk into a building with 100 VAV boxes, and look in the mechanical room, and determine there’s no leak in that room.....doesn’t mean there aren’t any leaks out in the other 10,000 feet of piping.
    Sent from my SM-G965W using Tapatalk

  9. #9
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Quote Originally Posted by BALloyd View Post
    Pretty sure Healy was implying an internal leak to the lower pressure side. This would not be visually apparent.

    Sent from my SM-G965W using Tapatalk
    See .........someone gets it round here .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  10. #10
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Have you noticed an increase in water volume in the lower pressure system?
    No man can be both ignorant and free.
    Thomas Jefferson

  11. #11
    Join Date
    Nov 2018
    Location
    Saudi Arabia
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by WAYNE3298 View Post
    Have you noticed an increase in water volume in the lower pressure system?
    Make up water is increasing by 50 l/h

    Sent from my INE-LX1r using Tapatalk

  12. #12
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    Quote Originally Posted by BALloyd View Post
    Pretty sure Healy was implying an internal leak to the lower pressure side. This would not be visually apparent.

    Sent from my SM-G965W using Tapatalk
    Yes, I was being facetious. If that were the case, the leak would be visually apparent, but he would still be required to leave the room to find it! LOL!

  13. #13
    Join Date
    Jan 2020
    Location
    SAudi Arabia
    Posts
    32
    Post Likes
    Most of asset inside bathroom which have drain

    Sent from my INE-LX1r using Tapatalk

  14. #14
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    You might need a different language translation tool.

    That last response didn’t make any sense.

  15. #15
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    By what I read you are up to 110 Liters/hour make up (or 30 gallons / hour). Pretty big leak.

    Walk the system down and find all air bleeders and manual vent and drain valve that might be dumping water to drainage system. Close them or cap them as best you can. See if that accounts for all or part of your makeup.

    If you do not find any external leakage, you better start isolating and doing a pressure drop check on various sections you can isolate to rule out or verify where the leak is or isn't.

    Good Luck

  16. #16
    Join Date
    Jan 2020
    Location
    SAudi Arabia
    Posts
    32
    Post Likes
    Quote Originally Posted by Answer-Man View Post
    By what I read you are up to 110 Liters/hour make up (or 30 gallons / hour). Pretty big leak.

    Walk the system down and find all air bleeders and manual vent and drain valve that might be dumping water to drainage system. Close them or cap them as best you can. See if that accounts for all or part of your makeup.

    If you do not find any external leakage, you better start isolating and doing a pressure drop check on various sections you can isolate to rule out or verify where the leak is or isn't.

    Good Luck
    Leak found by isolation method
    Thanks to all

    Sent from my INE-LX1r using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •