    Not enough vacuum for pressure switch

    I have a commercial building with 4 Goodman Furnaces and 2 of them are not able to close the pressure switch that comes of the condensate collector on the secondary heat exchanger. I cleaned all the lines--no pluggs but still is measuring below the vacuum needed to close the switch.
    Can this be anything other then a plugged exchanger??

  2. #2
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    If it's reading differential pressure do you have the correct differential between the high and low side? Have you checked the flue and intake for obstructions? If you put a manometer on it and it's with in range and still not closing the switch then you have a bad switch.

  3. #3
    Join Date
    Apr 2006
    Location
    Delano, MN 55328
    Posts
    212
    Post Likes
    Thread Starter
    Vents were checked an well with in the lengths. I did check with a manometer and I am right at the the limit of-.4 which is the rating on the switch.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Check the heat exchangers.

  5. #5
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Check the inducer squirrel cage wheel.

  6. #6
    Join Date
    Apr 2019
    Location
    central MN
    Posts
    23
    Post Likes
    the rating on the switch is the point it reopens not the point it closes. you do not have enough vacuum. have you ensured that the inducer assembly is clear? are the ports to the pressure switch clear of debris? I did not see an answer if the venting was inspected for clogs, bugs, standing water, etc. just a statement that the length was correct. how long are the venting runs? what size is the vent pipe? how many 45s and 90s on vent and intake. what is the model of the furnaces?

  7. #7
    Join Date
    Jul 2012
    Location
    WA
    Posts
    3,250
    Post Likes
    Pull the inducer to inspect it and take a look at the secondary heat exchanger.

  8. #8
    Join Date
    Aug 2010
    Location
    Living for the Lord
    Posts
    6,837
    Post Likes
    Just had one, that I found a wasps nest about the size of a silver dollar. Wasn't dropping out on low vacuum, but tripping out on the flue temp sensor.
    It doesn't take much, to obstruct the air flow.

    Sent from The Lions Lair
    "If you can’t describe what you are doing as a process, you don’t know what you are doing." ~ W. Edwards Deming

    All those who wander..are not lost.

    Do NOT..mistake my kindness for weakness.

    The early bird may get the worm..but the second mouse gets the cheese.

  9. #9
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by bow hunter View Post
    I have a commercial building with 4 Goodman Furnaces............
    Are they all the same model?

    To second what "JmanHVAC" said - what is the model number of these units?
    Instead of learning the tricks of the trade, learn the trade.

  10. #10
    Join Date
    Apr 2019
    Location
    central MN
    Posts
    23
    Post Likes
    Quote Originally Posted by Red Man View Post
    Pull the inducer to inspect it and take a look at the secondary heat exchanger.
    I just had a unit with the same issue. I pulled the inducer assembly to check the secondary and a dead mouse fell out of the inducer wheel, problem solved

  11. #11
    Join Date
    Apr 2019
    Location
    central MN
    Posts
    23
    Post Likes
    where did OP go? We would love to know what was found as the problem.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •