    Transformer Question

    I currently have 480VAC running on a 30amp 3 pole breaker. I need to use a transformer to bring it down to 240VAC to run a Warren Heaters heat strip. The specs call for 240VAC and 40 amps. I found one at Carrier but it was only rated to 250VA. Is that large enough to handle the needed amps? Is there a formula I should use to figure this out?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    VA ÷ V = A

    250 ÷ 240 = 1.042 Amps.

    Not even close.



    Sent from my SM-G965W using Tapatalk

  3. #3
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Better look closer at the existing line size.

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Seems contactor(s) should come into play somewhere in the mix
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  5. #5
    Join Date
    Oct 2019
    Location
    Bennett, CO
    Posts
    125
    Post Likes
    Thread Starter
    Is it possible to have a qualified electrician take the power at the panel down to 240? In looking at the panel it just said 480 main breaker panel. Had numerous 3 pole breakers, a few 2 pole breakers and 10 single pole breakers.


    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Oct 2019
    Location
    Bennett, CO
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by 2sac View Post
    Seems contactor(s) should come into play somewhere in the mix
    Can you please give me a little more detail on what you mean by this?


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Quote Originally Posted by Myhvacguy1 View Post
    Is it possible to have a qualified electrician take the power at the panel down to 240? In looking at the panel it just said 480 main breaker panel. Had numerous 3 pole breakers, a few 2 pole breakers and 10 single pole breakers.


    Sent from my iPhone using Tapatalk
    You can not get 240V from a 480V breaker box. Even if you could, your wires might be too small if they're sized for 30 amps, any you need them to be sized for 40 amps.

    You most likely have a 208V or 230V panel near by that can be used. Your wires (if they are the correct size) could probably be run to that panel instead. An electrician would have to look at it to see if that would be possible.

    Using BALloyd's formula (ohm's law), you would need at least a 9600VA transformer to do what you wanted to do.
    If at First You Don't Succeed, Skydiving Is Not for You.

  8. #8
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Why not just use a heat strip rated for the correct voltage you have?
    UA Local 32 retired as of Jan 2020

  9. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Myhvacguy1 View Post
    Can you please give me a little more detail on what you mean by this?


    Sent from my iPhone using Tapatalk
    I was drinking and misread the original post
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  10. Likes BALloyd liked this post.
  11. #10
    Join Date
    Oct 2019
    Location
    Bennett, CO
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by buford View Post
    Why not just use a heat strip rated for the correct voltage you have?
    On this particular project, the engineer drew in the plans an external duct heater running on 480VAC. The client isn’t happy with the look of this as the ductwork is visible in the space. They are wanting to have us place the heat strip inside the AHU for appearances. The AHU is currently powered by 208vac @ 20Amp and I can’t find a heat strip large enough to heat the space that won’t trip that circuit. I was looking for a way to run the current AHU off of the 480VAC that is powering the duct heater without having to have an electrician run larger wire. No one wants to cover that cost.


    Sent from my iPhone using Tapatalk

  12. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Who the hell does he think will be staring up at the ceilings ? Just put the duct heater in

    People are crazy ...

  13. #12
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Is there more than one element in the "strip" ?

    And hopefully an even number. <g>

    If so; the 240V unit could be re-wired to operate on 480V

    PHM
    --------




    Quote Originally Posted by Myhvacguy1 View Post
    I currently have 480VAC running on a 30amp 3 pole breaker. I need to use a transformer to bring it down to 240VAC to run a Warren Heaters heat strip. The specs call for 240VAC and 40 amps. I found one at Carrier but it was only rated to 250VA. Is that large enough to handle the needed amps? Is there a formula I should use to figure this out?


    Sent from my iPhone using Tapatalk
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  14. #13
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    You're going to be pulling new wire no matter what you do.

  15. #14
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    Is there more than one element in the "strip" ?

    And hopefully an even number. <g>

    If so; the 240V unit could be re-wired to operate on 480V

    --------
    Ewe that's right … that things probly wired up like a xmas tree
    Last edited by Snapperhead; 01-18-2020 at 05:09 PM.

  16. #15
    Join Date
    Oct 2019
    Location
    Bennett, CO
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by Snapperhead View Post
    Who the hell does he think will be staring up at the ceilings ? Just put the duct heater in

    People are crazy ...
    Snapperhead,
    You are correct that people are crazy. However, With that being said, these crazy people are paying the company I work for a lot of money for the finished product and potential future projects are what we’re looking for.
    I also agree that most people don’t look at the ceiling but ever since I got into the trade, when I see exposed ductwork, I critique it.


    Sent from my iPhone using Tapatalk

  17. #16
    Join Date
    Oct 2019
    Location
    Bennett, CO
    Posts
    125
    Post Likes
    Thread Starter
    Quote Originally Posted by Poodle Head Mikey View Post
    Is there more than one element in the "strip" ?

    And hopefully an even number. <g>

    If so; the 240V unit could be re-wired to operate on 480V

    PHM
    --------
    This unit has 4 strips in it. Are you serious when you say that? It would have to run the heating elements and the blower motor.


    Sent from my iPhone using Tapatalk

  18. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Oh trust me I've seen my share of people being overly fussy with how it looks , making my job a complete pain in the ass , but the bill also reflects it

    "that relay costs 800 dollars ?? "

    Yup for You it does …. I mean , Yes , yes it does

  19. #18
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Myhvacguy1 View Post
    On this particular project, the engineer drew in the plans an external duct heater running on 480VAC. The client isn’t happy with the look of this as the ductwork is visible in the space. They are wanting to have us place the heat strip inside the AHU for appearances. The AHU is currently powered by 208vac @ 20Amp and I can’t find a heat strip large enough to heat the space that won’t trip that circuit. I was looking for a way to run the current AHU off of the 480VAC that is powering the duct heater without having to have an electrician run larger wire. No one wants to cover that cost.


    Sent from my iPhone using Tapatalk
    Someone's going to have to. You've already got 208 in the building. If the panel can handle it, add another breaker and pull wire.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  20. #19
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by Myhvacguy1 View Post
    This unit has 4 strips in it. Are you serious when you say that? It would have to run the heating elements and the blower motor.


    Sent from my iPhone using Tapatalk
    yes , If you run 2 of the strips in series like a xmas tree it becomes 480 , you know , like batteries in a flashlight , so essentially it makes 1 long strip , but you can only hook up 2 , leave other 2 strips unhooked , then test how many amps shes pulling

    We cant draw a diagram in the open forum , or give you wire colors , but hopefully you can read in-between the lines

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •