    This will work.. Just need someone to do it for me.

    Put a outside HPCU inside a walkin cooler box. Put AHU in the Kitchen to dump heat.

    Parameters are within range. HPCU will have ambient of 35-40. AHU ambient is 78-80 degrees.

    I like it because HPCU is waterproof and set-up is much cheaper than refrigeration equipment.

    Who will do this for me?

  2. #2
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    3,104
    Post Likes
    Can you explain a bit more?
    What is an HPCU? (High pressure condensing unit?)

    Sent from mars using Tapatalk

  3. #3
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    3,104
    Post Likes
    Heat pump condenser?
    That makes more sense.

    Sent from mars using Tapatalk

  4. #4
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,434
    Post Likes
    Thread Starter
    heat pump

  5. #5
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    3,104
    Post Likes
    This is an intriguing idea.
    How will you take care of condensate?
    Also what humidity are you aiming for or is humidity not important for this application?

    Sent from mars using Tapatalk

  6. #6
    Join Date
    Sep 2002
    Posts
    28,351
    Post Likes
    Why put the condensing unit inside the 40 box? Wouldn't an AH take up less room? And where will all the condensate water go? Onto the floor?

    No wait; it's worse than that: a HPCU is not designed to be wet all the time - it generally frosts and defrosts and dries out inbetwen.

    And really; the best way to do this would be with a standard refrigeration coil hanging in the box.

    And "dumping heat" into a kitchen might be quite the trick to accomplish as these are often near 100 F. in the summertime.

    I have a number of times myself (refrigerate with AC equipment) and I've seen it done all over the Caribbean islands. You can run the box very cold and defrost it in a minute by switching the reversing valve. Or . . . you can just use a large evaporator, run a low TD, and not even need to use a heat pump. <g>

    PHM
    -------


    Quote Originally Posted by timjimbob View Post
    This will work.. Just need someone to do it for me.

    Put a outside HPCU inside a walkin cooler box. Put AHU in the Kitchen to dump heat.

    Parameters are within range. HPCU will have ambient of 35-40. AHU ambient is 78-80 degrees.

    I like it because HPCU is waterproof and set-up is much cheaper than refrigeration equipment.

    Who will do this for me?
    PHM
    --------
    Socialism is a zombie. It never dies - even though it is constantly decaying and decomposing.

  7. #7
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,434
    Post Likes
    Thread Starter
    AHU is not designed to operate at 40 ambient. HPCU is designed to be outside at 35 degree weather. Defrost water goes down floor drain. I don't think I can buy refrigeration equipment as cheaply as I can get builder grade HP.

    80 degree kitchens are common.

  8. #8
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    3,104
    Post Likes
    Like PHM said use the air handler or refrigeration evap with standard refrigeration defrost controls.
    Quote Originally Posted by timjimbob View Post
    AHU is not designed to operate at 40 ambient. HPCU is designed to be outside at 35 degree weather. Defrost water goes down floor drain. I don't think I can buy refrigeration equipment as cheaply as I can get builder grade HP.

    80 degree kitchens are common.
    Sent from mars using Tapatalk

  9. #9
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    3,104
    Post Likes
    Why don't you do it? You are a contractor.
    Quote Originally Posted by timjimbob View Post
    This will work.. Just need someone to do it for me.

    Put a outside HPCU inside a walkin cooler box. Put AHU in the Kitchen to dump heat.

    Parameters are within range. HPCU will have ambient of 35-40. AHU ambient is 78-80 degrees.

    I like it because HPCU is waterproof and set-up is much cheaper than refrigeration equipment.

    Who will do this for me?
    Sent from mars using Tapatalk

  10. #10
    Join Date
    Sep 2002
    Posts
    28,351
    Post Likes
    That logic escapes me. What about AH design would prevent it from working properly in a 35 ambient temperature?

    What you describe can be made to work but it's not how I would go about it.

    PHM
    --------



    Quote Originally Posted by timjimbob View Post
    AHU is not designed to operate at 40 ambient. HPCU is designed to be outside at 35 degree weather. Defrost water goes down floor drain. I don't think I can buy refrigeration equipment as cheaply as I can get builder grade HP.

    80 degree kitchens are common.
    PHM
    --------
    Socialism is a zombie. It never dies - even though it is constantly decaying and decomposing.

  11. #11
    Join Date
    Jan 2010
    Posts
    19,721
    Post Likes
    I buy used refrigeration equipment all the time. Quite often it's in new condition from a failed restaurant venture.
    Why even waste time / money reinventing the wheel ?

  12. #12
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,434
    Post Likes
    Thread Starter
    I don't see how an air handler is designed to work at a cold 40deg. A HPCU can be hosed down when cooler box is being cleaned.







    hpcu

  13. #13
    Join Date
    Jan 2010
    Posts
    19,721
    Post Likes
    Quote Originally Posted by VTP99 View Post
    I buy used refrigeration equipment all the time. Quite often it's in new condition from a failed restaurant venture.
    Why even waste time / money reinventing the wheel ?
    I just moved this unit today. Probably paid 100.00 and it's never been used.
    Attached Images Attached Images  

  14. #14
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,434
    Post Likes
    Thread Starter
    Used. My luck it would be three phase.
    Complete HP setup new would cost me $1100. And I can pick it up Saturday without ordering it in.

  15. #15
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    3,637
    Post Likes
    The thing you call a heat pump condensing unit is actually going to be an evaporator. The real condenser (the thing you will be putting in the kitchen) is designed to have a return air temperature of about 70F.

    You state that this kitchen will be 80F? That's pretty good as far as kitchen temps go, but it's pretty horrible for a heat pump air handler. That's right on the ragged edge of where that thing will be able to function without tripping it's high pressure switch (if it has one).

    Hey, I just came up with an idea for you. Instead of a "condensing" unit and an air handler, Why not get yourself 2 "condensing" units? One inside of the box and one on the outside. That way you will be good for a kitchen temperature of around 110 or so (and you'll have a spare compressor for "just in case").

    Just make sure you have really high ceilings in that kitchen (and inside of the cooler) to avoid recirculation issues.

    Great idea!

    If at First You Don't Succeed, Skydiving Is Not for You.

  16. Likes R600a, Core_d liked this post.
  17. #16
    Join Date
    Sep 2002
    Posts
    28,351
    Post Likes
    Brillant!

    So all you would need would be a lead/lag arrangement to alternate compressor operation and have a nice amount of redundancy.

    PHM
    --------






    Quote Originally Posted by ammoniadog View Post
    The thing you call a heat pump condensing unit is actually going to be an evaporator. The real condenser (the thing you will be putting in the kitchen) is designed to have a return air temperature of about 70F.

    You state that this kitchen will be 80F? That's pretty good as far as kitchen temps go, but it's pretty horrible for a heat pump air handler. That's right on the ragged edge of where that thing will be able to function without tripping it's high pressure switch (if it has one).

    Hey, I just came up with an idea for you. Instead of a "condensing" unit and an air handler, Why not get yourself 2 "condensing" units? One inside of the box and one on the outside. That way you will be good for a kitchen temperature of around 110 or so.

    Just make sure you have really high ceilings in that kitchen (and inside of the box) to avoid recirculation issues.

    Great idea!

    PHM
    --------
    Socialism is a zombie. It never dies - even though it is constantly decaying and decomposing.

  18. #17
    Join Date
    Sep 2002
    Posts
    28,351
    Post Likes
    OK; let's do it as you propose.

    Let's start with the cooling requirements.

    How big is the subject box?

    And what size HPCU/system are you going to use?
    PHM
    --------
    Socialism is a zombie. It never dies - even though it is constantly decaying and decomposing.

  19. #18
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    10,642
    Post Likes
    Why not just do it as a straight cool unit? The kitchen is already full of hot air. I'm sure another heat source of 130* won't affect it that much.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  20. #19
    Join Date
    Sep 2002
    Posts
    28,351
    Post Likes
    Because he wants the condensing unit inside the walkin box.

    Quote Originally Posted by 2sac View Post
    Why not just do it as a straight cool unit? The kitchen is already full of hot air. I'm sure another heat source of 130* won't affect it that much.
    PHM
    --------
    Socialism is a zombie. It never dies - even though it is constantly decaying and decomposing.

  21. #20
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    10,642
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    Because he wants the condensing unit inside the walkin box.
    My bad.....
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •