All.
But is best practice to backup each piece individually also, imo.
When you go into Tracer TU, and completely backup a controller does it contain all of the points, and TGP2? Or is it necessary to backup the devices, and backup the TGP2 separately through the TGP2 editor?
J. King
All.
I typically do back up the TGP2 on devices like UC600s that are being used for plant control, AHU control, etc. I have a job that has like 150 VAV boxes, and some of them have custom TGP2. I just didn’t know if it made sense to go through all of those devices and backup the TGP2 separately or if the standard backup would suffice. Thanks for your response.
J. King
Just wanted to explain that a backup is done as a backup.. not ‘save as’. Save as only gets config file.
(If i remember correctly).
Typically I use the backup utility at the top left of the screen to do the backup. From there it saves a zip file to my computer for that device. I just wanted to see if that included everything that I would need in the event of a controller failure. Particularly in regards to devices like VAV boxes. Going through a whole bunch of VAV controllers and backing up TGP2 is a lot more time consuming than just running the backup utility on all of the devices and walking away.
J. King
For vav’s i would just do the backup.
Can do them all at once via backup utility.
Might take an hour or three and miss a few (it gives a report of what was missed) but no user inputs after clicking all the check boxes) and starting.