    Clicking sound at condenser and air handler

    Been trying to diagnose why condenser and air handler is making a clicking sound. The condenser is a heat pump. After clicking for a while the clicking stops but the condenser contactor burns out. Any ideas?

  2. #2
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,906
    Post Likes
    Yes.
    Give us specifics. Model, a thing technical that you have measured.

    Also have your post moved to the correct forum, the tech to tech forum. Click the little black triangle at the bottom of your post and ask the moderators to move it.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  3. #3
    Join Date
    Jan 2020
    Posts
    7
    Post Likes
    Thread Starter
    The air handler doesn't have a model number but it's a Bryant. I've checked wires for continuity going to the condenser and thermostat. I've checked for 24v going to defrost board and coming off defrost board. I've also checked pressure switches and they was good

  4. #4
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,906
    Post Likes
    What is the source of the clicking? Fan, relay, refrigerant lines?
    What do you mean “the contactor burns out?” That would be my first concern, not the clicking.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    bad thermostat ?

    if you unhook stat , then from there twist a few wires together to make the unit run …. does it still click

  6. #6
    Join Date
    Jan 2020
    Posts
    7
    Post Likes
    Thread Starter
    The source of the clicking is the contactor and a relay. And what I mean by the contactor burns out is after it clicks for so long the button in the center of the contactor (that allows the high voltage to travel through) it breaks and the contactor is no longer operable

  7. #7
    Join Date
    Jan 2020
    Posts
    7
    Post Likes
    Thread Starter
    The thermostat is good

  8. #8
    Join Date
    Jan 2020
    Posts
    7
    Post Likes
    Thread Starter
    The wiring schematic is calling for the transformer tap to be set on 208v but I noticed the transformer is set to 240v. I'm wondering if that could be the problem

  9. #9
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    whats your voltage coming in ?

    That's what you set the transformer to

  10. #10
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    usually I find one of the high pressure sensors , or low pressure sensors is culprit

    Or bad solder joints on board

    Bypass those sensors and see if she still clicks

  11. #11
    Join Date
    Jan 2020
    Posts
    7
    Post Likes
    Thread Starter
    240v coming in. But if the schematic says set the transformer to 208v shouldn't I set it to 208v?

  12. #12
    Join Date
    Jan 2020
    Posts
    7
    Post Likes
    Thread Starter
    The high and low pressure sensors are good. I'm thinking it might be the defrost board

  13. #13
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes

    Clicking sound at condenser and air handler

    ...
    Quickly, I must hurry, for there go my people and I am their leader!

  14. #14
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by Jake2212 View Post
    240v coming in. But if the schematic says set the transformer to 208v shouldn't I set it to 208v?
    c'mon man .... why do you suppose they have a setting for 240 ....

    You wont find a 208 power supply until you get into a commercial building

    Set the transformer to the correct power , then make sure you have about 25v at board

    If you don't get 25 volts then I guess they know something that we don't and you will have to set it back to where it was
    Last edited by Snapperhead; 01-10-2020 at 06:39 AM.

  15. #15
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Once in awhile I come across a rooftop unit that's running just fine ....but only has 20 volts at the thermostat. I check power coming into the unit 208 which is landed on the 240 tap so I move it to the 208 tap and I get my 25 volts

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •