    Nitrogen testing

    I have had thus question for a while and never got around to ask anyone.

    On a system with a hard lockout TXV (I think that is what it is called), when putting nitrogen in a system to leak test through the liquid line, the low side stops at around 200 psi. Should I then open the suction side on the gauges to equalize the pressure so I have 400 psi on both sides? This would be for a 410a heat pump? Or an I going to hurt the TXV?
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Raise the pressures equally. Avoid putting too much pressure on one side or the other.

    This also applies to valve plates, Scroll check valves everything.

  3. #3
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Raise the pressures equally. Avoid putting too much pressure on one side or the other.

    This also applies to valve plates, Scroll check valves everything.
    OK. Thanks.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  4. #4
    Join Date
    Jun 2018
    Posts
    40
    Post Likes
    Open both your gauges all the way and turn on the nitrogen tank.

  5. #5
    Join Date
    May 2018
    Location
    Miami
    Posts
    781
    Post Likes
    i also open bot gauges all the way and let the nitrogen flow in slowly, but not going up to 400 PSI
    i stop at 250

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    i also open bot gauges all the way and let the nitrogen flow in slowly, but not going up to 400 PSI
    i stop at 250
    R410A systems need much higher test pressure

    600%’s

  7. #7
    Join Date
    May 2018
    Location
    Miami
    Posts
    781
    Post Likes
    nope i'm not go that high LOL
    250 is the limit period

  8. #8
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    What if your leak doesn't show up till 300# ?

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    nope i'm not go that high LOL
    250 is the limit period
    What’s the high pressure limit on that System?

    What’s the Test Pressure on that system?

  10. #10
    Join Date
    May 2018
    Location
    Miami
    Posts
    781
    Post Likes
    i do residential up to 5 tons
    pressure switches txv coils and compressor valve
    no need to go to 600 psi
    not me

  11. #11
    Join Date
    May 2018
    Location
    Miami
    Posts
    781
    Post Likes
    Quote Originally Posted by pecmsg View Post
    What’s the high pressure limit on that System?

    What’s the Test Pressure on that system?
    don't know i was just answering to a guy here

  12. #12
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    i do residential up to 5 tons
    pressure switches txv coils and compressor valve
    no need to go to 600 psi
    not me
    Discharge at the compressor is going to be over 400 psi on a 410a unit.

    Just saying.


    Sent from my iPhone using Tapatalk

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    When its a heat pump. Put the nitrogen in through the vapor side. The TXV is only hard shut off in cooling mode. It will still let nitrogen flow from the vapor side to the liquid line.

  14. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    i do residential up to 5 tons
    pressure switches txv coils and compressor valve
    no need to go to 600 psi
    not me
    Whats your concern?

    See Step 18:
    https://portal.fujitsugeneral.com/fi...ll%20Guide.pdf

  15. #15
    Join Date
    Dec 2019
    Location
    Lake of the Ozarks Mo
    Posts
    66
    Post Likes
    I was trying to find a leak on a 3 head mini split. Finally found it in a flair fitting. It took 400 psi to make it bubble. I left it with 200 psi for 2 days with no change

  16. #16
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Quote Originally Posted by HAWK71 View Post
    I was trying to find a leak on a 3 head mini split. Finally found it in a flair fitting. It took 400 psi to make it bubble. I left it with 200 psi for 2 days with no change
    Case in point.

  17. #17
    Join Date
    May 2018
    Location
    Miami
    Posts
    781
    Post Likes
    Quote Originally Posted by HAWK71 View Post
    I was trying to find a leak on a 3 head mini split. Finally found it in a flair fitting. It took 400 psi to make it bubble. I left it with 200 psi for 2 days with no change
    Nope i'm not going there
    period LOL
    400 psi too much it will leak at 200 and with a good leak detector you'll find it.

  18. #18
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    Nope i'm not going there
    period LOL
    400 psi too much it will leak at 200 and with a good leak detector you'll find it.
    No, not really.
    I’ve seen many systems where the leak only showed up at a higher pressure, say over 350-400 PSI.
    Most minis and all VRF now require ~600 PSI standing presssure for 24 hours.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  19. #19
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by rider77 View Post
    No, not really.
    I’ve seen many systems where the leak only showed up at a higher pressure, say over 350-400 PSI.
    Most minis and all VRF now require ~600 PSI standing presssure for 24 hours.
    Agreed, and its not even recent.
    I remember reading about it for fujitsu 10 years ago.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  20. #20
    Join Date
    May 2018
    Location
    Miami
    Posts
    781
    Post Likes
    everybody talking about mini split and VRF
    can you imagine 600 psi on a York micro channel coil ?
    they leak just if you look at them LOL

+ Reply to Thread
Page 1 of 6 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •