  1. #27
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    Look...………………...

    Were all here to learn. Please explain or post documents on why you wont follow the manufactures recommendations.

    Maybe you know something we don't.

    Do you flow N2 while brazing?

  2. #28
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    OK

    I'll go first


    From this Document on Micro Channel Condensers:
    https://www.cantas.com/urunpdf/sanhu...hannel_cat.pdf

    Page 12 R-410A Refrigerant

    Operating Pressure 4.5 mPa or 652 PSIG

    Burst Pressure 13.5 mPa or 1,958 PSIG

  3. #29
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,985
    Post Likes
    Thread Starter
    I use the standard of whatever the manufacturer states in their literature. Or at least I try to.

    But everyone has their own experience. As long as it works for you and doesn't cause problems, you should keep doing it.

    Just my opinion.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  4. #30
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    Quote Originally Posted by joemach View Post
    I use the standard of whatever the manufacturer states in their literature. Or at least I try to.

    But everyone has their own experience. As long as it works for you and doesn't cause problems, you should keep doing it.

    Just my opinion.
    The only problem I have with that is Others that don't know read this and think its OK.

    Not flowing N2
    Additives
    Topping off charges with different refrigerants.

    The list of Misinformation and or Bad information continues to grow instead of diminishing!

  5. #31
    Join Date
    Jan 2010
    Posts
    19,281
    Post Likes
    Quote Originally Posted by joemach View Post

    But everyone has their own experience. As long as it works for you and doesn't cause problems, you should keep doing it.

    Just my opinion.
    But it might not be working for him by not using the higher pressure when acceptable.

  6. #32
    Join Date
    May 2018
    Location
    FLORIDA
    Posts
    303
    Post Likes
    Quote Originally Posted by joemach View Post
    I use the standard of whatever the manufacturer states in their literature. Or at least I try to.

    But everyone has their own experience. As long as it works for you and doesn't cause problems, you should keep doing it.

    Just my opinion.
    i agree. LOL
    Finally someone taking my side LOL
    yes i flow nitrogen when I'm brazing and yes i do 3 vacuum
    and again i don't install VRF with hundred of brazing, YOU have to do 2 brazing on condenser and 2 on a/h.
    if you are confident with your brazing you don't need 600 psi
    Thats it.
    Visit our website at www.airconcomfortcooling.com

  7. #33
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    3 Vacuums?

  8. #34
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,985
    Post Likes
    Thread Starter
    I usually do 75-100 lbs, then soap my braze joints. The reason being that at 200+ lbs a small leak will just blow the bubbles away and I will not see them. Once I am satisfied with no leaks, I then pump up to manufacturer's recommended pressure.

    I figure there was a reason someone included the install manual with the equipment.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  9. #35
    Join Date
    May 2018
    Location
    FLORIDA
    Posts
    303
    Post Likes
    Quote Originally Posted by pecmsg View Post
    3 Vacuums?
    triple vacuum
    Visit our website at www.airconcomfortcooling.com

  10. #36
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    triple vacuum
    How many microns?

  11. #37
    Join Date
    Dec 2019
    Location
    Lake of the Ozarks Mo
    Posts
    26
    Post Likes
    I don’t always pressure up to 400 psi.

  12. #38
    Join Date
    Dec 2019
    Location
    Lake of the Ozarks Mo
    Posts
    26
    Post Likes
    Usually 200 is sufficient

  13. #39
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,284
    Post Likes
    The Leak Detection manual from refrigeration Technologies is a must read at least once.