    Quote Originally Posted by AIRCON8 View Post
    i do residential up to 5 tons
    pressure switches txv coils and compressor valve
    no need to go to 600 psi
    not me
    Whats your concern?

    See Step 18:
    https://portal.fujitsugeneral.com/fi...ll%20Guide.pdf

  2. #15
    Join Date
    Dec 2019
    Location
    Lake of the Ozarks Mo
    Posts
    26
    Post Likes
    I was trying to find a leak on a 3 head mini split. Finally found it in a flair fitting. It took 400 psi to make it bubble. I left it with 200 psi for 2 days with no change

  3. #16
    Join Date
    Jan 2010
    Posts
    19,281
    Post Likes
    Quote Originally Posted by HAWK71 View Post
    I was trying to find a leak on a 3 head mini split. Finally found it in a flair fitting. It took 400 psi to make it bubble. I left it with 200 psi for 2 days with no change
    Case in point.

  4. #17
    Join Date
    May 2018
    Location
    FLORIDA
    Posts
    303
    Post Likes
    Quote Originally Posted by HAWK71 View Post
    I was trying to find a leak on a 3 head mini split. Finally found it in a flair fitting. It took 400 psi to make it bubble. I left it with 200 psi for 2 days with no change
    Nope i'm not going there
    period LOL
    400 psi too much it will leak at 200 and with a good leak detector you'll find it.
    Visit our website at www.airconcomfortcooling.com

  5. #18
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    11,849
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    Nope i'm not going there
    period LOL
    400 psi too much it will leak at 200 and with a good leak detector you'll find it.
    No, not really.
    I’ve seen many systems where the leak only showed up at a higher pressure, say over 350-400 PSI.
    Most minis and all VRF now require ~600 PSI standing presssure for 24 hours.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  6. #19
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    7,326
    Post Likes
    Quote Originally Posted by rider77 View Post
    No, not really.
    I’ve seen many systems where the leak only showed up at a higher pressure, say over 350-400 PSI.
    Most minis and all VRF now require ~600 PSI standing presssure for 24 hours.
    Agreed, and its not even recent.
    I remember reading about it for fujitsu 10 years ago.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  7. #20
    Join Date
    May 2018
    Location
    FLORIDA
    Posts
    303
    Post Likes
    everybody talking about mini split and VRF
    can you imagine 600 psi on a York micro channel coil ?
    they leak just if you look at them LOL
    Visit our website at www.airconcomfortcooling.com

  8. #21
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    11,849
    Post Likes
    Still need to test conventional equipment at pressures similar to those it will be exposed to while operating.
    Now that said watching the micron level during evac will be the true end test, but 250 psi test pressure on equipment capable of over 400 psi during normal operation is a bit too low.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  9. #22
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    can you imagine 600 psi on a York micro channel coil ?
    they leak just if you look at them LOL
    B S

    What's the difference between 600 #'s N2 and 650 R-410A with a bad cond fan, overcharged Heat Pump?

  10. #23
    Join Date
    May 2018
    Location
    FLORIDA
    Posts
    303
    Post Likes
    Still not going there
    250 psi its my limit period LOL
    Visit our website at www.airconcomfortcooling.com

  11. #24
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,276
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    Still not going there
    250 psi its my limit period LOL
    So you don't follow Manufactures Recommendations and Best Industry Practice's.

  12. #25
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    11,849
    Post Likes
    Quote Originally Posted by AIRCON8 View Post
    Still not going there
    250 psi its my limit period LOL
    Why?
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  13. #26
    Join Date
    May 2018
    Location
    FLORIDA
    Posts
    303
    Post Likes
    Quote Originally Posted by pecmsg View Post
    So you don't follow Manufactures Recommendations and Best Industry Practice's.
    exactly
    250 and triple vacuum
    that's it
    Visit our website at www.airconcomfortcooling.com