    Quote Originally Posted by Snapperhead View Post
    The day I was diagnosing the fan .. I didn't have that oddball cap , so yes I made what looks like a dynamite pack strapped to the inside of hood exhaust fan housing

    Fired right up
    Does it magically connect to the motor ?

  2. #22
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    After you finish strapping them in place wit that black strapping and connect them red extension wires

  3. #23
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    After you finish strapping them in place wit that black strapping and connect them red extension wires
    You should connect it through wifi. That’s how all the kids are doing it these days. It’s the latest rage.


    Sent from my iPhone using Tapatalk
    Quickly, I must hurry, for there go my people and I am their leader!

  4. Likes UmmScott liked this post.
  5. #24
    Join Date
    Jun 2008
    Posts
    61
    Post Likes
    240V motors : Start winding is centre tapped between the 2 run windings; it is only subjected to 120V. See attached picture.Name:  IMG_1078.jpg
Views: 177
Size:  94.0 KB

  6. #25
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes

    Are start caps the same as run caps

    Quote Originally Posted by 508gm1 View Post
    240V motors : Start winding is centre tapped between the 2 run windings; it is only subjected to 120V. See attached picture.Name:  IMG_1078.jpg
Views: 177
Size:  94.0 KB
    Doesnt look to be the case from your drawings, looks parallel to both run winding circuits.


    Edit: atleast on the lower picture. Not shure how i missed that lol

    Sent from my iPhone using Tapatalk

  7. #26
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    That is interesting, dont believe ive ever seen a dual voltage psc motor before.


    Sent from my iPhone using Tapatalk

  8. #27
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Isn't the high voltage in series and the low voltage in parallel in his illustration ?

  9. #28
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Maybe the back EMF is less than 165 volts?

    When you measured it - what was it?


    Quote Originally Posted by Snapperhead View Post
    So how are manufacturers getting away with adding a 165v start cap into 220v supplied motors
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  10. #29
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    Its a capacitor start motor with a center tapped start winding that only sees 120 volts.

  11. #30
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Quote Originally Posted by Poodle Head Mikey View Post
    Maybe the back EMF is less than 165 volts?

    When you measured it - what was it?
    My meter isn't quick enough to test that during start up.

  12. #31
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Little trivia for ya'll

    Did you know you can use a Run cap in place of a Start Cap ?

    Yup , the only problem is you'd have to hook a bunch of them together to get the mfd needed

    BUT you cannot use a start cap in place of run cap

  13. #32
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    My Flukes have a peak-hold setting. Although I virtually never use them and I'm not sure if my Fieldpiece's have that feature.

    I do not Know - but I very much suspect that either the back EMF is less than the capacitor rating - or the motor maker has determined that the spike is too short to have bad effect.

    Run capacitors still last a long-ish time even with back EMF in excess of their rating. They certainly don't fail immediately. So maybe the voltage rating is in reference to 'continuous' back EMF - and not a momentary spike.

    Hey! Where are all the resident electrical geniuses? Why is a dummy like me having to attempt the heavy lifting here?

    PHM
    -----------


    Quote Originally Posted by Snapperhead View Post
    My meter isn't quick enough to test that during start up.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  14. #33
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I don't know about the genius part, but I was there in posts 6, 8, and 10.......
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  15. #34
    Join Date
    Jun 2008
    Posts
    61
    Post Likes
    Quote Originally Posted by Core_d View Post
    That is interesting, dont believe ive ever seen a dual voltage psc motor before.


    Sent from my iPhone using Tapatalk
    The picture just happened to be on my work phone; different application but same idea. Two winding's connected in series, start winding centre tapped between both winding's. Assuming the same inductor values for both winding's, both winding's would be subjected to half of the supply voltage.

    I assume in a PSC motor the start winding protects the capacitor from over voltage as they are in series together (half the voltage just as above)

    I am electrician with limited HVAC knowledge - just so everyone knows my back round.

  16. Likes Core_d liked this post.
  17. #35
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Just looked at 2 door cooler compressor not starting. Had one silver cap screwed next to the peckerhead. Had to do a double take on the mfds

  18. #36
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Actually, I think it's just the opposite. It has to do with the same principles as a transformer. The start windings are greater than the run windings, which means the voltage measured on the start winding will be greater. And in the case of a potential relay, the windings in the potential relay are greater than the start winding, so that creates the forces for the potential relay to pull in [opening the normally closed contacts], once the voltage increases after the motor is up to speed.

    With greater voltage, comes less current. Which, and I could easily be wrong on this point, the start cap is used to shift the phase and deliver more current to the start winding to get it going [the proper direction?].

    Think I remember most of this from trade school. I found it fascinating.

    On a bit of a tangent, you don't need this information to be an awesome service tech. There are specific skills/procedures for troubleshooting these things. But since I had a very good and well rounded electrical background before I went to HVAC trade school, learning these things really did fascinate me.


    Quote Originally Posted by thatguy View Post
    From what I’ve seen start capacitors are electrolytic while run capacitors are oil filled.

    I think pecmsg is on the right track with saying the voltage just isn’t there while the motor is starting up. Because the voltage it operates at is influenced by the back EMF, voltage is very low during the time it is in operation. Motor not spinning means no back EMF. Motor spins slow means low back EMF. Motor spins fast means high back EMF.


    Sent from my iPhone using Tapatalk
    I do a triple evac with nitro to remove non condensables.

  19. #37
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    I think someone with a peak reading meter should test the start cap voltage and report back. I would volunteer but I am pretty sure my fieldpiece doesn't read peak.

    Also I am not sure the original question was ever answered.
    Can you use a higher voltage start cap than originally specified?
    I would say yes because voltage rating is just what it can handle. The problem would likely be size.

    I agree with the OP I always use 440v run caps also. Our supply house doesn't sell 370v.

    Sent from mars using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  20. #38
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    You would probably need to measure short duration potentials with a recording oscilloscope.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  21. #39
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes

    Are start caps the same as run caps

    Quote Originally Posted by BBeerme View Post
    Actually, I think it's just the opposite. It has to do with the same principles as a transformer. The start windings are greater than the run windings, which means the voltage measured on the start winding will be greater. And in the case of a potential relay, the windings in the potential relay are greater than the start winding, so that creates the forces for the potential relay to pull in [opening the normally closed contacts], once the voltage increases after the motor is up to speed.

    With greater voltage, comes less current. Which, and I could easily be wrong on this point, the start cap is used to shift the phase and deliver more current to the start winding to get it going [the proper direction?].

    Think I remember most of this from trade school. I found it fascinating.

    On a bit of a tangent, you don't need this information to be an awesome service tech. There are specific skills/procedures for troubleshooting these things. But since I had a very good and well rounded electrical background before I went to HVAC trade school, learning these things really did fascinate me.
    I think we are saying the same thing just using different words. Because the start capacitor is removed from circuit once the motor speed is sufficient it won’t see the high voltage created by the back emf while its at full operating soeed. It’s only in circuit when the motor is stationary or low RPM so the generated voltage is still quite low at that moment in time.


    Sent from my iPhone using Tapatalk
    Quickly, I must hurry, for there go my people and I am their leader!

  22. #40
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Could be, I'm not very literate.


    Quote Originally Posted by thatguy View Post
    I think we are saying the same thing just using different words. Because the start capacitor is removed from circuit once the motor speed is sufficient it won’t see the high voltage created by the back emf while its at full operating soeed. It’s only in circuit when the motor is stationary or low RPM so the generated voltage is still quite low at that moment in time.


    Sent from my iPhone using Tapatalk
    I do a triple evac with nitro to remove non condensables.

  23. Likes thatguy liked this post.
+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •