    Post Likes

    Another Trane 2.5ton

    Same building as the 7.5ton

    This one was also grounded and blew its charge when i got to it. Blower was also LRA.

    This was a 5ton. Determined the duct was too small and it was apparently humid in this is "basement". 3 sides are underground. 1 side is open to the outside.

    Went with a 2.5ton hp with 037 AHU.

    New lineset. The old one was 1-1/8 x 1/2"

    Running new 3/4 x 3/8

    I ripped out the soundline that was in the ductwork. More pics to come.




    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter



    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    May 2006
    Posts
    3,680
    Post Likes
    looks better allready

  4. #4
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter
    There was a model 1700 dehumidifier that sat on 4x4s infront of the old AHU.

    I am terrible at taking before pictures. Wish i took them before i started ripping it out


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter
    More pics




    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    2,672
    Post Likes
    Aren’t those ducts off the top going to get a large portion of the air? Whats being done for balancing?

  7. #7
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter
    Balancing done at the registers. They are 24x24 layins.

    A scoop was added inside the transition to make the air go into the duct coming off the left.


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter



    Sent from my iPhone using Tapatalk

  9. #9
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter
    The 3/8 is bothering me. Ill probably tuck it in and hide it to the right.

    Did static testing.
    .5" at blower
    .13" in supply
    TESP- .63"

    Did electric heat cfm method and compared. Pretty close. Moving 1098cfm on low speed

    2.5ton outdoor with 037 indoor.

    Existing system was 5tons. No way ductwork was capable of moving that much air. So i downsized to match the ductwork. Ductwork could not be redone.

    Ran new lineset and got her down to 88 microns and weighed in additional charge.

    Will see how she runs over the weekend and will be back monday to start on the final 2, 4ton units.

    They will be trane h/p with unico ecm fan coils


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    26,577
    Post Likes
    It's times like this that I wish I had a camera/computer/Internet access/calculator/etc in my back pocket many years ago.
    I do a triple evac with nitro to remove non condensables.

  11. #11
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Thread Starter


    More pics from this job.

    2 other systems were unico high velocity paired with Trane HPs.