Thread: Air Flow Rate: Summer vs Winter

  1. #1
    Join Date
    Nov 2019
    Posts
    1
    Post Likes

    Air Flow Rate: Summer vs Winter

    Hello

    This is more of a conceptual question. I'm fairly new to all of this so bear with me.

    Say I have a 'constant' volume system (Air Handling Unit) with no recirculation that operates both during the summer and winter external conditions and maintains the same internal conditions (temp, relative humidity) all year round.

    If I size my Air Handler fan, say, for providing the required volumetric flow in the summer, what is the normal procedure for during the winter?:

    - accept that the pressure losses through the system will be different, and so the fan will output a different volume flow rate?
    - control the fan speed to ensure constant volume?

    Hope this makes sense
    Thanks

  2. #2
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    With no recirculation you have a make-up air unit. Provide the same amount of airflow year around. Size the heat and cooling source to handle it. The flow rate shouldn't vary enough to matter.
    No man can be both ignorant and free.
    Thomas Jefferson

  3. #3
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Furnaces have specific needs for air flow to avoid overheating. A/c air flow is adjusted to provide ideal moisture removal. They may be different.
    Keep us posted.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  4. #4
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Make-up air units are sized for a specific purpose and with no recirculation that purpose normally requires the same amount of airflow year around. For that reason design of the heating and cooling will handle the airflow. There are some MAU'S now that will do a lot of things. It depends on what you want them to do.
    I recently balanced a school that had three MAU'S with three different purposes. One was a football locker room that traditionally had odor problems. The supply and return both had VFD'S. I set the football locker room up to exhaust at 100% 24/7. The supply CFM varied to help control temperature and humidity. The heat wheel speed varied. Heating and cooling percentages varied. This unit would do anything you wanted and performed beautifully.
    One of the other MAU'S had to control room temperature and more importantly room pressure. The exhaust fan was set up to follow the supply fan at whatever speed necessary to keep the room at a positive pressure. The supply fan speed varied to control temperature and humidity. With both fans at 100% the room was positive.
    As you can see it depends on what you want the MAU to do and how much you are willing to spend.
    No man can be both ignorant and free.
    Thomas Jefferson

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •