    Bitzer Compressor - Low oil pressure alarm.

    Hello Guys...


    Need some help here please:


    I have a 30 HP Bitzer screw compressor on a refrigeration rack system with an Emerson CPC 835-0400 controller.

    The problem is that the compressor keeps alarming and shuts down. The alarm says low oil pressure/low suction. When onsite, everything looks normal, good suction pressure, good oil pressure and the alarm doesn't come back for days. There's 4 compressor in the circuit and it only happens on this compressor (#2).

    Any ideas or suggestions ?


    Thank you so much for any input.


    Rudy

  2. #2
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,388
    Post Likes
    None of the Bitzer screws I've seen had oil pumps, they typically use optical sensor for oil safety, maybe you should start by posting the compressor model.
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  3. #3
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,269
    Post Likes
    Is it on a pump down?

  4. #4
    Join Date
    Mar 2017
    Location
    Phoenix, AZ
    Posts
    33
    Post Likes
    Thread Starter
    Hi guys,

    Yes its in a pump down... BSE170

    Alarm says very low oil pressure. It has a noisy start (as if it was liquid flooded ) and goes away after 30 seconds. Then I can hear the 75% unloaded engaging, right after that compressor gets alarmed and shuts down.

    Any ideas?

    Thanks

  5. #5
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    8,704
    Post Likes
    That number is for oil.




    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,388
    Post Likes
    Quote Originally Posted by jlunaCR View Post
    Hi guys,

    Yes its in a pump down... BSE170

    Alarm says very low oil pressure. It has a noisy start (as if it was liquid flooded ) and goes away after 30 seconds. Then I can hear the 75% unloaded engaging, right after that compressor gets alarmed and shuts down.

    Any ideas?

    Thanks
    Post the compressor model number or take a picture, I never seen a Bitzer screw equipped with oil pressure switches or transducers, if its 75% unloaded that means its 25% loaded, are you taking infinity capacity control or step load? either way I never been able to hear one "engaging" are sure its not a recip? cause I dont think Bitzer makes a 30hp screw they start at 50hp.
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  7. #7
    Join Date
    Mar 2017
    Location
    Phoenix, AZ
    Posts
    33
    Post Likes
    Thread Starter
    Model number is CSH9573-180Y

    Step load.

    * I mixed the other post with this one. Different compressor same type of issue.

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,388
    Post Likes
    Quote Originally Posted by heatingman View Post
    That number is for oil.




    Sent from my iPhone using Tapatalk
    True .....it makes one wonder....
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  9. #9
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    8,704
    Post Likes
    How many compressors on the rack?

    Is there a secondary oil separator for the common rack?


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Mar 2017
    Location
    Phoenix, AZ
    Posts
    33
    Post Likes
    Thread Starter
    There’s two circuits, no secondary oil separator.

  11. #11
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    8,704
    Post Likes
    Are the compressors piped in Tandem, or truly separate circuits?


    Sent from my iPhone using Tapatalk

  12. #12
    Join Date
    Mar 2017
    Location
    Phoenix, AZ
    Posts
    33
    Post Likes
    Thread Starter
    Hi Heatingman,

    They’re truly independent circuits not piped in Tandem.

    Thanks

  13. #13
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,388
    Post Likes
    You need to figure where is the alarm coming from, there is not oil pump in that compressor so is not an oil pressure related alarm, now when compressor starts and trips hows the oil level in the sigh-glass? assuming the rack ran fine for years and just recently started to have issues, tell us more about the time line.
    There is not better place for the working men than the union! 100% UA the only HVAC union!