    I have an older 7.5 ton AAON unit that I work on ... Model RM-007-3-0-DA01-339. The unit dates from 2007. It has a clogged filter alarm. Not a big deal. I would like to know where the clogged filter switch is located. I'm not sure how to reset this minor alarm and I would like to at least verify the pressure switch is OK ... the filters are new. I do have the handheld service tool and Prism. It was raining today and I could not for the life of me figure out how to reset this alarm using the handheld. Any help would be appreciated.

  2. #2
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,433
    Post Likes
    I would think in the blower or filter section. They usually have very good wiring diagrams, i would check there also to see if wires are landed as the wiring shows. its sensing across the filters so should be close around there, or the tubing for it will go across the filters.
    UA Local 32 retired as of Jan 2020

  3. #3
    Join Date
    Oct 2015
    Location
    New Jersey
    Posts
    64
    Post Likes
    Thread Starter
    OK, that makes sense. I just checked the schematic. It has a blue and red wire. I did see a rather large rectangular metal switch in the blower cabinet with a tube that seemed to go over the filters and into the damper section. I did a search and that is apparently a P59900 Pressure Switch. So I'll check that and see if it's working.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,121
    Post Likes
    Remember to post back later so others can learn.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #5
    Join Date
    Feb 2014
    Posts
    6
    Post Likes
    The clogged filter switch is located in the return / air filter section of the unit right when you open the access door. Be sure the sensing / pick up tubing is not kinked or dust / debris built up.

  6. #6
    Join Date
    Oct 2015
    Location
    New Jersey
    Posts
    64
    Post Likes
    Thread Starter
    I'm probably going back in a week or two. I'll check it out. This unit has a few issues. Heat works but cooling is not operational. I'll bring those issues in a separate thread since they have nothing to do with the clogged filter alarm.

  7. #7
    Join Date
    Dec 2019
    Location
    USA
    Posts
    10
    Post Likes
    Yes most Aaons I’ve seen have the filter switch in the return air/filter section. Should have two pressure tubes 1 routed before and 1 after the filters taking A differential pressure reading. Like VA steam fitter said checking the tubing, they build up with dust and can cause an alarm. Blowing them out often takes care of that

  8. #8
    Join Date
    May 2018
    Location
    MN
    Posts
    122
    Post Likes
    Almost every CFS I've seen in an Aaon is in the blower section mounted on the right side of the HX enclosure.