Results 14 to 26 of 29
    Feb 2005
    Florida
    As far as it running in a vacuum for Ninety second, I don't know how many times the LP alarm was reset. This system has a Two second pump out, and on 407C it will drop to about 30PSI.
    So if you run it for another Eighty-Eighty seconds, where would the vacuum be?
    Also recently I had a tandem that the solenoid coil burned out, both compressor fried. Same Panasonic compressors, condenser full of oil. Again the unit had a Ninety second time delay on LP cutout.
    Aug 2009
    Beatrice, NE
    Sounds to me like more of a problem with oil return than running in a vacuum.
    Well; the manufacturer sure seems to think: more than 90 seconds. <g>
    I have been told with horrified seriousness to never run scrolls in a vacuum! Not Ever! Certain Death!!!
    As with many things which don't make sense to me; I kept probing for the exact genesis of the warning. And as is very often the case: Everybody knew the endless-repeated Caution - Nobody knew the core reason for it. <g>
    Not too too long ago I was talking to a Copeland rep. about some things and the vacuum-prohibition thing came back to me. He just parroted The Warning at first but I probed for the engineering reason. What exact bad thing will happen? Why is it unique to scroll compressors?
    The answer from the design boys was that a scroll is considered to be a positive displacement compressor with very low internal leakage / high efficiency and as such it is theoretically capable of achieving very deep vacuum levels. So the possibility exists that a scroll could create a low enough internal vacuum to allow internal arcing of the motor windings.
    The prohibition isn't really against Any vacuum - it is only against a deep (evacuation grade) vacuum.
    I can't see why a scroll wouldn't run as long as any other hermetic compressor while in a moderate vacuum. If you can; I'd like to hear your logic.
    PHM
    Quote Originally Posted by jimp View Post
    Its on a chiller.
    But how long can a scroll last running in a vacuum?
    PHM
    Or low and/or erratic SSH.
    Quote Originally Posted by BNME8EZ View Post
    PHM
    Feb 2005
    Florida
    One of my favorite parts of this “vacuum concern” is that “everybody” says that you can’t run a compressor in a vacuum. What is the difference between 0.1 psig versus -0.1 psig? In reality, there is no difference to the compressor. But manufacturers take phone calls from techs who have ZERO knowledge about what they are doing, so the manufacturers just give a blanket statement.
    The key is to understand where is the absolute lower allowable pressure the compressor can run. While I don’t know this exact number, there are going to be many factors that are involved.
    "Right" is not the same as "Wise".
  7. Likes icy78 liked this post.
  8. #20
  9. #21
    Mar 2015
    Medford, N.Y.
    I was taught by Copeland at their COSS class about Scrolls before they hit the "streets" and again years after that class. As said in this thread,Scrolls can not handle a "deep vacuum". They can handle a vac above that deep vac point. Scrolls were never made/produced to operate in a vac. As said, its the beauty of a Scroll to operate so wonderfully that it does create a deep vac rather quickly,killing itself. Simply front seating the SSV can kill a Scroll due to the deep vac being created so fast.
  10. #22
    Let's say we have a scroll pumping R-404. We want to run a -45 F. box. That will require a suction pressure of about 3-4". Assuming proper SSH and DSH - how would this 'running in a vacuum' cause harm to the low-stage scroll?
    PHM
    Quote Originally Posted by jayguy View Post
    PHM
  11. #23
    Mar 2015
    Medford, N.Y.
    PHM
    From my view point life would be a joy. From Copelands view point, I think you would need Factory Approval.
  12. #24
    Dec 2014
    Running in a vacuum causes scroll failure or I should say scroll compressor failure, by causing a short at the fuseite connections.
    Is that because there's no cooling effect and the Heat at that point causes breakdown?
    Sent from my SM-G950U using Tapatalk
  13. #25
    Mar 2015
    Medford, N.Y.
    Quote Originally Posted by icy78 View Post
    On Recip comps that are under a deep vac,there is a "warning". And that would be "DO NOT ENERGIZE THIS COMPRESSOR" because of the same type of electrical failure can/will happen. Using a Megger on a comp in a vac is not recommended,either. KindaSorta look at the "atmosphere" inside the comp motor section(freon,some oil vapor) as insulation on a wire. As the vac gets deeper,the "insulation" gets thinner.
  14. #26
    Quote Originally Posted by TechmanTerry View Post
    ...Using a Megger on a comp in a vac is not recommended,either. KindaSorta look at the "atmosphere" inside the comp motor section(freon,some oil vapor) as insulation on a wire. As the vac gets deeper,the "insulation" gets thinner.
    “Never meg in a vacuum” is also a myth. I have done it. The devil is in the details. In this case, the detail is the POWER behind the megger. Just like static electricity has enough voltage potential to jump a gap and cause a “spark” but you can’t weld with it. A battery operated megger won’t cause a fusite to blow up and be damaged...not enough power behind it...I know this by happenstance. Now a HIPOT would certainly cause damage.
    While i have always understood the vacuum as a “non-insulator” concept, however, I was never able to put it into words. I like your wording very much. Thank you for that!