Results 1 to 9 of 9
    Dec 2019
    Low suction low head pressure and gurgling
    Hi there and I hope I’m posting this on the right place.
    I am a marine mechanic and am currently having trouble with our dometic Hvac ac system on a boat. We are in the middle of nowhere and the Boss doesn’t want to move the boat until I can tell him what’s going on.
    System is running R22
    I have low suction pressure (45psi) and low superheat, lines frozen all the way from the condenser to the compressor.
    Discharge pressure is 155psi-165 and the discharge lines are hot to touch.
    The evaporators is water cooled but seams to be working fine as the refrigerant line out is room temp.
    There is also a bit of a gurgling sound coming from the unit.
    Current temp is 73f
    Hope I gave y’all all the info that’s needed.
    Cheers
    Jul 2011
    DFW, TX.
    Questions that need answers.
    Model and serial of said unit. Evaps water cooled? Smh idk... Condenser? Check the evap coil (that air flows past to cool you) to make sure its very clean. Other then that. This isn't a diy site, so not much can be said.
    Sent from my LG-G710 using Tapatalk
    Dec 2019
    Yer sorry condenser is raw water cooled, it’s been a long day.
    Evaporator is clean and the blower is working fine.
    No model or serial number to speak of just a sticker with the Hz on the compressor.
    Jan 2014
    New England
    Guessing Evaporator/and or suction line is icing?
    Dec 2019
    And sorry I realize it’s not a diy site. I just don’t know what else to do, closest big city is Cienfuegos and even then I don’t think they will let Cubans aboard. There rules not ours.
    Might have a leak in the system.
    Dec 2019
    Evaporator is fine, clean and no icing at all. Lots of airflow over it. Suction line ices up as soon as unit kicks on
    Dec 2019
    I thought so as well so I added 1/2 a pound of refrigerant and still low suction pressure so I removed it. Still same problem
    What is the factory charge amount? On some systems, half a pound won't make a difference, after the system is so low
    What was the condensers entering water temp when you took the readings, and the GPM going through the condenser.