    Hi there and I hope I’m posting this on the right place.

    I am a marine mechanic and am currently having trouble with our dometic Hvac ac system on a boat. We are in the middle of nowhere and the Boss doesn’t want to move the boat until I can tell him what’s going on.

    System is running R22

    I have low suction pressure (45psi) and low superheat, lines frozen all the way from the condenser to the compressor.

    Discharge pressure is 155psi-165 and the discharge lines are hot to touch.

    The evaporators is water cooled but seams to be working fine as the refrigerant line out is room temp.

    There is also a bit of a gurgling sound coming from the unit.

    Current temp is 73f

    Hope I gave y’all all the info that’s needed.

    Cheers

  2. #2
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    2,826
    Post Likes
    Questions that need answers.
    Model and serial of said unit. Evaps water cooled? Smh idk... Condenser? Check the evap coil (that air flows past to cool you) to make sure its very clean. Other then that. This isn't a diy site, so not much can be said.

    Sent from my LG-G710 using Tapatalk

  3. #3
    Join Date
    Dec 2019
    Posts
    5
    Post Likes
    Thread Starter
    Yer sorry condenser is raw water cooled, it’s been a long day.
    Evaporator is clean and the blower is working fine.

    No model or serial number to speak of just a sticker with the Hz on the compressor.

  4. #4
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,308
    Post Likes
    System is running R22

    I have low suction pressure (45psi) and low superheat, lines frozen all the way from the condenser to the compressor.

    and the discharge lines are hot to touch.

    Guessing Evaporator/and or suction line is icing?

  5. #5
    Join Date
    Dec 2019
    Posts
    5
    Post Likes
    Thread Starter
    And sorry I realize it’s not a diy site. I just don’t know what else to do, closest big city is Cienfuegos and even then I don’t think they will let Cubans aboard. There rules not ours.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Might have a leak in the system.

  7. #7
    Join Date
    Dec 2019
    Posts
    5
    Post Likes
    Thread Starter
    Evaporator is fine, clean and no icing at all. Lots of airflow over it. Suction line ices up as soon as unit kicks on

  8. #8
    Join Date
    Dec 2019
    Posts
    5
    Post Likes
    Thread Starter
    I thought so as well so I added 1/2 a pound of refrigerant and still low suction pressure so I removed it. Still same problem

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    What is the factory charge amount? On some systems, half a pound won't make a difference, after the system is so low

    What was the condensers entering water temp when you took the readings, and the GPM going through the condenser.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •