    Walk in Freezer

    Hey guys I have a walk in freezer(404a) that is reading OIL LOCKOUTout, AMB SBCL LOCKOUT.
    I do have ice build up from the compressor to Evap coil. My pressure is 227.4/31.6 156.1

    Any suggestions on best way to troubleshoot this issue?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,618
    Post Likes
    Quote Originally Posted by Ant100218 View Post
    Hey guys I have a walk in freezer(404a) that is reading OIL LOCKOUTout, AMB SBCL LOCKOUT.
    I do have ice build up from the compressor to Evap coil. My pressure is 227.4/31.6 156.1

    Any suggestions on best way to troubleshoot this issue?
    What temperatures go with those pressures?

    Whats the SH at the compressor?
    Whats the oil pressure at start up and 2, 5 and 10 mins later?

    Evaporator clear?
    Fan(s) turning right direction?

  3. #3
    Join Date
    Jan 2010
    Posts
    18,040
    Post Likes
    Indoor or outdoor condensing unit and what ambient ?

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,618
    Post Likes

  5. #5
    Join Date
    Jun 2019
    Location
    Austin TX
    Posts
    5
    Post Likes
    Ice build-up from the compressor to the evap... it sounds like the unit is flooding back.

  6. #6
    Join Date
    Sep 2009
    Location
    NorthEast
    Posts
    24
    Post Likes
    Oilfailure, probably due to compressor crank case full of liquid refrigerant due to flood back.

  7. #7
    Join Date
    Jan 2010
    Posts
    18,040
    Post Likes
    or liquid migration on off cycle.

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,653
    Post Likes
    Has someone bought an indoor condensing unit and put it outdoors ??

    That shit pisses me off so bad ...

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,618
    Post Likes
    Quote Originally Posted by ATX_Dan View Post
    Ice build-up from the compressor to the evap... it sounds like the unit is flooding back.
    Not in refrigeration! 30F SH at the pump with a -20 evaporator puts that line below freezing yet not flooding.

  10. #10
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,653
    Post Likes
    yup , and if the insulation is thin , and its humid out , the pipe will turn into a white baseball bat , and altho it looks bad , its normal

  11. #11
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,543
    Post Likes
    I love how people associate ice with flood back.

    It's a freezer, the refrigerant is like -10*F if not lower. WELL below freezing, any moisture would just freeze onto the pipe. All that ice means is that there's humidity in the air and the pipe is below freezing, that's it.

  12. #12
    Join Date
    Sep 2009
    Location
    NorthEast
    Posts
    24
    Post Likes
    Quote Originally Posted by Olivero View Post
    I love how people associate ice with flood back.

    It's a freezer, the refrigerant is like -10*F if not lower. WELL below freezing, any moisture would just freeze onto the pipe. All that ice means is that there's humidity in the air and the pipe is below freezing, that's it.
    You typically can thaw out a little frost or ice at the suction ball valve by just putting your hand on it for a few seconds. If you hand freezes to it and starts to burn, its flooding. 8/10 times.

    Without pictures or a better description, and the oil failures, I bet its flooding out the compressor.

  13. #13
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,543
    Post Likes
    It's possible that it is, but a quick SH measurement would confirm it either way.

    I'm just saying ice on a comp or pipes on a freezer does not mean it's flooding.