    New Code

    I have been having estimates to replace my A/C along with all new duck work. One of my contractors bidding on the job mentioned to me that, according to the new code, every bedroom needs to have a return line. Is that true? I am in Tampa Bay.

  2. #2
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    9,969
    Post Likes
    RETURN AIR DUCTS from All Bedrooms was first required
    for new construction more than a DECADE ago.

    The problems associated with No Bedroom Return Air path were
    first identified and tested > 18 years ago.

    Use of bedroom return air ducts is Not a " NEW " building code idea.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  3. #3
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    9,969
    Post Likes

    CURRENT CODE

    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  4. #4
    Join Date
    Dec 2019
    Location
    Tampa Bay
    Posts
    16
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    RETURN AIR DUCTS from All Bedrooms was first required
    for new construction more than a DECADE ago.

    The problems associated with No Bedroom Return Air path were
    first identified and tested > 18 years ago.

    Use of bedroom return air ducts is Not a " NEW " building code idea.
    Right now there is only one return duct (18 by 30) in the center of my home. That will change once I get my new system.
    Thanks

  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    9,969
    Post Likes
    Quote Originally Posted by Thomv47 View Post
    Right now there is only
    one return duct (18 by 30) in the center of my home.
    That will change once I get my new system.

    Thanks
    I presume the noted size actually refers The Single Filter Grille.

    18" x 30" = 3.75 sq feet filter
    ________ * 300 FPM
    ________ 1,100 CFM could be handled in many systems
    ________ IF the filter is < MERV 8
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    1,630
    Post Likes
    Also get a bid for a ductless mini split system. Might not need much backup heat in FL.

  7. #7
    Join Date
    Dec 2019
    Location
    Tampa Bay
    Posts
    16
    Post Likes
    Thread Starter
    Quote Originally Posted by Thomv47 View Post
    Right now there is only one return duct (18 by 30) in the center of my home. That will change once I get my new system.
    Thanks
    Yes. It is my only return.