Results 1 to 15 of 15

Thread: Help with a home heating issue causing headaches

  1. #1
    Join Date
    Dec 2019
    Posts
    6
    Post Likes

    Help with a home heating issue causing headaches

    Folks -

    Whenever my heater gets turned on I seem to get a headache. But nobody in my family does get the same headache I get...and the CO monitors don't ring any alarms.

    I assumed this is some kind of CO leakage or other gas leaking into the house from the furnace. Probably in smaller quantities not enough to trigger the CO alarm.I got a reputed heating company to come and take a look and they told me only one of the 4 burners is working and they need to change the gas valve. And that is a reason why the furnace is not working well... And also some cleaning was required. Given how ignorant I was about the furnace I agreed to it and signed their papers to get a valve and a future maintenance in six months !

    And then I started reading up on furnaces, saw a couple of youtube videos, got to this site yesterday and decided to post. To me it doesn't seem like the gas valves not working will trigger any leaks as the leaks will come from the heat exchangers or the exhaust flue pipes ? So this professional was a bit off in his diagnosis or is there a chance that a non working gas valve can trigger any leaks ?

    Looking for pointers - thanks !

  2. #2
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Off the shelf UL listed CO alarms will not trip until 70 PPM. You could have 69 PPM in your home and it’ll never set the detectors off.
    By contrast most fire departments will not enter a home without breathing apparatus if CO is over ~20 PPM.
    Low level CO alarms are what you want.
    What make and model furnace is this?
    It’s very dangerous is only one burner is working. It could cause CO poisoning or an explosion from raw unburned gas.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  3. #3
    Join Date
    Dec 2019
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by rider77 View Post
    Off the shelf UL listed CO alarms will not trip until 70 PPM. You could have 69 PPM in your home and it’ll never set the detectors off.
    By contrast most fire departments will not enter a home without breathing apparatus if CO is over ~20 PPM.
    Low level CO alarms are what you want.
    What make and model furnace is this?
    It’s very dangerous is only one burner is working. It could cause CO poisoning or an explosion from raw unburned gas.
    Thank you - I am not turning on the heater till the valve is replaced. Can you recommend low level CO monitors ?

    Also can you confirm if only one or 2 of the burners are operational can that really emit CO into the house or any other gases?

    Thanks!

  4. #4
    Join Date
    Dec 2019
    Posts
    6
    Post Likes
    Thread Starter
    I dont know the make and model - need to go up the attic to find it ...

  5. #5
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    If the burner isn’t lit there isn’t CO, but there could be raw gas.
    What did the tech say about the burners not firing?
    If the burners are firing poorly excess CO can be produced.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  6. #6
    Join Date
    Dec 2019
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by rider77 View Post
    If the burner isn’t lit there isn’t CO, but there could be raw gas.
    What did the tech say about the burners not firing?
    If the burners are firing poorly excess CO can be produced.

    Thank you rider ! The tech said one of the 4 burners was firing all the time , one was lit and then shutdown, two never came on

  7. #7
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    I think you could call the gas company or fire department to do a CO test for your home. That should give you some piece of mind until you get the low level CO detectors installed. Also alleviate your headaches.

    I think if you do a search on this site, someone will have mentioned low level CO detectors. Also try Google.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  8. #8
    Join Date
    Dec 2019
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by joemach View Post
    I think you could call the gas company or fire department to do a CO test for your home. That should give you some piece of mind until you get the low level CO detectors installed. Also alleviate your headaches.

    I think if you do a search on this site, someone will have mentioned low level CO detectors. Also try Google.
    Thank you joemach !

  9. #9
    Join Date
    Oct 2009
    Location
    God's country - Shenandoah Valley, VA
    Posts
    1,764
    Post Likes
    CAUTION!

    You have a very serous condition that could cause death!

    Turn the furnace off until it's properly repaired or replaced!

    I suppose it's possible that a bad gas valve could cause only one burner to fire, but I've never seen it in my 48 years in the trade.

    I would make that tech guarantee in writing that changing the gas valve and cleaning will fix the the issue and that the furnace will be safe to operate. A manometer and digital combustion analyzer should be used to confirm that and the results printed out and given to you. Accept nothing less.
    Bob Boan


    ​You can choose to do what you want, but you cannot choose the consequences.

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,743
    Post Likes
    The tech servicing your furnace should have a personal CO monitor on him! Ask him / her what its reading?

    There are several Low Level CO monitors on the market.

    Defender is one

  11. #11
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,116
    Post Likes
    To follow along with others I don't see how a bad valve can cause only 1 burner to operate. If this is a furnace with electronic ignition I don't see how it would light/stay lit as the flame sensor/board will not let it light if flame is present and if only one burner lights it will shut the whole thing down.

    Did the tech do a combustion analysis on the furnace? That would show how much CO it was producing. Did he leave it operational? I would hope not. The dangers of delayed ignition are nothing to take lightly. Did he check gas pressure? That can affect how burners light and burn. Is this LP or natural?

  12. #12
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes

  13. #13
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    After reading all, i might suggest a second opinion, something does not sound right, especially with what was reported to you and if they left the furnace operating. And i also think your gas provider and or fire dept would be a good call. Some gas company's also do some minor levels of repairs and safety inspections.
    UA Local 32 retired as of Jan 2020

  14. #14
    Join Date
    Dec 2019
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by buford View Post
    After reading all, i might suggest a second opinion, something does not sound right, especially with what was reported to you and if they left the furnace operating. And i also think your gas provider and or fire dept would be a good call. Some gas company's also do some minor levels of repairs and safety inspections.
    Thank you - I will not turn the thermostat onto "heat" till the valve is replaced.

  15. #15
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    Quote Originally Posted by mo_ View Post
    Thank you - I will not turn the thermostat onto "heat" till the valve is replaced.
    Better yet go up and turn the gas valve just outside your furnace to off. Perpendicular to the pipe is off. If you aren’t sure how to do that call the gas company immediately and they will do it.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •