Results 1 to 13 of 13
    Dec 2019
    New Furnace installed using existing flu and now condensate problem
    I had a new furnace installed last year, now we are getting condensate dripping and also some rust spots on top of the furnace and inside as well. I wanted to nip this issue in the bud so I called the installers. They said there was nothing they could do - that all 80% efficiency furnaces have this issue. I replied that my previous 25 year old 80% furnace didn't have this issue - what's changed?
    We gave a flat roof.
    5 foot section of 4" B vent goes through ceiling/roof.
    There is a galvanized single wall elbow, 2 foot section at a slight angle and another elbow into the top of the furnace.
    66,000 BTU in
    53,000 BTY out
    I have read that the burner can be adjusted to prevent this. They did no testing at all, other than to see if it ran.
    Possible that the blower is moving too much air. Or its not fired at it full 66,000 BTU input.
    What temp do you maintain it the house.
    Dec 2019
    At night we keep it at 68. During the day 70-72
    One more thing. There is an AprilAir humidifier attached to the new furnace. We keep it set between around 25-35 percent humidity dependent on outside temperature.
    S.E. Pa
    Need to run combustion analysis. Also consider a post purge cycle of about 4 minutes if not already.
    Dec 2019
    Thanks. Will call tomorrow for that. The installer recommended I run b vent all the way to the furnace. Said that might help. What do you think? 4 seems to be correct sizing. Could the stack be too short?
    State College, PA
    Have you called the manufacturer of the furnace? They should be able to help you out.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?
    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241
    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113
    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop
    Cincinnati, Oh
    Quote Originally Posted by JohnnyJack View Post
    Thanks. Will call tomorrow for that. The installer recommended I run b vent all the way to the furnace. Said that might help. What do you think? 4” seems to be correct sizing. Could the stack be too short?
    When you say "I" does he mean you, or does he mean he?
    "Just get it done son."
    Dad adjusted
    Jan 2012
    Broomall, PA
    What was the btu size & make and model of the previous furnace?
    If I do a job in 30 minutes it's because I spent 30 years learning how to do that in 30 minutes. You owe me for the years, not the minutes.
    Oct 2011
    Gladstone, Oregon (Portland)
    Is the furnace a Goodman?
    Dec 2019
    Quote Originally Posted by STEVEusaPA View Post
    It was a Trane
    Model:TUSO60A936A1
    60,000 BTU Input
    09/89 (whoops it was more than twenty five years old)
    Dec 2019
    The new furnace is a Lennox bought through Costco. Model ML180
    Quote Originally Posted by joemach View Post
    The manufacturer won't talk to the home owner. About technical aspects.
    Jun 2012
    Northern NV
    Should be B vent all the way. No single wall.
    A dying culture invariably exhibits personal rudeness. Bad manners. Lack of consideration for others in minor matters. A loss of politeness, of gentle manners, is more significant than is a riot.
    ― Robert A. Heinlein