  1. #14
    Join Date
    Dec 2014
    Posts
    2,920
    Post Likes
    Switch the pumps. What happens? Does it follow the questionable pump?

    Sent from my SM-G950U using Tapatalk

  2. #15
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    7,048
    Post Likes
    Ok. So the only issue is that the new pump (on the right) draws locked rotor amps when
    Started?

    You said nothing changed except
    You rotated the pump, and added piping. That could be quite a change for a small pump. First, I would verify check valve is actually opening.

  3. #16
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by 71CHOPS View Post
    Ok. So the only issue is that the new pump (on the right) draws locked rotor amps when
    Started?

    You said nothing changed except
    You rotated the pump, and added piping. That could be quite a change for a small pump. First, I would verify check valve is actually opening.
    If I pull the red hose and let it free flow its runs fine and draws 4.5 amps.

  4. #17
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,088
    Post Likes
    What took out the original pump?

    Sent from my SM-G960U using Tapatalk

  5. #18
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by Spitz View Post
    What took out the original pump?

    Sent from my SM-G960U using Tapatalk
    grounded

  6. #19
    Join Date
    Dec 2014
    Posts
    2,920
    Post Likes
    Did you try switching the pumps or is that not feasible here?

    Sent from my SM-G950U using Tapatalk

  7. #20
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,622
    Post Likes
    Check valve hung up?

  8. #21
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    3,759
    Post Likes
    Post the pump curve if you have it. When you tested the shut-off head did it match the pump curve?
    No man can be both ignorant and free.
    Thomas Jefferson

  9. #22
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    It's the same model pump that was removed.
    It flows 25 gpm at 45 psi.

  10. #23
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,388
    Post Likes
    Quote Originally Posted by jimp View Post
    If I pull the red hose and let it free flow its runs fine and draws 4.5 amps.
    That does not make any sense if we are talking about a centrifugal pump but if its a positive displacement pump then is very likely that the outlet is restricted somewhere!
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  11. #24
    Join Date
    Jan 2013
    Location
    United Kingdom
    Posts
    267
    Post Likes
    Pump wiring Star or Delta on both pumps ?


    Sent from my iPhone using Tapatalk

  12. #25
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by valdelocc View Post
    That does not make any sense if we are talking about a centrifugal pump but if its a positive displacement pump then is very likely that the outlet is restricted somewhere!
    Centrifugal, outlet goes from 3/4" to 1.5". I pulled the red hose off the barb and put a piece of 1.5" on it, then it pumped into the tank fine.

    It only stalls and pull high amps when its hooked up in normal configuration.

  13. #26
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,388
    Post Likes
    Quote Originally Posted by jimp View Post
    Centrifugal, outlet goes from 3/4" to 1.5". I pulled the red hose off the barb and put a piece of 1.5" on it, then it pumped into the tank fine.

    It only stalls and pull high amps when its hooked up in normal configuration.
    A centrifugal pump will draw more amps when pumping unrestricted, unless the tank is under vacuum the pump should draw less power with piping attached to the discharge and more amps free flowing!
    There is not better place for the working men than the union! 100% UA the only HVAC union!