Results 14 to 22 of 22
    Southold, NY
    Pressures without temperatures are worthless!
  2. Likes joemach liked this post.
  3. #15
    State College, PA
    Agreed.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?
    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241
    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113
    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop
  4. #16
    Southeastern Pa
    Quote Originally Posted by Snapperhead View Post
    Well lessseeee here
    Blower wheel was dirty , so the evap probly was too , and during a summer check someone added freeezy juice to bring up the low side
    Now winter is here and the thing is overcharged
    Ding ding ding.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
  5. #17
    Nov 2019
    Jacksonville, Fl
    This is a pretty straight forward call, but without any of the relevant information on hand you're probably not going to get the answer to it. You need the pressures at the liquid line service port and true suction port, ^T across drier, and temps on liquid and suction line all while running in heat.
  6. #18
    Mar 2015
    Medford, N.Y.
    60/215 summer press does not sound good to me. 215 head KindaSorta sounds like a 78-80*F ambient. So a 60psi loside sounds low.
  7. #19
    Jan 2014
    New England
    OK,OK,OK.. I think I got a piece of the puzzle figured out, used to be 30 degree over ambient in the 70’s and maybe 80’s? then convert to pressure, figure the 90’s its 20 degree over ambient? gives you a OD temperature of somewhere around 86 degree to get the posted 215 PSI head, is that correct OP? Was it at that OD temperature, please say that you checked the OD temperature..when you gave your readings. TP chart says 85 degree @ 211PSI
  8. #20
    Mar 2015
    Medford, N.Y.
    Quote Originally Posted by Bazooka Joey View Post
    OK,OK,OK.. I think I got a piece of the puzzle figured out, used to be 30 degree over ambient in the 70s and maybe 80s? then convert to pressure, figure the 90s its 20 degree over ambient? gives you a OD temperature of somewhere around 86 degree to get the posted 215 PSI head, is that correct OP? Was it at that OD temperature, please say that you checked the OD temperature..when you gave your readings. TP chart says 85 degree @ 211PSI
    Not quiet. More along the lines of what RSES says about "What Head Pressures Are Supposed To Be" and also what Jim Bergmann says in the Testo Article "Air-Conditioning Applications Guide" concerning Head Press.
    All a Good Read!
  9. #21
    Jan 2014
    New England
    Quote Originally Posted by TechmanTerry View Post
    All a Good Read!
    That was somewhat of a joke, to a degree...., maybe I should have put this symbol afterwards
  10. #22
    Mar 2015
    Tx
    If the blower wheel was dirty how was the amperage good?
    Super heat
    Sub Cooling #'s
    When was the last time this system was serviced?
    If the wheel is dirty, the evaporator coil is packed with crap too, usually.
Tags for this Thread
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR
