Thread: Crankcase heaters

  1. #21
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Poorly insulated ?
    I do a triple evac with nitro to remove non condensables.

  2. #22
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Well, If you have a 3 watt heater, with the mass of a compressor, and 5* ambient.....what’s going to win?

  3. #23
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    The little bit of heat that is put in even at 5 degrees OSA will still cause the refrigerant to migrate else where in the system. The refrigerant wants to go where it’s colder.


    Sent from my iPhone using Tapatalk

  4. #24
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Quote Originally Posted by heatingelement View Post
    Thanks for the info guys!!

    How about the ones that have a temp sensor, seen several on the Trane units that close at like 40 degrees or something.. any benefit to that instead of on 24/7?
    Energy savings. 480 volt unit have a transformer with stat to power CCH. Way to many parts. Trane use to trickle current through windings to generate heat

  5. #25
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Allied RTU do not come with CCH. Ordered a factory low ambient kit for RTU. Still not included. So, I guess they don't think it the risk is there for damaged compressors.

  6. #26
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Quote Originally Posted by stat View Post
    At Copeland school 25 years (Gene maybe?) ago we were told crankcase had no effect below 50F.
    Gene? Or Glenn Hannagan?

    My Copeland info in a Application Engineering Bulletin states that 0*F ambient is the boarder line for overpowering the heat produced by the properly sizes CCH.

  7. #27
    Join Date
    Sep 2014
    Location
    Portland, Oregon, United States
    Posts
    730
    Post Likes
    Thread Starter
    This may be related..
    Today I noticed a larger carrier RTU maybe 15 ton. On the side of the compressor contactors it had a separate contacts which were closed but open when the contactor pulls in. Is this for the crankcase heater? It didn't have a wire diagram to look through. What is the technical term for these contacts? Should they be replaced at the same time contactors are replaced?

  8. #28
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,564
    Post Likes
    Those would be called auxiliary contacts they are used for a few things including deenergizing the CCH while the compressor is on.

    Sent from my SM-G960U using Tapatalk

  9. #29
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Yes. Aux contacts (which are specific to the brand of contactor for reliable fit) should be replaced when the contactors are replaced.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #30
    Join Date
    Sep 2014
    Location
    Portland, Oregon, United States
    Posts
    730
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Yes. Aux contacts (which are specific to the brand of contactor for reliable fit) should be replaced when the contactors are replaced.
    Thank you

  11. #31
    Join Date
    Sep 2014
    Location
    Portland, Oregon, United States
    Posts
    730
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Yes. Aux contacts (which are specific to the brand of contactor for reliable fit) should be replaced when the contactors are replaced.
    What is the best thing to do when the aux. Contacts are not available anymore? Carrier has contactors but the aux contacts aren't available. Go with a different brand of contactor?

  12. #32
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,564
    Post Likes
    Leave them on all the time or you can go across one leg of the contactor.

    Sent from my SM-G960U using Tapatalk

  13. #33
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    Parallel the coil of contactor with a small relay to control heater on/off. See if you have enough room for a small relay and the coil of that relay’s amp draw won’t cause problems on the controller that tells the compressor contactor to pull in.
    This just adds more things to go wrong . Best may be to get all new contactor and six. switches. KISS (keep ,it, simple , stupid) No offense!!


    Sent from my iPhone using Tapatalk

  14. #34
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Or, you can let them run. Most of the units I see do not turn off the heaters when the compressors run. I see maybe 5% that turn them off.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  15. #35
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,746
    Post Likes
    On all the time or relay

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •