Thread: Question: How to Make Condo MAU More Energy Efficient?

  1. #1
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes

    Question: How to Make Condo MAU More Energy Efficient?

    First time poster on this forum. Not sure if I should be posting in the residential or commercial section.

    My questions are about a make-up air unit (MAU) for a small condo building (12 apartments) where I live, in Canada (i.e. cold climate). The building is a four story wood framed structure built in 1979. The MAU is an Engineered Air model S225/O/R which feeds air to three hallways in the building, pressurizing them slightly.

    Myself and some of the other owners are interested in optimizing the energy efficiency of this MAU, and the building in general. So I want to educate myself on what the options are so that I can discuss the issue intelligently with a professional.

    My questions:

    1) What considerations should be made in determining the hallway temperature set-point for the building?

    2) What is the typical range of temperature set-points for hallway air supplied by an MAU.

    3) Are there any code requirements for the temperature of condo building hallways?

    4) Is it possible to change the air flow rate from an MAU? If so how is this typically done?

    5) Are there any code requirement for the air flow rate to hallways from a MAU?

    6) Are there any other common ways to make a standard MAU operate more energy efficiently?

    Any suggestions would be appreciated.

  2. #2
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter

    How to Make a MAU More Energy Efficient?

    I live in a small condo building. Myself and some of the other owners are interested in improving the energy efficiency of the building. One of the things we are considering is adjusting the temperature and/or air flow rate from a make-up air unit (MAU) that supplies air to the building hallways.

    With respect to this, the questions I have are:

    1) Other than the comfort level of the temperature in the hallways, are there any other factors that we should be considering?

    2) Is there a simple way to adjust the air flow rate from a MAU?

    3) Are there any other common ways to make a standard MAU operate more energy efficiently?

    Any suggestions would be appreciated.

  3. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    The make up air unit's purpose is to replace the air that is being sucked out of the building by things like bathroom or kitchen exhaust fans, dryers, and gas burning appliances. I have also heard that maintaining a slightly positive building pressure can help keep out bugs. If a building is in a negative, things such as natural draft water heaters and boilers might not draft correctly and could cause a dangerous carbon monoxide situation.

    Ideally a building's pressure should be neutral to slightly positive. In my experience though, most buildings instead seem to be in a slight vacuum.

    How is your building? You probably don't want to hear this, but you likely should be thinking of increasing the blower speed, not slowing it down.

  4. #4
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by ammoniadog View Post
    The make up air unit's purpose is to replace the air that is being sucked out of the building by things like bathroom or kitchen exhaust fans, dryers, and gas burning appliances. I have also heard that maintaining a slightly positive building pressure can help keep out bugs. If a building is in a negative, things such as natural draft water heaters and boilers might not draft correctly and could cause a dangerous carbon monoxide situation.

    Ideally a building's pressure should be neutral to slightly positive. In my experience though, most buildings instead seem to be in a slight vacuum.

    How is your building? You probably don't want to hear this, but you likely should be thinking of increasing the blower speed, not slowing it down.
    I think we have pretty good positive pressure in our building. If I put my hand at the bottom of the entrance door to my apartment, I can feel air blowing lightly underneath the door from the hallway.

    In fact I am thinking there is too much positive pressure. The MAU was not working for a week or so in October this year. During this time I noticed that my apartment was about 2 degC (4 degF) cooler during the night. I figure this was because the MAU pushes warmed air continuously into my apartment from the hallway when it is working.

    I would like to set it at the minimum acceptable temperature and flow rate, to save some money on heating the air and to have better control of the temperature in my apartment. The temperature is easy to adjust, but the flow rate I don't know if there is a way to do this. And for both temperature and flow rate I'm not sure if there are code requirements as to what the settings must be.

  5. #5
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    It needs to be looked at by someone who can "see" the whole building picture. Mechanical as well.
    Small MUA savings realized by lower MUA cfm and temperature may become big building $ losses in a few years.

    Sent from my SM-G950U using Tapatalk

  6. #6
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by icy78 View Post
    It needs to be looked at by someone who can "see" the whole building picture. Mechanical as well.
    Small MUA savings realized by lower MUA cfm and temperature may become big building $ losses in a few years.

    Sent from my SM-G950U using Tapatalk
    Do you know where we should look for an HVAC expert that can look at the entire building?

    We have a mechanical maintenance company that maintains the MAU and other equipment. Should we have them do this, or would it be better to bring in somebody from a company that installs MAUs, or a company that manufactures MAUs?

  7. #7
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by nielkfj View Post
    I live in a small condo building.

    Myself and some of the other owners are interested in improving the energy efficiency of the building.

    One of the things we are considering is adjusting the temperature and/or
    air flow rate from a make-up air unit (MAU) that supplies air to the building hallways.

    With respect to this, the questions I have are:

    1) Other than the comfort level of the temperature in the hallways,
    are there any other factors that we should be considering?

    HUMIDITY CONTROL

    2) Is there a simple way to adjust the air flow rate from a MAU?

    __ AUTO ADJUST DAMPER would be standard on MAU.
    Damper would be controlled by providing ~ 0.05" W.C. Positive Pressure


    3) Are there any other common ways to make a standard MAU operate more energy efficiently?

    CO2 Controller may be an alternative in a few situations.

    _ Might wish to think about manually opening window during Clothes Air Dryer use.
    Control the TIMING AND AMOUNT of exhaust air from EACH Condo.

    ASHRAE STD. 62.2 - 2013
    ___ Understand & Use the INFILTRATION CREDIT _ _ from data provided by a BLOWER DOOR TEST

    For example,
    _ 30 CONDOS * ~ 40 CFM / CONDO = 1,200 CFM Total Continuous ( weekends )
    __________ 40 CFM Could be less than a Continuous flow rate.
    ______ … … No one home during the day _ _ Reduce exhaust air flow rate for upto 12 hours

    https://www.energy.gov/sites/prod/fi...ily_walker.pdf
    Last edited by dan sw fl; 11-29-2019 at 06:23 AM.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  8. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    You need a Mechanical Engineer. There are several factors involved, Building code and Fire Codes. Residential building Common areas are Positive pressure. Hallways, Emergency stairs Etc. Air changes per hour requirements need to be meet!

  9. #9
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Is the MAU using gas for fuel? And do each units have a gas fireplace? I have seen condos where the gas is on a common meter and during the winter, the fire places are on and drives up usage.
    UA Local 32 retired as of Jan 2020

  10. #10
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    3,404
    Post Likes
    Big capital expense, but might consider an air-to-air heat exchanger that takes all the exhaust air (bath vents) from the building in a common duct and transfers the recovered heat into the supply air. Supply air will be cooler than what you have now, but economy of operation is worth the look.. All the new hotels I've seen use these.

    As to efficiency of MAU, if it is a direct fired type, it is 100% efficient. Engineer is recommended in any case, one that has actually worked hands on in the field is preferable..
    “A dying culture invariably exhibits personal rudeness. Bad manners. Lack of consideration for others in minor matters. A loss of politeness, of gentle manners, is more significant than is a riot.”
    ― Robert A. Heinlein

  11. #11
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    3,404
    Post Likes
    double..
    “A dying culture invariably exhibits personal rudeness. Bad manners. Lack of consideration for others in minor matters. A loss of politeness, of gentle manners, is more significant than is a riot.”
    ― Robert A. Heinlein

  12. #12
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    IMO, you need a good tech, who can also think like a mechanical engineer.
    Or a good mechanical engineer, who has a tech who can make the ME's design work properly.

    Sent from my SM-G950U using Tapatalk

  13. Likes UmmScott liked this post.
  14. #13
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    Quote Originally Posted by Juan Madera View Post

    As to efficiency of MAU, if it is a direct fired type, it is 100% efficient.
    Ha, I was waiting for someone to say this! It don't get more efficient than 100%, well unless it's a heat pump, but I've gotten into some heated arguments about how it's impossible for heat pumps to defy the laws of physics, so I'm not going to go there.

    With that being said, I believe direct fired units are banned from areas where people sleep, so I'm guessing it has heat exchangers.

    Quote Originally Posted by nielkfj View Post
    I think we have pretty good positive pressure in our building. If I put my hand at the bottom of the entrance door to my apartment, I can feel air blowing lightly underneath the door from the hallway...
    This doesn't prove anything other than that your apartment is at more of a negative pressure than the hallway is. A better test would be to go down near the water heaters/boilers when they're not running and hold a match near the flue pipe and see which direction the flame goes (assuming that they're natural draft with no dampers), or go near an outside door to the building and do the same thing with the door slightly cracked.
    Last edited by ammoniadog; 11-29-2019 at 09:27 PM.
    If at First You Don't Succeed, Skydiving Is Not for You.

  15. #14
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    HUMIDITY CONTROL
    I'll keep humidity control in mind. But Calgary is fairly dry, if anything we could probably use higher humidity.

    __ AUTO ADJUST DAMPER would be standard on MAU.
    … Damper would be controlled by providing ~ 0.05" W.C. Positive Pressure
    Interesting. I didn't know that. If it has an auto damper that controls the air pressure that would be ideal. I'll ask the manufacturer.

    Is there some sort of small compressor built into the MAU that provides the air pressure to control the damper?

    CO2 Controller may be an alternative in a few situations.
    Not sure what you mean here. The MAU only supplies air to hallways (and the boiler room), not a garage, if that's what you mean.

    _ Might wish to think about manually opening window during Clothes Air Dryer use.
    I guess that would reduce the amount of air going through the MAU. But I imagine the amount of energy savings would be minimal, and people are unlikely to do this in the winter when the weather is cold.

    Control the TIMING AND AMOUNT of exhaust air from EACH Condo.

    ASHRAE STD. 62.2 - 2013
    ___ Understand & Use the INFILTRATION CREDIT _ _ from data provided by a BLOWER DOOR TEST

    For example,
    _ 30 CONDOS * ~ 40 CFM / CONDO = 1,200 CFM Total Continuous ( weekends )
    __________ 40 CFM Could be less than a Continuous flow rate.
    ______ … … No one home during the day _ _ Reduce exhaust air flow rate for upto 12 hours
    A lot of information to absorb here, but at first glance it looks like an interesting possibility - beyond what I had in mind, but perhaps a re-think of the ventilation system for the whole building would be worth it if the energy savings are large.

    According to some old drawings that I have, the original MAU (replaced 12 years ago) was rated for 1,500 cfm. The square footage of the entire building, 12 apartments and all common areas, is roughly 18,000 sqft (not all areas are ventilated by the MAU). Assuming the current MAU has the same flow rate, does 1,500 cfm seem excessive?

  16. #15
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    You need a Mechanical Engineer. There are several factors involved, Building code and Fire Codes. Residential building Common areas are Positive pressure. Hallways, Emergency stairs Etc. Air changes per hour requirements need to be meet!
    I see. I was kinda thinking it would require an engineer if the air flows are changed.

    However, I think the first thing that needs to be done is to find out if the current MAU system is operating as intended. Perhaps it is providing too much flow rate. Do you know how this would be checked? Would this typically be done by a maintenance technician?

  17. #16
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by buford View Post
    Is the MAU using gas for fuel? And do each units have a gas fireplace? I have seen condos where the gas is on a common meter and during the winter, the fire places are on and drives up usage.
    The MAU is indeed gas fired, but there are no gas fireplaces in the building.

    However, the boiler and hot water heater are also gas fired and there is only one meter for the whole building, as far as I know. So we don't actually know how much gas the MAU uses. But I think it will be much more than the boiler and water heater combined, since the MAU runs continuously 24/7 and heats air from sometimes sub-zero temperatures to room temperature. Whereas the boiler is normally only maintaining room temperature in each zone.

  18. #17
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    Quote Originally Posted by nielkfj View Post
    I'll keep humidity control in mind. But Calgary is fairly dry, if anything we could probably use higher humidity.



    Interesting. I didn't know that. If it has an auto damper that controls the air pressure that would be ideal. I'll ask the manufacturer.

    Is there some sort of small compressor built into the MAU that provides the air pressure to control the damper?



    Not sure what you mean here. The MAU only supplies air to hallways (and the boiler room), not a garage, if that's what you mean.



    I guess that would reduce the amount of air going through the MAU. But I imagine the amount of energy savings would be minimal, and people are unlikely to do this in the winter when the weather is cold.



    A lot of information to absorb here, but at first glance it looks like an interesting possibility - beyond what I had in mind, but perhaps a re-think of the ventilation system for the whole building would be worth it if the energy savings are large.

    According to some old drawings that I have, the original MAU (replaced 12 years ago) was rated for 1,500 cfm. The square footage of the entire building, 12 apartments and all common areas, is roughly 18,000 sqft (not all areas are ventilated by the MAU). Assuming the current MAU has the same flow rate, does 1,500 cfm seem excessive?
    That's a tiny MUA.
    Probably everyone was thinking at least 6-12000 cfm.
    Also, are you sure it doesnt use some return air?
    Altho 1500 ÷ 18 is only about 80cfm per apartment, so it's probably sized to make up the exhaust air.

    Sent from my SM-G950U using Tapatalk

  19. #18
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by Juan Madera View Post
    Big capital expense, but might consider an air-to-air heat exchanger that takes all the exhaust air (bath vents) from the building in a common duct and transfers the recovered heat into the supply air. Supply air will be cooler than what you have now, but economy of operation is worth the look.. All the new hotels I've seen use these.

    As to efficiency of MAU, if it is a direct fired type, it is 100% efficient. Engineer is recommended in any case, one that has actually worked hands on in the field is preferable..
    Ya, probably a big capital expense and unlikely to be accepted by other owners. What I'm focussing on is trying to optimize the efficiency of the existing equipment. I figure that means reducing the supply temperature from the MAU, and reducing the flow rate if possible. It seems like there is no code restriction on the supply temperature. However, reducing the flow rate is restricted by code. That's where the engineer would be needed I assume.

    Another option mentioned is installing a programmable thermostat that will set the hallway temperature back during the night.

    I sure hope the MAU isn't direct fired. I'm pretty sure it is indirect, otherwise we would smell natural gas from time to time I would think.

  20. #19
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    85
    Post Likes
    Thread Starter
    Quote Originally Posted by icy78 View Post
    That's a tiny MUA.
    Probably everyone was thinking at least 6-12000 cfm.
    Also, are you sure it doesnt use some return air?
    Altho 1500 ÷ 18 is only about 80cfm per apartment, so it's probably sized to make up the exhaust air.

    Sent from my SM-G950U using Tapatalk
    I'm quite sure there is no return air going into the unit. I've been up on the roof and took photos. Just checked the photos now and there is definitely no ducting going into the unit upstream of the fan.

    There's only 12 apartments. So 1,500 ÷ 12 = 125cfm per apartment.

    For some reason the hallways for the two basement apartments do not have any make-up air. I might be because both of these apartments have their own hallway with no other apartments sharing that hallway.

  21. #20
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by nielkfj View Post
    I'll keep humidity control in mind. But Calgary is fairly dry, if anything we could probably use higher humidity.

    Interesting. I didn't know that. If it has an auto damper that controls the air pressure that would be ideal. I'll ask the manufacturer.

    ___________
    _______ I suspect damper may have electrical controller. ___ ie.. Belimo or similar

    Is there some sort of small compressor built into the MAU that provides
    the air pressure to control the damper?
    ___________

    Not sure what you mean here.
    The MAU only supplies air to hallways (and the boiler room), not a garage, if that's what you mean.

    I guess that would reduce the amount of air going through the MAU.
    But I imagine the amount of energy savings would be minimal, and
    people are unlikely to do this in the winter when the weather is cold.

    A lot of information to absorb here, but at first glance it looks like an interesting possibility -
    beyond what I had in mind, but perhaps a re-think of the ventilation system
    for the whole building would be worth it if the energy savings are large.

    According to some old drawings that I have, the original MAU (replaced 12 years ago)
    was rated for 1,500 cfm.
    __ Actual set-up and rating would not necessarily be the same.

    The square footage of the entire building, 12 apartments and all common areas,
    is roughly 18,000 SqFt (not all areas are ventilated by the MAU).

    Assuming the current MAU has the same flow rate,
    does 1,500 cfm seem excessive?
    12 CONDOS _ 2 BEDROOMS _ ~ 1,200 SQ FT EACH

    ASHRAE 62.2 -2013

    Required Make-Up air flow rate would be in the Ball park of 30 CFM
    after an Infiltration Credit of 30 CFM is used.

    The existing Infiltration amount must be verified by an actual Blower Door Test.

    EXAMPLE WORK SCOPE:
    _________ One OPTION

    Hallways = 0.03 * ~ 3,000 = ~ 90 CFM

    12 * 30 CFM = 360 CFM
    ____________+ 90 CFM
    ___________+ ___ ___ any Make-up Air for any other COMMON Areas
    _____ Total < ~ 600 CFM.

    POSITIVE PRESSURE MUST BE MAINTAINED in Hallways.

    It appears that 1,500 CFM is excessive IMO.
    However, your local requirements may be based on
    a Canadian IAQ standard that I am not familiar with.

    NOTE: Hallways are not considered to have Occupants.

    AHJ in applicable Calgary Building Department / Disciplines
    should review your proposed MAU plans.

    AUTHORITY HAVING JURISDICTION

    ANY STRUCTURAL CHANGES WOULD BE SUBJECT TO LOCAL PERMITING PROCESS IMO.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •