    Savings based on 780 CFM MAU air flow rate versus MAU rated air flow rate
    __ = $ 43 / Year at $ 0.30 / N.G. THERM

    __ Reducing the MAU Supply Air Temperature is Not reasonable.

    __ Determination of an appropriate air flow rate & set-up
    __ is part of the on-site TAB process (Test, Adjust & Balancing ).
    Attached Images Attached Images  
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  2. #28
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    9,712
    Post Likes
    MAU EFFICIENCY IMPROVEMENT
    AIR FLOW RATE REDUCTION
    PROJECT BUDGET

    $ 522 / YEAR Savings 12 Condos
    ______ _____ at $0.30 per N.G. THERM

    __ Expenses __
    1. ENGINEERING
    2. Blower Door Testing
    3. Permitting, IF Any.
    4. MAU CONTROLS
    ___ Hallway Pressure Sensor(s)
    ___ Damper Control
    5. MAU Controls INSTALLATION
    6. Ventilation EXHAUST Control - 12 Condos
    7. Commissing, TAB
    8. MAINTENANCE

    How does the long term Cost Benefit look at-this-time?

    Payback Period Estimate: ? __ Years
    . < 8 Years __
    . < 10 Years __
    . < 12 Years __
    . < 14 Years __
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  3. Likes icy78 liked this post
  4. #29
    Join Date
    Nov 2019
    Location
    Calgary, Alberta, Canada
    Posts
    54
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    MAU EFFICIENCY IMPROVEMENT
    AIR FLOW RATE REDUCTION
    PROJECT BUDGET

    $ 522 / YEAR Savings 12 Condos
    ______ _____ at $0.30 per N.G. THERM

    __ Expenses __
    1. ENGINEERING
    2. Blower Door Testing
    3. Permitting, IF Any.
    4. MAU CONTROLS
    ___ Hallway Pressure Sensor(s)
    ___ Damper Control
    5. MAU Controls INSTALLATION
    6. Ventilation EXHAUST Control - 12 Condos
    7. Commissing, TAB
    8. MAINTENANCE

    How does the long term Cost Benefit look at-this-time?

    Payback Period Estimate: ? __ Years
    . < 8 Years __
    . < 10 Years __
    . < 12 Years __
    . < 14 Years __
    OK, thanks for listing the factors that should be taken into consideration.

    At only $522/year savings it might take several years to pay back.

    But the savings might be higher. We are assuming that the current MAU is pushing 1,500 cfm. It may be pushing more than that. The people who have commented on the videos that I made of air entering and exiting my apartment all said that there is excessive flow rate. So perhaps when they replaced the MAU in 2007 they installed a larger unit - who knows.

    Also there would be improvements to the living environment. As it is right now, the MAU makes it more difficult to cool my apartment at night because it keeps pumping in room temperature air. Also, when I crack a window open a bit, the outside air doesn't flow into my apartment because the MAU is creating a slight positive pressure, forcing air out instead. These aren't such big problems but it would be nice if they were resolved.

  5. #30
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    2,185
    Post Likes
    One part of the design of the MAU is to make the hallway positive to control offensive odors from cross contaminating other condos.